Discuss Very very Hight Co2 ppm old Myson velarie... Help in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Messages
181
Got called out this morning to a lock out boiler. . Myson Valerie 50/70 At first look it sounded like motor stuck. I checked fan moving freely, pump a little resistance but seemed ok. When fan removed it started slow but ok. my thoughts were capacitor. original one was 3UF. I had an old 3uf and same struggle to start fan. I had a 4.5UF . I put that in and stared no problem. Then client asks if i can service it. I give chamber a goo clean etc . New nozzzle . I have no manufacturers guide so previous plumbers service was 0.60 / 80 deg/ EH . so copied that. Put pressure tester on pump and pressure stuck on 90 psi. When I tried to adjusted it it leaked from the pressure adjuster, and wouldnt move from 90 psi (bfp21 l3). So off to merchant new pump. changed pump . pressure set at 115psi (as shown in previous plumbers test sheet).
Done smoke test about a 2. added a bit air to get a 1 smoke test. then put analyzer in and COPPM started shooting up 6-700++ I pulled probe out quick. ..
I then checked baffles and all ok . changed the nozzle for a 0.5/ 60/ES
and same again. I pressed save an analyzer before pulling out and get 12.2 02, 6.5 %co2 , 810ppm, flue temp 127 deg, Exess air 140%. The air intake is almost closed..
Does the capacitor have any influence on the fan speed or is it just a kick start?,, could too much air push co ppm up that high. ?
Any one have a recommended nozzle size for this boiler as a start.?
I then switched boiler off and told client not to use until sorted and safe.
Any ideas where I went wrong..?
Thanks
 
not sure before my time. Could not see any names it is Orange.. looks same as this pic

myson valarie.jpg
 
I suspect that capacitor is a "run" capacitor rather than a start capacitor, if it is different than yes it can affect its performance, always making it worse. Your readings are at least in the "zone" apart from CO, lol so i suspect its more of a tweak to get it acceptable. Try the right size cap first, i dont do oil.... is that temp in the range ? as i would have expected north of 150 degress.
 
temp is a bit low on 130 on quick test test then 180. would expect 210 +/-
how do you tell if you have or can order a run capacitor or start capacitor... I suspected the fan was running faster with the new capacitor, but then I thought it was new pump with less resistance.
 
That's out of the instalation manual . I tried to upload but it's through GIW ( gas installers workmate) an app I use for boiler manuals but it won't let me . Hope the pic helps
 
I have the manual for the Myson Velaire boilers.
That burner is the old Electro oil Swedish burner and is a superb burner.
It should be easy to set up.
I assume the nozzle assembly has not been tampered with?
You either have a faulty new nozzle (unlikely) or the motor is knackered.
The capacitor should not make any difference to that motor functioning once it starts.
 
Thanks Kris . Ill cherish that. Ill up pressure to start with..

You don’t need to up the oil pressure to achieve combustion on that burner.
100 psi will even be fine, although it probably should be 120 at least.
Something else is badly wrong.
Edit, - 150 psi is too much, despite it being on an old specification that Kris has kindly put on.
 
not sure before my time. Could not see any names it is Orange.. looks same as this pic

View attachment 36172

Just suddenly realised you said burner is orange in colour!
The air “door” on the orange burners is a round piece of metal band that is adjustable by a bolt and is a stupid idea because it can block with dust where it gradually tightens.
 
Yes and a thin threaded adjustment shaft to adjust with. I think im going to order 3uf capacitor and have another look another look Monday. Just feel bad about leaving with no heat..
 
I have the manual for the Myson Velaire boilers.
That burner is the old Electro oil Swedish burner and is a superb burner.
It should be easy to set up.
I assume the nozzle assembly has not been tampered with?
You either have a faulty new nozzle (unlikely) or the motor is knackered.
The capacitor should not make any difference to that motor functioning once it starts.
If the pump is knackered would it not spin less or could it spin more. The client says it is a lot quieter now. And it does sound ok. Is it normal for start up sequence to be.. fan spark then at start 4 second later coil and ignition. Aftet 10 seconds electrodes go off. The nozzel sits about 4mm below blast tube.
 
The capacitor is "tuned" to the windings of the motor. Its the way you get the right phase of magnetic field to make the motor turn. I would always replace with exactly the same spec of capacity, including material type and voltage spec. Its not going to run faster on full load but may run more erractic. When you close off the air it reduces the load on the fan, if you open the air to max, that will give you a better idea if the fan can work OK. Its not a huge difference in size of cap, but i would not do it as it may causes premature fan failure later down the line. Hope this helps.
The reason i believe its a run capacitor as its very low in value, start capacitors are much much bigger, plus a fan has so little load at rest that it can start without a start cap. I order Caps from RS components, they have loads of them
 
The capacitor is "tuned" to the windings of the motor. Its the way you get the right phase of magnetic field to make the motor turn. I would always replace with exactly the same spec of capacity, including material type and voltage spec. Its not going to run faster on full load but may run more erractic. When you close off the air it reduces the load on the fan, if you open the air to max, that will give you a better idea if the fan can work OK. Its not a huge difference in size of cap, but i would not do it as it may causes premature fan failure later down the line. Hope this helps.
The reason i believe its a run capacitor as its very low in value, start capacitors are much much bigger, plus a fan has so little load at rest that it can start without a start cap. I order Caps from RS components, they have loads of them

I haven’t much of an idea about motor types, as not a spark, but all I can add to that is those motors on the burner can be started by hand and will work fine until they have to stop and start again.
The OP said he changed the oil pump, so I assume the motor might be faulty and is very little money (comes complete with capacitor)
But I think the air is set too high and that is the first thing to check.
On those burners the air should be shut down to lowest numbers of approx 2 or below I think.
 
The nozzle assembly on these burners. Do they have an air diffuser? One i changed straight shaft with nozzle at end held central by a ring bracket off blast tube.

I would be concerned that the boiler is running quieter because that could mean it is sooting.
Your blast tube will be one piece type.
The air setting is far too high.
You should have used a smoke pump and lower the air setting until the boiler can still work ok still with close to zero smoke reading.
The CO2 should then be the reading to alter to achieve about 10% and no more than 11% on that
 
Dont know oil, closest to that for me is Riello burners and their knockoffs on NG
Sometimes i am so far out, i cannot even get it to start, he has it starting and has some readings so by trial and error he can tweak it. I was also think too much air but he has air closed right down, very confusing.
 
Dont know oil, closest to that for me is Riello burners and their knockoffs on NG
Sometimes i am so far out, i cannot even get it to start, he has it starting and has some readings so by trial and error he can tweak it. I was also think too much air but he has air closed right down, very confusing.

Yes, I think the OP has been thinking parts are faulty, rather than working on the air setting.
The air adjuster on those old orange coloured Electro oil burners is very misleading as it will look like it is near closed off with it being a metal band, but it actually could be still allowing a lot of air in.
The motor on oil burners turns a fan and the oil pump, so can be under load with oil pump as they can be tight to turn.
 
ahh didn't know its the same motor that runs the pump, still the cap value is so low it must be the run cap. single phase induction motors need a cap, some have a start cap and a run cap, some just a run cap.
 
Capacitors a start capacitor. Other than change a nozzle the black silver and orange ab burners I tend to leave alone.
Far too much air. Oil pressure about 115 psi maybe a touch higher.
Check the nozzle is in properly and tightened up.
 
I find the air settings on the aluminium band very sensitive to adjust. Like Best says they collect dust and fluff, make sure that's cleaned off. Could air be entering elsewhere?
There should be an air diffuser around the nozzle.
 
I find the air settings on the aluminium band very sensitive to adjust. Like Best says they collect dust and fluff, make sure that's cleaned off. Could air be entering elsewhere?
There should be an air diffuser around the nozzle.
Thanks. Im going to check to see if air getting in somewhere else, and clean band. Tell me more about the air diffuser. There definitely was not one there. How much difference does it make.? Is it something i can make without or do i need to make one up..washer.. what sort of diamiter . Would one work from another burner. .?
 
Just stumbled across this . Looks like my troublesome burner. Cant see a diffuser washer behind nozzle on it or am i mistaken. Is this the same burner for myson valarie ..?

Screenshot_20190106-104505_Dropbox.jpg
 
There is no separate air diffuser on that burner.
It is a one piece blast tube and that tends to make it much better and not complicated
 
Best is right, no separate diffuser. I have managed to reassemble the burner with the nozzle not in the correct central position! Ie not in the circular holder, if you see what I mean?
Sounds like too much oil or not enough air though.
 
Probably the most common burner I have worked on until recent years when Riello became more prevalent.
The blast tube is removable by slackening the 2 grub screws and makes the nozzle easy to work on without risk of damaging it
 
The plastic bit, no 17, locating block... No not replaced this. What is it for? I did not access through bank plate.

No 17 part is to hold the nozzle assembly centre at the front of burner (to keep the nozzle at other end straight) and no 17 also adjusts the nozzle distance to front of diffuser. (It has a bolt threaded through it to pull nozzle out and in.
Do not adjust it!
 
Update on boiler. Got there this am with new capacitor. On arrival noticed lock out on..Odd considering I had switched off at wall and at boiler and told client not to use boiler.. Different story..
Re-cleaned the now oil wet combustion chamber..*?@*%
Removed burner and removed fan and cleaned loosened air band and cleaned. Found small stone jammed in back of band preventing it closing fully. So when I thought I had closed air band there was actually gap at the back. TOO much air... So with that sorted . I replaced nozzle thanks to Kris's Myson performance data sheet, and set pressure. Done smoke test at low air and adjusted down to 2 smoke. Then fine tuned with FGA. Ended with 11.2 co2, 37% excess air, flue temp 277 C, 70 co ppm. any more air to bring co2 down a bit then co ppm rises. Not sure what the recommended co2 is for that boiler.
Anyway happier with that. All that headache from a 2mm stone..
Must say the air band is very fine movements to tune in. I ended up at just under 1 on the settings.
 
Last edited:
What is the advice around switching off unsafe boiler. I was taught that with oil we have no legal right to disconnect boiler. but if pumping out co @ 800ppm... Surely.. I told client on Friday boiler not safe and do not switch on, 3 times I told him. Could not believe when he said he had it on. Luckily it locked out...
 
What is the advice around switching off unsafe boiler. I was taught that with oil we have no legal right to disconnect boiler. but if pumping out co @ 800ppm... Surely.. I told client on Friday boiler not safe and do not switch on, 3 times I told him. Could not believe when he said he had it on. Luckily it locked out...
Did you document it was unsafe to use?

I'll pull the fuse and turn the oil off. Document unsafe, get them to sign and keep a copy. After that its up to them.
 
Yes put it on a job sheet that I start before starting job. Would normally get them to initial any changes etc. I get then to sign and authorization to proceed before I start any job. Client had left before I finished and not back before I left, so phoned client and explained all to client before I left and he seemed happy.. Should have waited until they returned to sign, but next job waiting...
 
What is the advice around switching off unsafe boiler. I was taught that with oil we have no legal right to disconnect boiler. but if pumping out co @ 800ppm... Surely.. I told client on Friday boiler not safe and do not switch on, 3 times I told him. Could not believe when he said he had it on. Luckily it locked out...

I turn switches off and sometimes remove the solenoid to prevent burner firing.
Fuse out and oil off for extra safety.
Can’t trust customers or friends they bring later to interfere. Or children obviously can be at switches.
 
I turn switches off and sometimes remove the solenoid to prevent burner firing.
Fuse out and oil off for extra safety.
Can’t trust customers or friends they bring later to interfere. Or children obviously can be at switches.
Ill keep that in mind. Ill take solenoid with me. For better piece of mind.
 
Update on boiler. Got there this am with new capacitor. On arrival noticed lock out on..Odd considering I had switched off at wall and at boiler and told client not to use boiler.. Different story..
Re-cleaned the now oil wet combustion chamber..*?@*%
Removed burner and removed fan and cleaned loosened air band and cleaned. Found small stone jammed in back of band preventing it closing fully. So when I thought I had closed air band there was actually gap at the back. TOO much air... So with that sorted . I replaced nozzle thanks to Kris's Myson performance data sheet, and set pressure. Done smoke test at low air and adjusted down to 2 smoke. Then fine tuned with FGA. Ended with 11.2 co2, 37% excess air, flue temp 277 C, 70 co ppm. any more air to bring co2 down a bit then co ppm rises. Not sure what the recommended co2 is for that boiler.
Anyway happier with that. All that headache from a 2mm stone..
Must say the air band is very fine movements to tune in. I ended up at just under 1 on the settings.

You don’t want the Co2 much more than 11% for that burner.
There was some of them supplied with a slightly different blast tube and you will find it had to burn slightly higher smoke number to achieve reasonable CO2.
I have the actual paperwork for the Velaires, but can’t be bothered looking for it.
 
Ill keep that in mind. Ill take solenoid with me. For better piece of mind.

I also remove the solenoid on boilers that haven’t full isolation switches, just to be safe when I go out to van to get tools or parts.
Don’t want to walk back into a fire. :eek:
 
You don’t want the Co2 much more than 11% for that burner.
There was some of them supplied with a slightly different blast tube and you will find it had to burn slightly higher smoke number to achieve reasonable CO2.
I have the actual paperwork for the Velaires, but can’t be bothered looking for it.
Thats good about the smoke number, I ended up with about a 2 smoke , but any less pushed other figures out..
 
Thats good about the smoke number, I ended up with about a 2 smoke , but any less pushed other figures out..

Sometimes you just have to be unconcerned with the CO2 being a little low and be happy the boiler is running clean. Over 10% is fine on some old burners I find.
That Electro oil burner was a great burner though. Must be over 30 years old if orange colour
 
Sometimes you just have to be unconcerned with the CO2 being a little low and be happy the boiler is running clean. Over 10% is fine on some old burners I find.
That Electro oil burner was a great burner though. Must be over 30 years old if orange colour
At the figures above should I be worried about sooting up then.
Job all done, dont really want to say to client I have to go back and do more.. But if it will be all sooted up in a few weeks then better sort.
 
At the figures above should I be worried about sooting up then.
Job all done, dont really want to say to client I have to go back and do more.. But if it will be all sooted up in a few weeks then better sort.

The figures seem very good.
Much the same as a new type burner would be set at.
Co is a bit high, but not bad
 
so to bring co2 down to between 10-11% i'd increase excess air. Pushing excess air to about 49% . less soot (good) . But this increases CO (bad) How to get CO down and Co2. down ..Decrease pressure? Pressure set to MI 145psi and Nozzle .5 80 H
 

Reply to Very very Hight Co2 ppm old Myson velarie... Help in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

About 12 days ago attended a boiler lock out. Apparently another plumber was there a week before to and adjusted the photo cell. .. It is a grant...
Replies
25
Views
3K
Hi, I'm hoping for some suggestions as to where I go next in my endless mission to stop my system taking on air. The house has a gravity fed...
Replies
25
Views
5K
We have a Rayburn 460k Nuway burner which is now over 20 years old which has been regularly serviced and maintained by myself and has generally...
Replies
11
Views
9K
  • Locked
Hi Just come away from a 22 year old Boulter oil boiler. Carried out a service, the exchange and baffles were in quite a state. Cleaned it all...
Replies
9
Views
2K