Discuss Boiler not firing up sometimes in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.
Messages
35
I put this problem to the forum 3 weeks age and everyone said I should get the installer back.

I did that and he could not find a problem.

I also had British gas out twice (I have a yearly maintenance contract with them) and the first man changed the motor on the Honeywell 3 port valve - result no difference. The second man changed the complete 3 port valve after checking that all the voltages were ok and again no change.

Does anyone have any ideas where the problem could be. I have updated what the fault appears to be


I have astrange problem (to me). Sometimes the new Worcester 18RI does not fire up whenI would expect it to, for example.

I sometimes get up in the morning and the heating has not come on. If I turn off the hot water using the Hive controller then the boiler fires up and the radiator start to get warm


Does this sound ok or could there be a problem.


 
sounds like something with your hive setup maybe
 
it sounds like a it could be problem with the wiring have they wired the cylinder stat correctly or is the cylinder stat faulty
 
I'll have a check but it was fine before the new boiler went in, maybe they moved a wire or something.

Thanks for your help again, I will report back with the results (one day soon hopefully)
 
I've been doing some checks of the wiring in the Honeywell junction box and I have attached a photo of the present layout

I looked at an old photo taken before the hive was fitted and the only thing that changed when the hive was fitted, was a link where the room stat was.

The only thing I can see that has changed on the new photo since the new boiler was fitted is the new brown live wire to the boiler and the grey wire from the boiler connected by chocolate block to the brown wire to the pump. (the switched live to the boiler is now black instead of brown previously)

Should there have been any other changes or links cut etc.

SEE BELOW FOR POST WITH PHOTO
 
Last edited:
I've been doing some checks of the wiring in the Honeywell junction box and I have attached a photo of the present layout

I looked at an old photo taken before the hive was fitted and the only thing that changed when the hive was fitted, was a link where the room stat was.

The only thing I can see that has changed on the new photo since the new boiler was fitted is the new brown live wire to the boiler and the grey wire from the boiler connected by chocolate block to the brown wire to the pump. (the switched live to the boiler is now black instead of brown previously)

Should there have been any other changes or links cut etc.

JB Wiring after New Boiler.jpg
 
I have been doing some more checking and reading various Honeywell documents.

Should the grey wire from the boiler that has been put into the chocolate block go into the boiler P/L terminal in the photo above, and the brown wire it was connected to, go back into the pump L terminal above. Also, should link 6 be cut.
 
I would ask them to rewire it in a normal wiring centre as it could be that one of the links that was cut originally should be whole again either that or just get them to start from scratch
 
Last edited:
I am going by the Honeywell diagram I have attached which says to do so in Note 4, now I am no expert so you could be correct
View attachment 29040


But only if your boiler requires pump overrun, it basically means that the pump runs for a short period after the heating is turned off... to take away any hot water from boiling and damaging your heat exchanger ...
 
I would ask them to rewire it in a normal wiring centre as it could be that one of the links that was cut originally should be whole again either that or just get them to start from scratch

According to the Honeywell info the correct links were cut and the only one different could be the link 6 that I mentioned
 
According to the Honeywell info the correct links were cut and the only one different could be the link 6 that I mentioned

But only if your boiler requires pump overrun, it basically means that the pump runs for a short period after the heating is turned off... to take away any hot water from boiling and damaging your heat exchange.
 
But only if your boiler requires pump overrun, it basically means that the pump runs for a short period after the heating is turned off... to take away any hot water from boiling and damaging your heat exchange.

The boiler is a Worcester 18Ri which does require pump overrun
 
According to the Honeywell instructions, boilers which require pump overrun the links 4,5&6 should be cut and the wires ( boiler = p/l ) should be connected into the terminal as well as the ( pump = l ) should be connected to the pump terminal.
 
The boiler is a Worcester 18Ri which does require pump overrun


If it requires then link 6 should be cut and wires should be connected into the terminals as shown on your previous Honeywell instructions.
 
According to the Honeywell instructions, boilers which require pump overrun the links 4,5&6 should be cut and the wires ( boiler = p/l ) should be connected into the terminal as well as the ( pump = l ) should be connected to the pump terminal.

That is what I said in post 8, I was checking to make sure i was correct
 
The pump, cylinder stat and the diverter valve are supplied pre-wired that's the dot line in your diagram.
 
All you need is a decent heating engineer as the system you have got is not complicated but may be causing confusion to folk who have looked at it since its been modified
 
he has a hive for controlling the system so something is wrong either with the wiring or the hive programming
 
But, if you do not feel confident enough then I would suggest get a professional electrician out.
 
You don't need to cut link 6. The pump live is wired direct to the boiler as the PCB in the boiler controls the overrun on that boiler.
It will be a control issue. You just need someone to spend a little time going over the wiring to check the controls.
 
You don't need to cut link 6. The pump live is wired direct to the boiler as the PCB in the boiler controls the overrun on that boiler.
It will be a control issue. You just need someone to spend a little time going over the wiring to check the controls.

Is that the correct way to not use the terminals and connect the pump l to boiler p/l ? I am just wondering if you cannot use the terminals and cut link 6
 
You don't need to cut link 6. The pump live is wired direct to the boiler as the PCB in the boiler controls the overrun on that boiler.
It will be a control issue. You just need someone to spend a little time going over the wiring to check the controls.

Is that the correct way to not use the terminals and connect the pump l to boiler p/l ? I am just wondering if you cannot use the terminals and cut link 6
 
Well I connected the wires as we said and cut the link 6 and it all seems to work ok including the pump overrun.

Now I have to see if that has cured the origional problem
 
It will work that way, but the boiler is now not installed to manufacturer's instructions so you could risk voiding the warranty. The pump should be wired directly to the boiler.
 
So does that mean that if you have a Honeywell Junction Box you cannot use it to connect the pump to the boiler.

Does that apply to using any junction box or does the pump have to be wired directly to the boiler
 
So does that mean that if you have a Honeywell Junction Box you cannot use it to connect the pump to the boiler.

Does that apply to using any junction box or does the pump have to be wired directly to the boiler

No just don't wire the pump live to the controller,

I'm sorry to say get a heating engy in to test things before you start ripping things out and re wiring them, when the problem might not be with that
 
Thanks for all your help with this.

Now put back to the old wiring.

Are there any recommended heating engineers in the Middlesbrough area, as so far i am not very impressed with the ones that have been round.
 
Thanks for all your help with this.

Now put back to the old wiring.

Are there any recommended heating engineers in the Middlesbrough area, as so far i am not very impressed with the ones that have been round.
 
Status
Not open for further replies.

Reply to Boiler not firing up sometimes in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, I have a Vailant EcoTec Boiler with a Megaflo. These are controlled by a Honeywell controller. I have one 3 port diverter, where one of the...
Replies
5
Views
292
Hi, Can I pick your brains? My boiler is often reluctant to start, sometimes it does, sometimes it seems that it will if the demand is from the...
Replies
19
Views
1K
I am having a problem with my main 24he boiler where the flame is constantly clicking on and off with the heating and when using hot water. Some...
Replies
6
Views
465
Hi, Over the past few months, my wife and I have noticed a constant pulsing sound throughout the house which is particularly noisy at night (this...
Replies
4
Views
686
Hi I have a Glow-worm back boiler which is giving me grief (I would have upgraded it by now but its a listed building and there's issues with...
Replies
6
Views
569
Back