I still don't see why the pipe has to be 22mm as long as the pressure drop is within regs (as per Shaun and Snowhead's advice).
 
I still don't see why the pipe has to be 22mm as long as the pressure drop is within regs (as per Shaun and Snowhead's advice).

The only time is if it's out of spec e.g. More than allowed pressure drop
 
If the old boiler has a pilot light then it will be an atmospheric burner, it will only require enough gas pressure to make Burner pressure, for example 10mb, your new boiler will be a zero governer, these ideally require 20mb inlet working, but depending on the boiler can be as low as 14mb, more usual is 16.5 to 18mb. If your meter regulator is supplying 19-21mb working pressure and you then don't have enough working pressure at the boiler, then your Pipework is undersized. The engineer who carried out the survey should have carried out a pipe sizing exercise to determine if the existing pipe is suitable, he has said it is not and requires upgrading for a new boiler, if he hadn't done this and just fitted a new boiler, he would be liable to correct the installation error at his own cost. Sounds like he is a professional doing a good job, I would suggest you follow his advice
 
Providing the pressure drop is within the regulations then you are ok , if not then it will need to be addressed i am afraid ,when you upgrade any proffesional Gsr would upgrade a 30year old gas supply when fitting a new modern condensing boiler any debris rust or otherwise would not be a issue then and you will have a supply correctly sized and which will last the life of the boiler and longer regards kop
 
The only time is if it's out of spec e.g. More than allowed pressure drop

Ok, thanks Shaun - I understand. What do you think of my plan in post 17?

The engineer who carried out the survey should have carried out a pipe sizing exercise to determine if the existing pipe is suitable, he has said it is not and requires upgrading ................. I would suggest you follow his advice

Thanks for that explanation GH77.

The pipe coming out of the meter is 22mm, so it reduces to 15mm somewhere inside the house. It would be really good if I could find out exactly where - maybe it's right next to the boiler (the 15mm disappears into the plaster so I can't tell).

Btw, there's a rust-coloured deposit all over the inlet pipe to the meter. I wonder if it's got inside the pipe as well. Hmm.

Providing the pressure drop is within the regulations then you are ok , if not then it will need to be addressed .....

Ok, thanks Kop.
 
I would get no 2 done first and see what you get
 
IMG_5893.PNG
Depends where your pressure test point at the boiler is, whether you've got one before the boiler or using the test point on the Gas Valve, picture paints a thousand words
 
Status
Not open for further replies.

Reply to Gas pressure question in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two...
Replies
2
Views
224
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
560
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
285
PSxxxxxx
P
The fittings below are for a mixer bar attached to a self contained shower. i.e not a wall. The attaching screws have snapped. I could get two new...
Replies
1
Views
276
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m...
Replies
6
Views
321
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock