Hi I have a baxi boiler behind fireplace in the cupboard beside fireplace there is a pipe that has a screw thread in it but no screw this is where it is dripping the cupboard is dry but can tell damp over time, salty deposits also I know nothing about boilers but don't want to be ripped of by engineer as last person to touch was engineer last year, can you tell me if pipe should be open and dripping or requires screw also name of pipe please pic attached thank you

sketch-1502386776664.png
 
That looks very much like an old spring tensioned safety valve.

These often drip when very old. These are still available and usually
a fairly quick and easy job for a plumber to replace.

It is unlikely to burst and flood the place and would probably
weep for a long time without being too much of a problem.
 
That looks very much like an old spring tensioned safety valve.

These often drip when very old. These are still available and usually
a fairly quick and easy job for a plumber to replace.

It is unlikely to burst and flood the place and would probably
weep for a long time without being too much of a problem.
Thank you so much I was so worried
 
Its a old style saftey valve employ a GSRI to replace it and service and test the back boiler and fire front , the regulations have been contravened if you have removed the fire front and are not GAS SAFE REGISTERD . KOP
 
Its a old style saftey valve employ a GSRI to replace it and service and test the back boiler and fire front , the regulations have been contravened if you have removed the fire front and are not GAS SAFE REGISTERD . KOP
Thank you I'm not touching anything as I know nothing, the engineer was in there December last year today I noticed salting outside the small cupboard and signs of long term dripping it's dripping probably ever 10 minutes but has obviously damaged some brickwork, thanks your advice helped
 
That ok then Misty just get it replaced and a service and gas saftey check regards Kop
 
Status
Not open for further replies.

Reply to Pipe dripping from open end boiler pipe in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello, bit of a noob question but would someone be able to help me to understand the pipes coming off our boiler. It's a Grant oil combi boiler...
Replies
9
Views
702
  • Question
Hi, We have a Grant oil combi boiler. Only 3 years old. Been a right pain. Already had expansion vessel replaced and the 3 bar PRV and another...
Replies
1
Views
590
Hi, can anyone tell me which pipes are flow and return please. I removed old leaking 2008 C26 firebird oil boiler in June . We have now...
Replies
2
Views
548
Hi, Looking to see if anyone can give some advice please. My Baxi boiler has been losing pressure and I am having to top it up approx. every 4...
Replies
7
Views
784
V
After power cut boiler over heated, since then water is dripping from the over flow pipe. I have a heat genie could it be stuck open or dirt...
Replies
0
Views
1K
Vinny99m
V
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock