Discuss Any ideas? Unreliable heating. in the Central Heating Forum area at PlumbersForums.net

Messages
46
Heating issues. Had new water pump fitted 3 weeks ago, new 3 port valve 18 months ago, boiler is 4 years old. I balanced radiators when new pump was installed and for 2 weeks or so the heating and hot water worked a treat. 3 days ago, woke up to find neither working properly. Timer comes on, boiler fires up but radiators downstairs not getting warm. Hot water not great. Balanced radiators again and all was fine but last two days every time I turn heating on nothing warm downstairs in spite of balanced radiators two days ago working fine. Pump does seem to work fine when it runs quietly but each time it starts there is a whirring noise and you know it won't work properly. Any ideas?
 
What’s the make of the pump ?
 
Is it this one?, if so post a photo of the LEDs while running.
1670786266161.png
 
Ups3 any red lights when running / having problems?
 
How many rad? and is it a sealed or open vent system with a Feed&Expansion (small) Tank in the attic.
If a sealed system ensure that the system pressure is 1.5bar cold.
If a OV system, present setting of CC3 at 6.4M is too high IMO and can cause air ingress.
Suggest, in either case, c/o to constant pressure setting 2, CP2 which is 4.5M.
Press the setting button for ~ 3 secs until the yellow LED illuminates at the far right, then briefly press the button until the green LED and the yelloe LED next to it are also illuminated, you are now on CP2 at a constant 4.5M head.

(Also, these pumps have had more than their "fair" share of failures.)
 
How many rad? and is it a sealed or open vent system with a Feed&Expansion (small) Tank in the attic.
If a sealed system ensure that the system pressure is 1.5bar cold.
If a OV system, present setting of CC3 at 6.4M is too high IMO and can cause air ingress.
Suggest, in either case, c/o to constant pressure setting 2, CP2 which is 4.5M.
Press the setting button for ~ 3 secs until the yellow LED illuminates at the far right, then briefly press the button until the green LED and the yelloe LED next to it are also illuminated, you are now on CP2 at a constant 4.5M head.

(Also, these pumps have had more than their "fair" share of failures.)
I think it is an open vent system. I have no way of setting system pressure and I know there is a small tank in the attic. We have 5 rads upstairs and 7 downstairs. I will follow your instructions and see how we get on. Cheers.
 
Pumps set too high and probably drawing air in, causing your downstairs circuit to air lock. The new Grunfos ones are more powerful than the old, you'll probably easily get away with I or II on the new model.
Thank you. Lights now flashing like in screenshot on Constant pressure 2. Should I restart system to deal with airlock downstairs?
Screenshot_20221211-200810.png
 
Thank you. Lights now flashing like in screenshot on Constant pressure 2. Should I restart system to deal with airlock downstairs?View attachment 79951
Bleed any rads. Turn HW on, on it's own. Let it circulate round the HW system. When Hot and returning, turn HW off and CH on. Let upstairs rads get hot, when they're hot turn them all off and it should force it through to downstairs.

See how you go on 2, if it keeps airlocking you may need to turn it down to 1.
 
When you have done the above go up to the attic and get someone to stop the boiler and watch and see if any spurt of water from the vent when the pump stops probably a few minutes after switching off the boiler, then get them to restart the boiler/pump and watch again for any pump over.
 
Bleed any rads. Turn HW on, on it's own. Let it circulate round the HW system. When Hot and returning, turn HW off and CH on. Let upstairs rads get hot, when they're hot turn them all off and it should force it through to downstairs.

See how you go on 2, if it keeps airlocking you may need to turn it down to 1.
Thanks to both of you. Issue now sorted. You have been a massive help!!!
 
Glad you are sorted.
Some OV systems with the traditional V,C,P system still have problems with air ingress with a pump head > than say 3.5/4.0M that may be required for systems with a large number of rads or small bore piping can be "cured" by changing the above to a combined vent and cold feed like my 50 year old system (from new), I could run my system with one rad and still get no carry over at a pump head of 6M.
 

Attachments

  • Combined Cold Feed & Vent. rev1.JPG
    Combined Cold Feed & Vent. rev1.JPG
    37.8 KB · Views: 13
Last edited:
Glad you are sorted.
Some OV systems with the traditional V,C,P system still have problems with air ingress with a pump head > than say 3.5/4.0M that may be required for systems with a large number of rads or small bore piping can be "cured" by changing the above to a combined vent and cold feed like my 50 year old system (from new), I could run my system with one rad and still get no carry over at a pump head of 6M.
Cheers. I am no plumber so much if that is like a different language. Sadly, it seems that as predicted CP2 might still be too much. Good heat last night, this morning but this evening after about 3 hours, I could hear a different 'tone' in the pump and once again the downstairs rads went cold. Trying to change to CP1 and go through same steps as last night. Bloody nightmare.
 
Its quite likely that you have a partial blockage where the cold feed joins the system, if you still have a problem at CP1 @ 3M then almost a certainty IMO. Any idea of the old pump (and setting).
 
I'd say speed 3 was running at; at least a 5M head, can you check the direction of flow on the UPS3, if your system is something like the attachment, then the arrow on the pump should be pointing downwards.
 

Attachments

  • VCP Rev0.jpg
    VCP Rev0.jpg
    656.8 KB · Views: 13
The pump was upside down so the picture I sent is after I have rotated it
What do you mean by upside down? the pump label etc may be upside down but all that matters is that the arrow on the pump body is pointing in the correct direction.
Your picture is only darkness.
 
What do you mean by upside down? the pump label etc may be upside down but all that matters is that the arrow on the pump body is pointing in the correct direction.
Your picture is only darkness.
The picture of the old pump (blue) is rotated. The writing on it was upside down. It was the pump installed when the house was built.
 
So, are you absolutely certain that the new pump is pumping in the same direction as the old one, ie, the arrow on the old pump was also pointing downwards??, Is you system as I showed above or can you post a photo of it?, its strange that you are getting problems at CP2 even though it is a bit high so CP1 may sort out the problem, was that system chemically cleaned or anything like that between pump changes?.
 
So, are you absolutely certain that the new pump is pumping in the same direction as the old one, ie, the arrow on the old pump was also pointing downwards??, Is you system as I showed above or can you post a photo of it?, its strange that you are getting problems at CP2 even though it is a bit high so CP1 may sort out the problem, was that system chemically cleaned or anything like that between pump changes?.
Screenshot_20221212-220258.png

This is the old pump and if it appears you will see what I mean by upside down. I don't have any other image so can only presume the British gas engineer who put the new one in ensured it is pumping on same direction. No chemical cleaning I am aware of.
 
Well you will have to be happy (ensured) that the UPS3 is pumping in the correct direction before taking any drastic or unnecessary action, if the pipe coming out of the bottom of the pump then goes to either a three way valve or to a number of valves (all/any of which will have a motor with a cable) then pump direction is downwards, if these valve(s) come off the top pipe then the pump must pump upwards.
 
Well you will have to be happy (ensured) that the UPS3 is pumping in the correct direction before taking any drastic or unnecessary action, if the pipe coming out of the bottom of the pump then goes to either a three way valve or to a number of valves (all/any of which will have a motor with a cable) then pump direction is downwards, if these valve(s) come off the top pipe then the pump must pump upwards.
Yes, that's where the 3 port valve is
 
so 3 port below pump and pump pumping downwards is correct, CP1 or just maybe PP2 next step??

WhT was happening when the pump was stopping as can't see it
 
Your old pump was probably a 6M Selectric (made in 2007) so the pump curves may look like this. If so then even speed 3 has a relatively low head of 2.5m at 0.7ms/hr and hopefully CP1 or PP3 will also not cause any pumpover problems.

1670917782263.png
 
Last edited:
so 3 port below pump and pump pumping downwards is correct, CP1 or just maybe PP2 next step??

WhT was happening when the pump was stopping as can't see it
The pump was making a very strange noise. The file I added was a video file.
Starting from scratch tonight. Photo of setup attached showing port valve etc. Going to try CP1 following the details posted on Sunday, starting with HW ON ETC.
PXL_20221213_184006839.jpg

Gary, getting a bit confused myself re arrow on pump, can you just confirm that (if) the pump is now pumping downwards then the engineer will then have turned the head through 180 deg and the arrow will be on the right hand side of the pump body, pointing downwards.

Assuming it was how is your system performing now?.
The arrow is downwards on the left side behind the cable socket. I can't see anything on the right hand side. Best photo I can take given the angle is here.
PXL_20221213_215740774.jpg
 
Not getting anywhere really. I had to leave heating on today as someone was home so it was on CP1 with all upstairs rads off so the living room rads were warm. The kitchen rads beyond those never really warmed up properly. Have tried to restart CP1 following the process I was asked to go through on Sunday evening but when I switch upstairs rads off there heat is not too hot downstairs with the last 2 or 3 on system almost getting nothing. Like i say I am not a plumber so have no knowledge at all but I know when it won't work just by noise of pump. When it is almost silent I know it will work but when it makes more noise it won't. I think I need to have the system cold to be able to try a proper CP1 or PP1 reset.
 
Not getting anywhere really. I had to leave heating on today as someone was home so it was on CP1 with all upstairs rads off so the living room rads were warm. The kitchen rads beyond those never really warmed up properly. Have tried to restart CP1 following the process I was asked to go through on Sunday evening but when I switch upstairs rads off there heat is not too hot downstairs with the last 2 or 3 on system almost getting nothing. Like i say I am not a plumber so have no knowledge at all but I know when it won't work just by noise of pump. When it is almost silent I know it will work but when it makes more noise it won't. I think I need to have the system cold to be able to try a proper CP1 or PP1 reset.
Got closer. Yes arrow on right is downwards.
PXL_20221213_220628339.jpg
 
Very strange allright, presume not something daft like the pump valves not opened fully, they look like gate valves so should be ~ 3 or 4 full turns from fully shut to fully open. There arn't too many things left, the pump was probably changed out without drain or partial system drain down, possible sludge build up but unlikely except the F&E tank was full of crap and drained down into the system. (if system drained)

The possibility of a faulty UPS3 still exists but if so unlikely that air would continue to build up, are you still venting air, you say all rads have been bled?.

CP1 at 3M should not cause any problems and is required for most systems of your size, my system runs at 3.5/3.6M with the (Wilo) pump set to a PP setting of 4.6M.
 
Very strange allright, presume not something daft like the pump valves not opened fully, they look like gate valves so should be ~ 3 or 4 full turns from fully shut to fully open. There arn't too many things left, the pump was probably changed out without drain or partial system drain down, possible sludge build up but unlikely except the F&E tank was full of crap and drained down into the system. (if system drained)

The possibility of a faulty UPS3 still exists but if so unlikely that air would continue to build up, are you still venting air, you say all rads have been bled?.

CP1 at 3M should not cause any problems and is required for most systems of your size, my system runs at 3.5/3.6M with the (Wilo) pump set to a PP setting of 4.6M.
What does venting air mean?
 
What does venting air mean?
Opening the vent screws and getting rid of any air in the rads. (Bleeding the rads)
John, should the gate valve directly under the pump be fully open? The middle of the three you can see in the photo I uploaded yesterday.
Not sure about the one with the red handwheel (you would have to trace it but let it be just now whatever its opening is).

The two brass valves, immediately above and below the pump MUST be fully open, get a adjustable spanner or even a pliers and try shutting first, if they are open then you should get 3 to 4 turns to shut, then immediately reopen, ie they must be ~ 3 to 4 full turns open from fully shut.
 
Last edited:
Opening the vent screws and getting rid of any air in the rads. (Bleeding the rads)

Not sure about the one with the red handwheel (you would have to trace it but let it be just now whatever its opening is).

The two brass valves, immediately above and below the pump MUST be fully open, get a adjustable spanner or even a pliers and try shutting first, if they are open then you should get 3 to 4 turns to shut, then immediately reopen, ie they must be ~ 3 to 4 full turns open from fully shut.
Cheers. In work now so will try again when I get home late afternoon.
 
Opening the vent screws and getting rid of any air in the rads. (Bleeding the rads)

Not sure about the one with the red handwheel (you would have to trace it but let it be just now whatever its opening is).

The two brass valves, immediately above and below the pump MUST be fully open, get a adjustable spanner or even a pliers and try shutting first, if they are open then you should get 3 to 4 turns to shut, then immediately reopen, ie they must be ~ 3 to 4 full turns open from fully shut.
Yes, all rads are bled - doing it all the time. No air in them.
The way I got the CP2 to work on Sunday (bleed rads, turn on HW, run HW, turn off HW, turn on CH, when upstairs rads get hot, switch them off and pump heat downstairs) is failing on the last part with CP1 as only 3 or 4 of the 7 rads downstairs get the heat - should I switch all off apart from last one and rebalance the rads?
 
When you bled the rads on Sunday, how much water did you bleed off each?

If no air in them then pointless venting, except that you are getting some heat in them by actually bleeding off a few litres of water which means no circulation or circ pump defective, CP2 at 4.5M even with all rads open (no balancing) should circulate plenty of water to get all/most quite hot, you have another problem IMO.
When you come home and if you find that the pump valves are fully open (and probably are) then may have to check the circ pump.


That middle pipe seems to go into the bottom of the immersion heater.
probably the cold water supply to your HW cylinder.
 
Last edited:
If no air in them then pointless venting, except that you are getting some heat in them by actually bleeding off a few litres of water which means no circulation or circ pump defective, CP2 at 4.5M even with all rads open (no balancing) should circulate plenty of water to get all/most quite hot, you have another problem IMO.
When you come home and if you find that the pump valves are fully open (and probably are) then may have to check the circ pump.



probably the cold water supply to your HW cylinder.
Thanks John. I have bled the rads but not emptied them per se - when you say 'no circulation or corc pump defective' what else could cause the 'no circulation'? The weird thing is that on Sunday after I changed to CP2 all rads were hot, same Monday but then Monday night the downstairs rads went cold. So that must be an airlock? But there is no air in rads! Given that we have had heat i would guess the pump valves are fully open.
 

Reply to Any ideas? Unreliable heating. in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hi All, In Dec 2023 I had my annual boiler service and asked the plumber to change 2 radiator valves as the radiator in the toilet downstairs was...
Replies
7
Views
537
I have had a problem where 2 downstair radiators are not heating up the same as the rest of the radiators around the house, now previously i had...
Replies
2
Views
287
T
Hi We urgently need to get our h/w cylinder replaced because it's leaking. Our current system is oil boiler feeding underfloor downstairs...
Replies
2
Views
434
Oil boiler (now~15 years old) unvented system with 17 radiators. We moved in 5 years ago and I had to keep bleeding the same radiator. The bleed...
Replies
1
Views
284
Hi, I have a Vailant EcoTec Boiler with a Megaflo. These are controlled by a Honeywell controller. I have one 3 port diverter, where one of the...
Replies
5
Views
292