Hi, new to this forum. I hope someone experienced out there can help me find the fix. We recently finished a building project and had a major re-design/move of all of our hot water (megaflo), boiler and central heating system. I am not a plumber nor do I know much about plumbing but I know enough about how the system is designed. During the building project we added 100m2 of wet underfloor heating to our existing central heating system (which is pressured/non-vented - it had been previously converted from a vented system in 2018). This is a NuHeat designed/installed system which integrates with our Nest controlled central heating radiators. Everything had to be moved and completely re-plumbed during the project into our new garage being built on the side of our house (converting existing garage). Project has completed fine and everything has been commissioned ok - its been ~ 6-7 months now running. My building is chasing me for the final part of the 5% retention payment (~£4K). But we have a frustrating slow leak on the system - the pressure will drop on the central heating loop to zero over about 7-10 days from its usual 1.5 to 2 Bar - hence not paying the remaining £4K until it is fixed. I didnt really pay much attention to the leak in the early weeks and months post commissioning as the project was still de-snagging and the plumber coming back to complete some minor pieces, etc. We have bled out all of the air in the system multiple times (rads and high points), and cannot see any visible water leaks anywhere - all rad valves fine etc. At the moment no evidence of water on ceilings etc as there was a bunch of pipe mods made in the ceiling/floor voids when the steels were going in. I am in discussion with the Builders plumber to try various things, and he is coming over this coming week to have a look. We isolated the boiler and the NuHeat system and the system pressure was still dropping so it seems almost certainly not the boiler (relatively new Worcester Bosch) or the NuHeat wet underfloor system. Our system is copper but the builders plumber ran much of the new stuff in plastic - particularly under the floor etc. Should I be worried about the integration of copper and plastic pipes? We checked the pressure of the expansion tank using a bike pump and it was at 2.5 bar - so ok? This issue is keeping me awake at night - the thought that somewhere perhaps water might be leaking and it could take several months before we see it. Any thoughts on further diagnosis, checks etc. Whats a reasonable pressure drop for my system - its large ~ 20 rads + UFH system (6 bed house). See photos.

Many thanks,
Nick
 

Attachments

  • image.jpg
    image.jpg
    319.9 KB · Views: 17
  • image.jpg
    image.jpg
    392.8 KB · Views: 17
  • image.jpg
    image.jpg
    436.9 KB · Views: 17
your expantion vessel is over presure, lock off boiler, drain, then take it to 1.2bar, then open up you c heating.
 
your expantion vessel is over presure, lock off boiler, drain, then take it to 1.2bar, then open up you c heating.

Was taken with water / pressure in
 
Thanks… so an expansion vessel over pressure will result in a pressure drop.. where is the pressure drop going if so?… I will try what you say. I don’t see any water in the tundish drain by the over pressure valves.
 
If the system is pressurized to 2.5bar while cold then almost a certainty that it will rise to 3.0bar and lift the PRV when hot.
 
If the system is pressurized to 2.5bar while cold then almost a certainty that it will rise to 3.0bar and lift the PRV when hot.

Pre charge Jon with there still system pressure on
 
Thanks… so an expansion vessel over pressure will result in a pressure drop.. where is the pressure drop going if so?… I will try what you say. I don’t see any water in the tundish drain by the over pressure valves.
Just to say/update. This fix worked brilliantly. I dropped the pressure in the expansion vessel back to system pressure at 1.5bar using a bike track pump - previously it was overpresssured at 3.0 bar ish. Now no issues on pressure drop - the system is completely stable. Brilliant - many thanks.
 

Reply to Slow leak on my pressured central heating system in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Our kitchen mixer tap has started dripping. Like so much of the plumbing in our almost new build bungalow, it is lacking! The plumber didn't install any isolating cocks in the H&C feed to the tap so how can I identify which of the valves is passing? Shut the whole H&C water system down?
Replies
12
Views
318
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
428
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
240
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
316
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
243
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock