Pump is running through Megaflow. Turn off the outlets and it is fine.

Find this on top of the cylinder, was this normal to put on top of cylinder? So the secondary return goes into the cold feed which taps into the top of this...

20181120_165917.jpg
 
Yes the tmv3 is to reduce the temp but normally fitted at tap ends as temp can drop a bit

As for the pump should be hot out to cold inlet

Or like any other src hot to cylinder port
 
Got an email today saying that now I have replaced the SR pump, check valve and mixing valve from top of cylinder it is taking 3 minutes for hot water to get to the kitchen tap. Hmm
 
Is the pump on ?
 
Pumping in the right direction? Back to the cylinder
 
Pull it through? Not cleared up on that terminology. All I did was replace the pump.

Cheers Chris. Good to see the old boys still on the forum

Didn't change the pump valves ?
 
Soshould be still full need to check the pipe is warm if it isn't could be an air lock as chris says
 
Was there anything to stop the secondary return going back to the cylinder ?
Just thinking it is strange to have a blending (tempering) valve on the outlet of an un-vented as they should be controlled by the stats. If it has been fitted to actually reduce the temperature of the HW flow to the fittings then the return could have been taken back into the cold supply to the valve, otherwise the return water to the cylinder would cool its stored temperature causing it to reheated. This HW would then be drawn out of the flow only to be blended back down by the cold, if that make sense. Very poor design, my guess is the return goes through the valve no (or very little) back to the cylinder.
 
Was there anything to stop the secondary return going back to the cylinder ?
Just thinking it is strange to have a blending (tempering) valve on the outlet of an un-vented as they should be controlled by the stats. If it has been fitted to actually reduce the temperature of the HW flow to the fittings then the return could have been taken back into the cold supply to the valve, otherwise the return water to the cylinder would cool its stored temperature causing it to reheated. This HW would then be drawn out of the flow only to be blended back down by the cold, if that make sense. Very poor design, my guess is the return goes through the valve no (or very little) back to the cylinder.

Hi Chris, below is a sketch up of the old set up before I removed the valve.

Not the best sketch but hopefully you get the just. I believe the return was basically feeding the valve.

Screenshot_20181212-211505_Samsung Notes.jpg
 
No
 
This is how it is now. But I still for the life of me cannot think why this alteration would make it take longer to get to the kitchen. Surely the water would arrive at the tap at the same time as the flow and pressure are the sMe and the water is stored at 60

1547114748333968844529.jpg
 
Problem is your pulling blended water round so it's cooler

Try putting a nrv just above the cold tee
 
This is how it is now. But I still for the life of me cannot think why this alteration would make it take longer to get to the kitchen. Surely the water would arrive at the tap at the same time as the flow and pressure are the sMe and the water is stored at 60

View attachment 36283

So you've removed the tmv3 and capped the cold ?
 
In theory it should work is the pipework warm going to the pump ?
 
Yea normally set for hours that the place is in use with a boost / overrun
 
Very strange

Only thing I can suggest is remove pump and open the return leg to the cylinder does that get hot hot

If yes put a nrv where I said eg after the tee where the pump is on the cold pipe to the cylinder
 
Very strange

Only thing I can suggest is remove pump and open the return leg to the cylinder does that get hot hot

If yes put a nrv where I said eg after the tee where the pump is on the cold pipe to the cylinder

When you say remove pump and open return leg, do you mean open the pump valve and let water out and see if it is hot?
 
When you say remove pump and open return leg, do you mean open the pump valve and let water out and see if it is hot?

Yes checking there's no restriction/ blending valve passing back would be the same temp as the water going out of the cylinder after the leg is clear of any cold / lower temp water etc
 
Valve shut ?
 

Reply to Really loud noise when secondary... in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I want to reconnect some outbuildings to an existing water supply. The supply pipe is old 22mm MDPE and buried for a fair distance so not going to dig it up and replace it 😬. Question is can I use normal 22mm plumbing push-fit connectors to make the connection as finding 22mm MDPE fittings...
Replies
1
Views
289
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
372
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
499
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
211
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock