Hi ppl,

Been to a customers this afternoon who have been experiencing problems with a Tiger 944 nat gas fire (stove).
It has been shutting off between 25-45 mins of being lit.

I was at the property for about 45 mins today checking various things. (inlet gas pressure, spillage, flue flow, oxypilot seems clean) fire was working fine until i packed all my kit away and then all of a sudden it just went off.
My customer said that it seems to happen when the boiler fires for heating or when someone opens a hot water outlet in the kitchen. Could this be coincidence? When the fire is on max gas inlet is 19.8 mbar when i fired the boiler it went down to 15.9 mbar and then steadied at 17 mbar. There was no spillage from the fire so i assume that ventilation isn't the problem.
Please excuse my basic drawing skills :).

Grant.JPG

Any suggestions please?
 
Have you checked the gas pressure at meter with all appliances running?
 
Have checked at meter with everything on and getting a reading of 18.2 mbar.
 
Call transco your gov is goosed. Oh and you might have a piping issue to stove as there is more than a mbar difference
 
Last edited:
Call transco your gov is goosed. Oh and you might have a piping issue to stove as there is more than a mbar difference

Thanks Atouchofgas i will give them a call when i am back there tomorrow and will see if i can find where the pipe is buried
 
A quick phone call to Transco, new meter was fitted and everything was sorted. Once again thank you.
 
Status
Not open for further replies.

Reply to Tiger 944 gas fire problems in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

All, Belfast, Northern Ireland. I am in a bit of a predicament. I have recently had a stove fitted in a chimney that had a disconnected and...
Replies
8
Views
1K
Hi, Can I pick your brains? My boiler is often reluctant to start, sometimes it does, sometimes it seems that it will if the demand is from the...
Replies
19
Views
1K
Hi. just had my probationary inspection. Most of the inspection went ok, apart from when the inspector asked me questions about gas fires and gas...
Replies
1
Views
841
Deleted member 120897
D
T
For about a year, my shower on a third floor is giving an on off gas smell sometimes after a shower and particularly in the morning not long after...
Replies
0
Views
430
Timmy1
T
I have a Viessmann Vitodens 222-F FS2B 26kW Storage Gas Boiler installed in 2014. The boiler has developed a problem recently where it short...
Replies
11
Views
2K
tinodj
T
Back
Top