Vaillant f75! Why bother we all no this one lol
What's that then? Don't work on valiants much.
Sorry missed that vaillant water pressure switches detect system pressure but also look for a 0.3 bar spike when the pump first kicks in, if it doesn't detect the spike thinks its a pump failure. So if the pumps running but getting f75 it's a blocked up pressure sensor. Bad position on the old models bottom left now top left on the new models.What's that then? Don't work on valiants much.
Sorry missed that vaillant water pressure switches detect system pressure but also look for a 0.3 bar spike when the pump first kicks in, if it doesn't detect the spike thinks its a pump failure. So if the pumps running but getting f75 it's a blocked up pressure sensor. Bad position on the old models bottom left now top left on the new models.
Changing one of these on Monday. Vaillant also say there is a filter that can be accessed and cleaned if you remove the rubber flow hose.
Glowworm ci. flexi hose to expansion vessel becomes kinked/blocked. Can usually fixed by giving a gentle squeeze with grips. PITA to replace.
Vaillant also say there is a filter that can be accessed and cleaned if you remove the rubber flow hose./QUOTE]The filter is is plastic and i have found it very hard to remove to clean. You are better of chucking the whole piece in a bucket of descaler.
Sorry missed that vaillant water pressure switches detect system pressure but also look for a 0.3 bar spike when the pump first kicks in, if it doesn't detect the spike thinks its a pump failure. So if the pumps running but getting f75 it's a blocked up pressure sensor. Bad position on the old models bottom left now top left on the new models.
Not really a fault as such but if you get asked to service a powermax (the older version 155 i think) take the burner gaskets with you and take the burner out. 9 times out of 10 the baffels in the heat exchanger have fallen to bits. They are about £17 each and there are 8 of them. (read in manuall you are suposed to replace the baffels every 2 years!) To remove once cracked you have to remove the sump and its a good few hours. Boiler classed as ID. The last 3 powermax boilers I have serviced have all resulted in winning new boiler changes.
Some of the guys in work checked with Powermax and they said that it's only NCS if the baffles aren't replaced as long as it isn't having an effect on combustion as they are only there to make the boiler a bit more efficient.
Also, you can sometimes get away with getting some condensate pipe and pushing it down on to the broken baffles at the bottom and then they'll pull out with the condensate, and you can get some really long nose pliers - never work on Powermax myself but the guys that do never seem to remove the sump to remove the old baffles.
Baxi Duo Tec/Potterton Promax Combi HE/Main Combi HE.
The serial numbers on these boilers all begin with 3 letters, followed by some numbers. The first 2 numbers are the build year, the second 2 the build week. The rest are random. So for example, a 28 HE A Duo Tec built in the 23 week of 2010 will be CAC1023XXXXXXX.
E119 - Low water pressure - Look for water leak coming from the water pressure switch of the diverter valve spindle. Also check and re-charge the vessel if required.
E133 - Failure to ignite - On older models built pre 2010, the ignition electrodes warp with the heat. They are now re-designed and much better. As a temporary fix, bent them back to make the gap the thickness of a pound coin.
E131 - (not listed) - Can be caused by a few things, sometimes if 2 fault codes come up together, such as E133 (failure to light) then E119 (low system pressure). It can also be caused by power failure during fault code.
E168 - Communication Error (not listed) - Most likely the PCB. Check the voltage and polarity before ordering a replacement.
E160 - Fan fault - Most of the time the fan is faulty. Check the loom to it. If you unplug the rectangular connector block, the fan should run at fall speed. If it doesn't, the fan is definitely goosed.
E20 - CH NTC sensor fault - Most likely needs replacing.
E50 - DHW NTC sensor fault - Most likely needs replacing. Could have been caused by a leak from the it's gasket. It can then corrode the sensor and the loom. This fault should still provide CH, just not DHW.
E110, E125 and E193 - Circulation fault - Pump could be seized or faulty. Also worth checking is the filter located in the return isolation valve behind the blanking cap or (if fitted) the integral filling loop.
Another fault that I have come across a couple of times is with boilers fitted with a verticle flue. The boiler doesn't provide enough hot water. When it fires up, the boiler becomes noisy and eventually goes out. Check the air intake side on the flue test point. If the CO rises the plastic flue exhaust could well be cracked. You'll have to pull the flue apart to check it.
The gas valve on these boilers also need adjusting, the CO2% should be 8.7 on high and 8.4 on low. Adjustment is made on the gas valve, the throttle for high is behind the blue cap, the offset on low is behind the brass flat headed cap.
To ACCESS SERVICE MODE - Turn the potentiometers to min, then turn the DHW potentiometer to the 3 o'clock position and back to the 12 o'clock position twice. The display should change briefly to SF, the LEDs flash and the boiler should light up. Turn the CH potentiometer to MAX (will display 00) for max fan speed and turn back down to MIN for minimum (will display 0). The temp should then cycle with the letter P. To get out of service mode, turn the DHW potentiometer to any position from 12 o'clock (min).
All greenstar boilers will pulse the fan on power up
No pulse. Fan usually broken
But I think you have to check for 240v on orange wire?
When I spoke with Baxi tech regarding the broken baffels they said it is classed as ID (not that they seem to know much themselves about these boilers) as they are there to slow the gasses down and it would effect the flame. I have replaced the baffels before by pulling them through the bottom but the time it takes to do that and the cost of them makes it seem like a bad choice in my opinion. Plus the fact that if you leave a powermax turned off for more than a day several components seem to fail at once for some reason.