Hi all
I am new to this forum so if I put in too much information please forgive me. I have a WB Heatslave 18 25 oil combi boiler. I have had it for a number of years. I know WB has a great reputation which is why I bought this boiler but it has been temperamental, to say the least.
It has always had a propensity to lose pressure. I have called out engineers on many occasions and even WB came to look at it but it remains unreliable. It is serviced regularly. Currently it is losing pressure again and from my limited knowledge I think it could either be a faulty pressure relief valve or a faulty expansion tank. The latter is almost new so I suspect the pressure relief valve.
My question is, how do I safely check to see if it is this valve that is malfunctioning?
 
Worcester dont really have a great reputation especially when it comes to oil.

But if you have had several engineers look at it it may not be the boiler.

Check all your radiator valves for a green stain on crumbly greenish stuff that is a sign of a leak.

How long is it taking to lose the pressure? What are you pressuring it to?
 
Worcester dont really have a great reputation especially when it comes to oil.

But if you have had several engineers look at it it may not be the boiler.

Check all your radiator valves for a green stain on crumbly greenish stuff that is a sign of a leak.

How long is it taking to lose the pressure? What are you pressuring it to?
Thanks for the reply. There are no leaks in the system and the rads are new. Pressure loss is variable in that it can lose pressure over a couple of days and on other occasions, it stays fine for a few weeks. There is a new stain on the wall outside under the pressure relief pipe so I guess that pinpoints the problem.
 
Thanks for the reply. There are no leaks in the system and the rads are new. Pressure loss is variable in that it can lose pressure over a couple of days and on other occasions, it stays fine for a few weeks. There is a new stain on the wall outside under the pressure relief pipe so I guess that pinpoints the problem.
Oh and I only pressure it to 1.5 bar. Thanks again for responses.
 
Sounds like a problem within your boiler that you would need an oil engineer to sort out for you. A good one should find the fault relatively quickly from what you have said.

Maybe post your location up on here and one of the oil lads on here might be able to help.
 
Well known fault - your boiler expansion vessel is only 12 litre and will not be big enough for all the total volume of water in the rads, pipes and boiler.
Your engineers don’t know much if they didn’t suggest it.
Have a second expansion vessel installed to return pipe, preferably near to boiler if possible, but not essential.
The existing boiler vessel and the extra vessel will need the air charge to be same and this also requires checking and air recharged each year.
You probably do not need to have your system at 1.5 bar. Usually 1 bar when system cold is plenty, but your engineer, if you can find a decent one, will advise.
 
Well known fault - your boiler expansion vessel is only 12 litre and will not be big enough for all the total volume of water in the rads, pipes and boiler.
Your engineers don’t know much if they didn’t suggest it.
Have a second expansion vessel installed to return pipe, preferably near to boiler if possible, but not essential.
The existing boiler vessel and the extra vessel will need the air charge to be same and this also requires checking and air recharged each year.
You probably do not need to have your system at 1.5 bar. Usually 1 bar when system cold is plenty, but your engineer, if you can find a decent one, will advise.
That is new to me and really helpful. Thank you. Finding a decent engineer is another matter entirely where I live. Recently my sister had a leaking tap (I was out of the country), she phoned a local firm and two weeks later they sent out an "engineer" who said, "Yep you have a leaking tap but I don't have any tap washers on the van". (???????!!!) He went away but two days later a bill for £50 arrived!
 
That is new to me and really helpful. Thank you. Finding a decent engineer is another matter entirely where I live. Recently my sister had a leaking tap (I was out of the country), she phoned a local firm and two weeks later they sent out an "engineer" who said, "Yep you have a leaking tap but I don't have any tap washers on the van". (???????!!!) He went away but two days later a bill for £50 arrived!

Where abouts are you? Maybe one of the oillies on here can help you.
 
If the E.vessel pressure rises to > 2.8/2.9bar with the system hot then you will loose pressure, the PRV can also then weep at normal pressures but very easy to check as shown.
 

Reply to WB HEATSLAVE 18 25 losing pressure in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
122
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
224
I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about this one. Granddaughter just moved house and this valve decided to leak when it was closed. When open its fine. Normally I have repacked the gland on...
Replies
7
Views
186
I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler pump menu for either 70% or 100%, so, is the pump set at either one of two fixed speed percentages or does the pump actually vary speed, (modulate)...
Replies
1
Views
143
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
144
PSxxxxxx
P
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock