I'm looking to replace my water supply. I will be digging the trench on my side myself. I have all the safe dig plans etc and found the guide on the southern water website:

Screenshot 2021-11-28 at 10.20.15.png

Slightly confused by the 750mm minimum from the outside wall. Is this an actual thing? Every stopcock I have ever seen has been secured to the wall in some way. My wall construction is solid block-work with insulated stud wall which comes to 342.5mm thick all in. This means the pipe would come up in the middle of the floor.

2nd question is if I use 32mm MDPE the minimum bend radius would be 480mm. Would I be allowed to use a compression elbow like the one in this link within the pipe lagging part after the footings so that it can come up closer to the internal wall?

Below Ground Elbow
 
Have a look for INSUduct fully compliant with all regulations no hole to dig under footings!
Thank you, I did have a look at this. I can't see them doing a 32mm unfortunately but not a deal breaker. The issue I have is that this is a listed building so anything visible outside like this would need to go through Listed Building Consent. (i.e. painful and slow)

My bad. Just seen the 32mm INSUduct External Water Supply Protection - https://store.jdpipes.co.uk/insuduct-external-water-pipe-supply-protection-box/
 
We have used them on listed properties by finishing insuduct just below ground level then core drilling at a angle from inside to meet it.
We use 110mm core hole correct insulation then foam fill.
 
Tbh I wouldn’t want fittings below ground unless you really have to also use some 4” drain and long radius bends to sleeve it into your house
 
We have used them on listed properties by finishing insuduct just below ground level then core drilling at a angle from inside to meet it.
We use 110mm core hole correct insulation then foam fill.
I might be missing something but I don't really get the benefit? You would still need to core drill, just one system slightly higher than the other. They also don't seem to make the 32mm hockey sticks so would force me to use 25mm.

The other problem is that the building where this is going to be is 40cm higher above ground level than the other part of the house so I don't think I would be able to achieve this without some of it being visible.
 

Or

 

Reply to Water mains trench - bend radius in the DIY Plumbing Forum area at PlumbersForums.net

Similar plumbing topics

Hi, basic question, any insight much appreciated. Looking to have an outdoor tap in my front porch fed from 15mm pex coming up from suspended floor. Pic 1 is inside porch, pex temporarily clipped to give an idea of pipe placement (ignore shoddy blockwork of booted cowboy builder!), Pic 2 is...
Replies
6
Views
254
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
281
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
262
I want to reconnect some outbuildings to an existing water supply. The supply pipe is old 22mm MDPE and buried for a fair distance so not going to dig it up and replace it 😬. Question is can I use normal 22mm plumbing push-fit connectors to make the connection as finding 22mm MDPE fittings...
Replies
1
Views
286
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to run the water line underneath. There are existing drain (and who knows what) pipes running along the same wall so I'm nervous about digging too far...
Replies
6
Views
243
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock