Also mate sure that the inner flue has not corroded where the terminal is.I have not checked voltage between T2 and T4.
I have replaced APS.
I have not checked overheat stat.
I will check these tommorrow. Thanks.
Discuss Potterton Profile 50e not sparking in the Plumbing Jobs | The Job-board area at PlumbersForums.net
Also mate sure that the inner flue has not corroded where the terminal is.I have not checked voltage between T2 and T4.
I have replaced APS.
I have not checked overheat stat.
I will check these tommorrow. Thanks.
thanks for your repliePretty sure a profile wouldn’t spark without the case on even with a new APS,sometime trying to simulate enough pressure to operate the switch is not exact enough & trying to see the spark with the case on can be hard to confirm.Try disconnection the HT lead from pcb an using an insulated screw driver near by weather it’s bridging a spark to that. If you’ve got continuity through your lead then there is no reason it should not spark at pilot assembly. Could be wrong but maybe take out pilot injector an check this is not blocked
Pretty sure a profile wouldn’t spark without the case on even with a new APS,sometime trying to simulate enough pressure to operate the switch is not exact enough & trying to see the spark with the case on can be hard to confirm.Try disconnection the HT lead from pcb an using an insulated screw driver near by weather it’s bridging a spark to that. If you’ve got continuity through your lead then there is no reason it should not spark at pilot assembly. Could be wrong but maybe take out pilot injector an check this is not blocked
I have tried a new PCB and a new APSYou’re right. I wasn’t thinking. It’s a positive pressure case isn’t it.
I am going to try another PCB which I know has come from a working boiler and make sure that the Fan is changing over the ApsGot to be the fan not running fast enough or you have been unlucky & new board was faulty !
Was the APS from a working boiler?I am going to try another PCB which I know has come from a working boiler and make sure that the Fan is changing over the Aps