My Son has a problem with rads not getting hot and we think it may be caused by either the flow or return pipework. He has 2 rad on his living room one is hot and one is cold. Fig 1 is how the pipe work is currently, both the flow and return have tee connectors feeding the rads, the first rad is hot and the flow pipe to the second is hot but not the rad. The return pipe from the first rad is hot up to the tee and of course the return pipe from the second rad is cold. Am I correct in thinking that the flow and return pipes should be staggered as shown in fig 2 or is it only the return that this would affect as the flow does appear to be ok. Your advice would be appreciated.
Roy
 

Attachments

  • 69C78217-BC71-4C1D-9A89-D6EDD0E7363E.jpeg
    69C78217-BC71-4C1D-9A89-D6EDD0E7363E.jpeg
    344.1 KB · Views: 18
These have been added as he has had some building work. The first rad get hot but the other 2 are only warm, if that, so they are getting hot water but it appears not to be flowing.
 
Ok. It could simply be the radiators need balancing, which honestly should have been done by the installer.
What size are these radiators and the pipework feeding them? You could have an underflow proplem, or perhaps the boiler is now not man enough for the job.
First approach would be to try and balance them.
 
Ok. It could simply be the radiators need balancing, which honestly should have been done by the installer.
What size are these radiators and the pipework feeding them? You could have an underflow proplem, or perhaps the boiler is now not man enough for the job.
First approach would be to try and balance them.
Ok, I’ll try balancing the rads, the rad are tall rads about 400mm wide x 1500mm high the pipework is 15mm. I assume you don’t think it is a problem with the flow at the tee in the pipework?
 
Ok, I’ll try balancing the rads, the rad are tall rads about 400mm wide x 1500mm high the pipework is 15mm. I assume you don’t think it is a problem with the flow at the tee in the pipework?

At the moment I don't think so. It's much more likely to be a balancing issue but there are other possibilities. First try and balance the system so you have equal flow to all radiators. If you're unsure on how to do this there are discriptions on here or videos online, pretty straight forward though 👍
 
If it is all 15mm then it will work to a fashion as long as pump head sufficient except that piping is cross connected but I suppose it should be 22mm with short 15mm rad tails?.
I have two bedroom rads connected some what like that, no problems, pump head with all rads (10) in service is 3M.
 
Yeah,
At the moment I don't think so. It's much more likely to be a balancing issue but there are other possibilities. First try and balance the system so you have equal flow to all radiators. If you're unsure on how to do this there are discriptions on here or videos online, pretty straight forward though 👍
 
Ok, I’ll try balancing the rads, the rad are tall rads about 400mm wide x 1500mm high the pipework is 15mm. I assume you don’t think it is a problem with the flow at the tee in the pipework?

Ok, I’ll try balancing the rads, the rad are tall rads about 400mm wide x 1500mm high the pipework is 15mm. I assume you don’t think it is a problem with the flow at the tee in the pipework?
The tall rads (5 FT high??) are probably "1/2" the problem, are they fitted with baffles with the flow/return connected at the right ends?.
 
Maybe shut one valve on all rads except these two, ensure their valves fully open, (if downstairs can be zoned off just get this zone isolated by turning downstairs stat down) fire up the boiler and see if if the rads start heating up, even if they are being short circuited the flow and return should get hot, might tell you something.
 
Maybe shut one valve on all rads except these two, ensure their valves fully open, (if downstairs can be zoned off just get this zone isolated by turning downstairs stat down) fire up the boiler and see if if the rads start heating up, even if they are being short circuited the flow and return should get hot, might tell you something.
That’s great, thanks. I’ll give it a go.
 
Hi
I have spoken to the rad supplier and they say that the rad are not supplied with baffles and do not need them. I have returned to my Sons today and turned all the rads upstairs off, the rads downstairs heated up, I then balanced all the rads and they are now all hot as required. Many thanks for all your help.
 

Reply to Flow and no return in the USA area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
139
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
252
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
339
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
137
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock