Another boiler suggestion post.

4 bed detached house built 20 years ago with cavity wall insulation and double glazing. 1 bathroom and separate ensuite shower. 2 adults and 1 child.

Cold water flow is 20l/m. 16 radiators but 6 are single panel. Already have Tado which supports OpenTherm.

Want to convert gravity fed system to a combi. Primarily to get rid of the airing cupboard which houses the hot water cylinder. We need this space to enlarge the bathroom. Also prefer on-demand hot water. Fully aware of the disadvantages of the combi.


Getting conflicting information from the gas engineers that came out to quote. Some quote 30kw boilers and way 35kw-40kw is overkill, some say I need to go for 35-40kw.

I am contemplating between these

Ideal Logic+ C35

DHW output 35kw
DHW flow rate 35C rise : 14.5l/m
CH output 70C min/max : 7.1kw -24.2kw
7 year warranty 10 years on heat exchanger

Ideal Logic Vogue Gen2 C40 or Vogue Max C40

DHW output 40kw
DHW flow rate 35C rise : 16.4l/m
CH output 70C min/max : 5.7kw-32.0kw
10 year warranty for Vogue and 12 for Vogue Max.

I think all 3 have stainless steel heat exchangers and support OpenTherm.


I am leaning towards the Vogues as they provide better flow rate and can modulate to lower CH output so assuming will be cheaper to run?

Are there any major disadvantages going for 40kw Vogue?
Too much for our needs ?
I am happy to pay a bit more and get a really good shower.
Is 14l/m Vs 16l/m that noticeable?
Or 7l/m Vs 8l/m when running 2 showers or taps at the same time (not very often).

Thanks in advance.
 
Why not start with the basics and calculate your heat demand. Look for ways in which the heat loss can be reduced (insulation) then re-calculate. Designing for maximum need (@ -2 degrees) has to be realistic...do you often have -2 where you live and for how many days each year (met office have the data).
So lets say your average working load is 20kw, min 15kw and max 25kw then a boiler that can modulate down to 15kw and max out at 25kw would be fine. So the question is not how far can it modulate, the question is how far do I need it to modulate.

Hot water then is another issue. The boiler output @ 16l/m is significant flow by any standards but can the boiler have the full 20l/min cold input at all times (priority) and can it raise this volume of cold quickly enough to give 16l/min @ say 48 degrees( to allow for mixing).
Do you believe that having 2 showers running simultaneously is simply a matter of dividing the theoretical output of the boiler by 2?

Modulation prevents the stop start but that is not what saves money. Loosing less heat is what saves money by using less gas.
Do you stop start the heating cycle as well? How much heat is used to heat the fabric of the building before heating the room?
Heat to 21 degrees for x hours per day and then allow to cool to y degrees before starting again. Do the math, which is the better option.
You also need to consider the benefits of a constant temp throughout the house (I live in a house, not a series of interconnected rooms) as this helps with humidity and you can establish comfort levels @ 18-19 degrees rather than 21-22. That reduces gas consumption.
If you want to be able to have lower temp circulating in the system, does your choice of boiler allow for the flow to be controlled? Is this on offer? If you can opt for flow temp then lower the temp and upsize the rads then leave it running 24/7.
This 24/7 works great with flow temp provided you have external temperature sensing as it needs to operate on automatic. Room thermometers won't work in this situation
 
You won’t get a combi running two outlets either unvented cylinder or Viessmann 222
 
Results from temp and humidity sensors around the house. 2,500 sq feet property. No room thermostats, no heating zones. Wall radiator heating on Heating 24/7. Perfect heating and humidity.
 

Attachments

  • IMG_3062.JPG
    IMG_3062.JPG
    329.4 KB · Views: 3
Not really relevant to the question asked though?
The question posed related to boiler selection
I proposed using maths to create the perfect heating profile and to use that as the start point then find a boiler to suit
I them posted a picture to demonstrate that perfect heating profiles can be achieved through maths
Which part does not related to the question?
 
The question posed related to boiler selection
I proposed using maths to create the perfect heating profile and to use that as the start point then find a boiler to suit
I them posted a picture to demonstrate that perfect heating profiles can be achieved through maths
Which part does not related to the question?
The question was about 3 specific combi boilers. You are referring to your property and how you use your heating which could be totally different
 
perhaps this is a perfect example of why the UK heating industry is considered the worlds most inefficient and outdated. Plumbers can't understand the vital importance of first principles and instead have fashion parades
 
Thanks for the input everyone.
I think our property is well insulated and I do understand the importance of preventing heat loss. But very interesting insights @hometech

To be honest I am not that concerned about the heating, it's the water flow rates that am more worried about. I am sure if I spend time working out the requirements for heat properly I will end up with a small number and a combi most suited for this will have low DHW output and flow rate. So I think I have to overspec anyways.
 
Looks like the Vogue is a much better model so the choice now is probably between the 32kw with 13l/min and 40kw with 16l/m.

How noticeable will this difference of 3l/m be in the real world? I have no way of gauging this.

Regarding modulation, from what I understand, as my smart thermostat (Tado) tries to reach desired temperature in the room it will taper the demand from the boiler as it gets closer to reaching that temperature as not to "overshoot". My thinking is that the better the boiler's modulation the more granular this tapering can be and less gas used and wasted (overshooting).

So if the boiler spec says

Min/max 4.6 - 26.0kW

Min/max 5.7 - 32.0kW

Are there levels within those ranges? If so, how many?
Or is that not how it works?
 
Have you considered a Viessmann 111 wall mounted storage combi? Flow rate of up to 18 lpm and better modulation than the boilers mentioned above.
 
Have you considered a Viessmann 111 wall mounted storage combi? Flow rate of up to 18 lpm and better modulation than the boilers mentioned above.
No, looks very interesting! What are the disadvantages of a storage combi? Can in bypass the tank and provide DHW on demand if the water in the tank isn't warm enough? Does it constantly keep the water in the tank hot?
 
No, looks very interesting! What are the disadvantages of a storage combi? Can in bypass the tank and provide DHW on demand if the water in the tank isn't warm enough? Does it constantly keep the water in the tank hot?

Boiler does it automatically
 
You can’t range rate the central heating output on Ideal boilers.
They start high and modulate down as the return begins to warm up.
You can easily add weather compensation and load compensation with Ideals own controls or opentherm controls.
 
Get the vogue max with a 12 year warranty

You size an open vent or system boiler output to the size of the property. With a combi boiler, you buy more KW's to give you more hot water output.

Dont get a viessmann 111 or 222. if you are desperate to run 2 showers at the same time or run a bath, go the traditional route of a boiler and cylinder.

A combi is a compromise. its was designed to save space for small spaces. if you have more than 1 bathroom, then usually a combi is not for you.
 
Looks like the Vogue is a much better model so the choice now is probably between the 32kw with 13l/min and 40kw with 16l/m.

How noticeable will this difference of 3l/m be in the real world? I have no way of gauging this.

Regarding modulation, from what I understand, as my smart thermostat (Tado) tries to reach desired temperature in the room it will taper the demand from the boiler as it gets closer to reaching that temperature as not to "overshoot". My thinking is that the better the boiler's modulation the more granular this tapering can be and less gas used and wasted (overshooting).

So if the boiler spec says

Min/max 4.6 - 26.0kW

Min/max 5.7 - 32.0kW

Are there levels within those ranges? If so, how many?
Or is that not how it works?
Did you go for the Vogue 40kw or 32kw in the end?

I'm in a very similar position as I have to replace my combi and have been recommended a Vogue and would prefer not to drop DHW down from our current 14.5l/min (with our old Vaillant that needs replacing).
 
Did you go for the Vogue 40kw or 32kw in the end?

I'm in a very similar position as I have to replace my combi and have been recommended a Vogue and would prefer not to drop DHW down from our current 14.5l/min (with our old Vaillant that needs replacing).

No, decided to go for Viessmann Vitodens 100-W 35kW Combi as it can modulate down to 3.2kw
 

Reply to Ideal Logic+ 35 Vs Vogue 40kw in the Gas Engineers Forum area at PlumbersForums.net

Similar plumbing topics

We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
499
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
261
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
367
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to run the water line underneath. There are existing drain (and who knows what) pipes running along the same wall so I'm nervous about digging too far...
Replies
6
Views
244
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
265
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock