Would need some advice if I could replace Newlec Economy to OP Ecosave Timer control for “Unvented Cylinder Megaflo Water heater”

As the current Newlec Economy timer control limits to heat up full tank of water during midnight only( one time a day. )

OP Ecosave Timer control allows to set 2-3 different time slot to heat up full tank hot water by moving the tappets. It is more flexible to have hot water in different time period.
But I do not know if this OP Ecosave is suitable for Unvented Cylinder. Your advice is appreciated. Thank you.
 

Attachments

  • Timer 2 to set different time slot.png
    Timer 2 to set different time slot.png
    726.8 KB · Views: 22
  • A B timer.png
    A B timer.png
    678.4 KB · Views: 20
  • 1A.png
    1A.png
    146.7 KB · Views: 20
I'm not familiar with the 'OP Ecosave'. Personally, I'd replace that programmer with a Horstmann Electronic 7 unit. I've always been happy with Horstmann products and quality.
 
The older timer you have is made by Horstmann. The one Chuck suggests would be a good replacement, and has electronic controls rather than a mechanical clock, so is more up-to-date.
However, the 'Optimum Ecosave' timer you suggest would work OK as a replacement - internally it does the same job as your existing one, by switching the single incoming mains supply on either with the timeswitch (to the lower immersion) or if you operate the boost button (to the upper immersion).
Both, and indeed other options, would be suitable for your cylinder.
It will require an electrician to isolate and disconnect the cables from the backplate of your present timer, affix and reconnect a new backplate for the Optimum timer, and test it.
If you chose a Horstmann Electronic 7 timer, I believe it would would be a drop-in replacement in the wall box you presently have, so none of the fixed wiring would need to be touched, just the timer module connected to the terminals within the existing box.

Assuming you are on a Economy 7 tariff with your electricity supplier, if you set 'on' times outside the E7 hours (midnight? to 7am?), you will be paying daytime rate for the electricity - approximately three times more costly!
That is why the timeclock is set to heat the whole tank overnight, leaving you to boost it if needed during the day.
If you are constantly running out of hot water during the day, either the timer is not set to be on long enough over night to heat the tank fully (unlikely), or your tank is not big enough to meet your needs! Though fixing the latter is no doubt even more costly than paying for daytime electricity 🙂
 
The older timer you have is made by Horstmann. The one Chuck suggests would be a good replacement, and has electronic controls rather than a mechanical clock, so is more up-to-date. However, the 'Optimum Ecosave' timer you suggest would work OK as a replacement - internally it does the same job as your existing one, by switching the single incoming mains supply on either with the timeswitch (to the lower immersion) or if you operate the boost button (to the upper immersion). Both, and indeed other options, would be suitable for your cylinder. It will require an electrician to isolate and disconnect the cables from the backplate of your present timer, affix and reconnect a new backplate for the Optimum timer, and test it. If you chose a Horstmann Electronic 7 timer, I believe it would would be a drop-in replacement in the wall box you presently have, so none of the fixed wiring would need to be touched, just the timer module connected to the terminals within the existing box. Assuming you are on a Economy 7 tariff with your electricity supplier, if you set 'on' times outside the E7 hours (midnight? to 7am?), you will be paying daytime rate for the electricity - approximately three times more costly! That is why the timeclock is set to heat the whole tank overnight, leaving you to boost it if needed during the day. If you are constantly running out of hot water during the day, either the timer is not set to be on long enough over night to heat the tank fully (unlikely), or your tank is not big enough to meet your needs! Though fixing the latter is no doubt even more costly than paying for daytime electricity 🙂
The older timer you have is made by Horstmann. The one Chuck suggests would be a good replacement, and has electronic controls rather than a mechanical clock, so is more up-to-date. However, the 'Optimum Ecosave' timer you suggest would work OK as a replacement - internally it does the same job as your existing one, by switching the single incoming mains supply on either with the timeswitch (to the lower immersion) or if you operate the boost button (to the upper immersion). Both, and indeed other options, would be suitable for your cylinder. It will require an electrician to isolate and disconnect the cables from the backplate of your present timer, affix and reconnect a new backplate for the Optimum timer, and test it. If you chose a Horstmann Electronic 7 timer, I believe it would would be a drop-in replacement in the wall box you presently have, so none of the fixed wiring would need to be touched, just the timer module connected to the terminals within the existing box. Assuming you are on a Economy 7 tariff with your electricity supplier, if you set 'on' times outside the E7 hours (midnight? to 7am?), you will be paying daytime rate for the electricity - approximately three times more costly! That is why the timeclock is set to heat the whole tank overnight, leaving you to boost it if needed during the day. If you are constantly running out of hot water during the day, either the timer is not set to be on long enough over night to heat the tank fully (unlikely), or your tank is not big enough to meet your needs! Though fixing the latter is no doubt even more costly than paying for daytime electricity 🙂
 
Thank you very much for your advice and explanation.
Electronic timer control is not easy to do setting.
Yes, I would need extra full tank water in day time using the day rate /peak rate. So, the E7 timer I need should allow to set different /multi time slot of peak hour to heat up the water using the bottom element.
Boost mode can supply very little hot water as only heating by top element only.

Please advise if remove the timer switch is helpful. both elements can operate the same time and they can keep the water fully heated. Once the tank water is heated to temperature like 60C that triggers the the thermostat to shut off.
 
Please advise if remove the timer switch is helpful. both elements can operate the same time and they can keep the water fully heated. Once the tank water is heated to temperature like 60C that triggers the the thermostat to shut off.
The wiring in your house from the consumer unit (fuse box) to the timer, and the circuit breaker in the fuse box, will almost certainly not be capable of running both immersion heaters at once, so you cannot have both immersion heaters on at the same time, without having an electrician change the wiring to a more substantial cable and circuit breaker first.
(2 x 3kW heaters = 6kW = 26Amps. Your cable probably 2.5 sq mm rated at 20A and circuit breaker 16A, so not suitable)

The timers we have discussed are designed to run just one immersion heater at a time.
I would not recommend trying to run both heaters simultaneously.

You could have the timer removed and replaced with a fused spur connected just to the bottom immersion, and run that all the time (or as you need), but then you don't have the possibility of 'boost' (which may not matter)

If you prefer a mechanical time switch with tappets, which is easy to use, the one you suggested would be fine.
If you had that installed, you could set all the tappets to be on all the time if you need. Otherwise you might find setting a few on periods during the day will suffice.
Best wishes for resolving this.
 
Hi Baster, Thank you so much for your detailed information and explanation . It is very helpful. A mechanical time switch with tappets set with multi time slot will suit me best. Thanks again for your great advice.
 
The wiring in your house from the consumer unit (fuse box) to the timer, and the circuit breaker in the fuse box, will almost certainly not be capable of running both immersion heaters at once, so you cannot have both immersion heaters on at the same time, without having an electrician change the wiring to a more substantial cable and circuit breaker first.
(2 x 3kW heaters = 6kW = 26Amps. Your cable probably 2.5 sq mm rated at 20A and circuit breaker 16A, so not suitable)

The timers we have discussed are designed to run just one immersion heater at a time.
I would not recommend trying to run both heaters simultaneously.

You could have the timer removed and replaced with a fused spur connected just to the bottom immersion, and run that all the time (or as you need), but then you don't have the possibility of 'boost' (which may not matter)

If you prefer a mechanical time switch with tappets, which is easy to use, the one you suggested would be fine.
If you had that installed, you could set all the tappets to be on all the time if you need. Otherwise you might find setting a few on periods during the day will suffice.
Best wishes for resolving this.
Hi Baster, Thank you so much for your detailed information and explanation . It is very helpful. A mechanical time switch with tappets set with multi time slot will suit me best. Thanks again for your great advice.
 

Reply to advice on timer control for Unvented Cylinder in the USA area at PlumbersForums.net

Similar plumbing topics

The left rear floor corner is highest (the shower pan touches/sits on the floor), sloping down diagonally to the front right corner (lowest). The front right corner shim is 5/8", the left front corner is 3/8" shimmed, with shorter shims under left middle and right rear corner. The pan perimeters...
Replies
5
Views
130
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
276
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
323
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
125
Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to space for servicing and changing parts if ever needing to. I am finding my decision rather hard due to the different clearances on flue runs and cupboards...
Replies
9
Views
188
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock