Boiler and cooker will fire up initially however when temperature hit neither will reignite, they go to lockout
You can hear them switch and the solenoids switch but the fan pre purge does not engage, if I continually turn the boiler temperature switch on and off eventually the fan kicks in and everything fires up? I’ve swamped solenoids over, photocells, and control boxes, cleaned the fan blades etc, any ideas?
[automerge]1577463008[/automerge]
Boiler and cooker will fire up initially however when temperature hit neither will reignite, they go to lockout
You can hear them switch and the solenoids switch but the fan pre purge does not engage, if I continually turn the boiler temperature switch on and off eventually the fan kicks in and everything fires up? I’ve swamped solenoids over, photocells, and control boxes, cleaned the fan blades etc, any ideas?
Should also mention this has occurred over the past few weeks before that it was working perfect.
 
Are both burners not igniting? These cookers have two motors, one for cooker fan and oil pump the other for boiler fan, are both not working?
 
Are both burners not igniting? These cookers have two motors, one for cooker fan and oil pump the other for boiler fan, are both not working?
Both are igniting when I initially get them going, they work perfect up to the desired temperature but when they try to engage a while after, you can hear a switch, a buzz then the solenoids switching but no fan, then lockout.
[automerge]1577474321[/automerge]
Both are igniting when I initially get them going, they work perfect up to the desired temperature but when they try to engage a while after, you can hear a switch, a buzz then the solenoids switching but no fan, then lockout.
Also if I turn the boiler or cooker dial setting on and of several times it does fire up and goes on to reach temperature, and the lockout cycle continues...
 
Last edited:
Can you send me a picture of burners please.
It sounds like a motor is not rotating
I’ve taken another look over all fittings etc and found the capacitor loose and very sticky around the top and the connectors, after trawling various forums I found a post describing almost the same symptoms as mine, that was a failing capacitor. As mine is sticky/leaking and negligible in cost I will replace Monday along with blast tube fire seals (mine have seen better days)
 

Attachments

  • image.jpg
    image.jpg
    116.6 KB · Views: 18
Yes everything you've said would suggest it's the capacitor. Do you have a multimetre that can read capacitance? While replacing the cap I would check for tight spots on fuel pump and motor at the same time.

Edit: multiple burners have been used for these cookers I believe and my original comment about two motors is not relevant for the ecoflam replacement
 
Last edited:
Yes everything you've said would suggest it's the capacitor. Do you have a multimetre that can read capacitance? While replacing the cap I would check for tight spots on fuel pump and motor at the same time.
I’ve got test equipment, I’ll take a measurement to confirm, any idea what the reading should be ?
I’ll try and pick one up Monday and hope it works. I’ll post an update as soon as it’s done. I hope it’s that’s simple!
 
Have a look on the capacitor and it should tell you the microfarad rating, symbol uF. Probably 4.5 or 5 uF. A healthy cap is anything above 70% of original value. If you said there is signs of dielectric material leaking then I suspect its value will be lower than 70%. To be safe short the cap out before touching using a metal shafted, handle insulated screwdriver just to make sure, although the current from a cap is a reaction to the change in voltage across it and should be discharged. You might need suitably rated connectors to reattach the new one.
 
SJB060685, I had to order the capacitor as I couldn't find one locally (Christmas and all!). It arrived this lunchtime and fitted this afternoon, I am happy to report since firing it back up approximately 3 hours ago it hasn't missed a beat. I hope this continues, I will also get a spare capacitor in stock just incase!!!
At least now im not constantly pressing the reset, so much spare time now...
Thanks again for your assistanace
hello mate, do you have the details of the Cap you bought for the Rayburn. serial, etc. I have the same issue and will follow your lead here. cheers
 
Have a look on the capacitor and it should tell you the microfarad rating, symbol uF. Probably 4.5 or 5 uF. A healthy cap is anything above 70% of original value. If you said there is signs of dielectric material leaking then I suspect its value will be lower than 70%. To be safe short the cap out before touching using a metal shafted, handle insulated screwdriver just to make sure, although the current from a cap is a reaction to the change in voltage across it and should be discharged. You might need suitably rated connectors to reattach the new one.
SJB060685, I had to order the capacitor as I couldn't find one locally (Christmas and all!). It arrived this lunchtime and fitted this afternoon, I am happy to report since firing it back up approximately 3 hours ago it hasn't missed a beat. I hope this continues, I will also get a spare capacitor in stock just incase!!!
At least now im not constantly pressing the reset, so much spare time now...
Thanks again for your assistanace
 
That's good to know my friend. Yes get a couple caps as spare and store in a safe dry space.
Don't get into the habit of constantly pressing the reset button everytime a lockout occurs. It's not good for the burner components trying to constantly start and fail, any problems ask on here.
If you felt compelled to google it you'll find information on how a capacitor works so you have a better understanding, or I can tell you.
Well done and happy new year 🙂
 

Reply to Rayburn 499k intermittent lockout in the USA area at PlumbersForums.net

Similar plumbing topics

We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
450
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
257
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
231
Hi all, I'm installing a concrete patio out back. By the wall under the kitchen sink I have an existing P-Trap gully for the grey water from the sink, dishwasher, washing machine etc. When I pour the concrete there won't be any chance to dig it up anymore. From my own research I get the...
Replies
0
Views
93
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
323
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock