Hello. I am a homeowner and have a Valliant EcoTech 835 (2017). Serviced every year and worked like a treat until about a few months ago when I notified the pressure reading was too high (> 3 bar). My plumber came and did a regular service and told me the boiler is in tip top condition. The pressure remained high upon inspection. To relieve, I use the radiator valve to remove some water. I am then told that I need to replace the expansion vessel and PRV. Both done. Pressure was ok for about a week then started climbing and now is again consistently >3 bar. My plumber now tells me I need to replace the Pressure Gauge Sensor. Just wanted some advice from the experienced heads here. Am I going down the right path or should I be looking at a different solution? Thanks
 
1 is filling loop passing.
2 if it’s a combi could be a breach between the plates on plate heat exchanger.
3 Vaillant pressure sensors tend to get clogged up so either stick on a reading.
 

Reply to Valliant EcoTech High Pressure in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
111
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
322
Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to space for servicing and changing parts if ever needing to. I am finding my decision rather hard due to the different clearances on flue runs and cupboards...
Replies
9
Views
186
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
123
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
231
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock