Sorry to trouble you but I wondered if one of you genius out there could help with some technical advice?


I have a Vokrea i36 Utica (of which I am very pleased it’s a nice piece of kit). It is classed as an opentherm boiler. Additionally it modulates on a 10.1 ratio.


Now. I have it wired to a nest 3rd generation thermostat. Currently it is just wired to on/off however I am led to believe that it should be wired to opentherm and NOT on off. What I am slightly confused with is that if the temp of the boiler (heating) is set within the while settings it is in modulating mode. As I result I fail to see why setting it up to opentherm would make any difference?


I am assuming that opthetherm in the back slowly condensing and keeping the rads as a lowest temp but maintaining the temp of 20 degrees for example. Surely is that not what modulating does?


SO should it be rewired to opentherm and no on and off? The object is to save money on fuel (gas). However it seems counter intuitive to have boiler running all day even when it running on a low temp?


Please forgive the question as what may seem simple to one is very complicated to another!


Finally Vokrea and Nest seem a little clueless
 
Last edited:
Diagram

COntrols.jpeg
 
Last edited:
Either would’ve been fine don’t worry all new postings show up so we can see them
 
I am assuming that opthetherm in the back slowly condensing and keeping the rads as a lowest temp but maintaining the temp of 20 degrees for example. Surely is that not what modulating does?
Modulating does not maintain the room temperature - the room stat does that - it tries to maintain the required flow temperature. If you have an on-off thermostat the required flow temperature is constant, say 75°C. When it is very cold outside and the room is also cold the radiators need to give out the maximum heat, so a flow temperature of 75°C is required. But as the room warms up the radiators do not need to give out as much heat. If you have an on-off thermostat, and fixed flow temperature, the return temperature will rise. this causes the flow temperature to also rise above the desired 75°C. So the boiler shuts of until the water temperature has dropped. And the cycle repeats itself.

If you have an opentherm controller, this compares the actual room temperature with the desired temperature and instructs the boiler what flow temperature to use. If the difference is high, the required flow temperature will be high; if there is a small difference between desired and actual the required flow temperature will be lower. (I am assuming that there is no external temperature sensor.) As the room temperature rises the flow temperature will decrease.
 
Modulating does not maintain the room temperature - the room stat does that - it tries to maintain the required flow temperature. If you have an on-off thermostat the required flow temperature is constant, say 75°C. When it is very cold outside and the room is also cold the radiators need to give out the maximum heat, so a flow temperature of 75°C is required. But as the room warms up the radiators do not need to give out as much heat. If you have an on-off thermostat, and fixed flow temperature, the return temperature will rise. this causes the flow temperature to also rise above the desired 75°C. So the boiler shuts of until the water temperature has dropped. And the cycle repeats itself.

If you have an opentherm controller, this compares the actual room temperature with the desired temperature and instructs the boiler what flow temperature to use. If the difference is high, the required flow temperature will be high; if there is a small difference between desired and actual the required flow temperature will be lower. (I am assuming that there is no external temperature sensor.) As the room temperature rises the flow temperature will decrease.

Thank you, there is no external sensor, just Nest (google location) temp. Sorry to be dim but if opentherm is installed then surely if the boiler is going to conflict on modulation mode? Is there much difference really between the to or just preference? Im struggling with this!
 
Sorry to trouble you but I wondered if one of you genius out there could help with some technical advice?


I have a Vokrea i36 Utica (of which I am very pleased it’s a nice piece of kit). It is classed as an opentherm boiler. Additionally it modulates on a 10.1 ratio.


Now. I have it wired to a nest 3rd generation thermostat. Currently it is just wired to on/off however I am led to believe that it should be wired to opentherm and NOT on off. What I am slightly confused with is that if the temp of the boiler (heating) is set within the while settings it is in modulating mode. As I result I fail to see why setting it up to opentherm would make any difference?


I am assuming that opthetherm in the back slowly condensing and keeping the rads as a lowest temp but maintaining the temp of 20 degrees for example. Surely is that not what modulating does?


SO should it be rewired to opentherm and no on and off? The object is to save money on fuel (gas). However it seems counter intuitive to have boiler running all day even when it running on a low temp?


Please forgive the question as what may seem simple to one is very complicated to another!


Finally Vokrea and Nest seem a little clueless
Are you an engineer ? Are you allowed to wire into the boiler ?
 
Modulating does not maintain the room temperature - the room stat does that - it tries to maintain the required flow temperature. If you have an on-off thermostat the required flow temperature is constant, say 75°C. When it is very cold outside and the room is also cold the radiators need to give out the maximum heat, so a flow temperature of 75°C is required. But as the room warms up the radiators do not need to give out as much heat. If you have an on-off thermostat, and fixed flow temperature, the return temperature will rise. this causes the flow temperature to also rise above the desired 75°C. So the boiler shuts of until the water temperature has dropped. And the cycle repeats itself.

If you have an opentherm controller, this compares the actual room temperature with the desired temperature and instructs the boiler what flow temperature to use. If the difference is high, the required flow temperature will be high; if there is a small difference between desired and actual the required flow temperature will be lower. (I am assuming that there is no external temperature sensor.) As the room temperature rises the flow temperature will decrease.


I think may be getting confused with modulation and the SARA (in the diagram) function?
 
but if opentherm is installed then surely if the boiler is going to conflict on modulation mode? Is there much difference really between the to or just preference?

the OT stat tells boiler what to do
The OT stat calculates the required flow temperature and sends this information to the boiler. The boiler then modulates the boiler to maintain the required temperature.

To quote the Opentherm Protocol:

The slave (boiler) does not need to know how the master (thermostat) has calculated the control setpoint (flow temperature), e.g.whether it used room control or OTC, it only needs to control to the value. Likewise, the master does not need to know how the slave is controlling the supply.

The boiler controls the flow temperature by modulating.
 
Just been advised by Vokera that their Opentherm boilers even though they boast "Advanced energy saving credentials define this product range" they have advised me that NEST will not work when wired to Opentherm. As Openthem appears to be a standard protocol across boilermakers I would have thought that Vokera would have got their act together. Anyway looks like it just and on/off function with the NEST or buy BeSmart which looks pretty poor to me with very poor reviews. Anyway the boiler is excellent, very disappointed with Vokera and shame about the technical side of things. Thanks for all these who gave advice.
 
Just been advised by Vokera that their Opentherm boilers even though they boast "Advanced energy saving credentials define this product range" they have advised me that NEST will not work when wired to Opentherm. As Openthem appears to be a standard protocol across boilermakers I would have thought that Vokera would have got their act together. Anyway looks like it just and on/off function with the NEST or buy BeSmart which looks pretty poor to me with very poor reviews. Anyway the boiler is excellent, very disappointed with Vokera and shame about the technical side of things. Thanks for all these who gave advice.
I thought Open Therm was a bit advanced for Vokera! ;)
 

Reply to Complicated? Opentherm or on/off in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
179
Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to space for servicing and changing parts if ever needing to. I am finding my decision rather hard due to the different clearances on flue runs and cupboards...
Replies
9
Views
261
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
306
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
247
PSxxxxxx
P
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
393
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock