C

coggers

I was called to a house that reported the hot water header tank was over flowing, so I expected a passing float valve and visited.

The valve operated correctly and the problem was more involved. They have 3 showers running from a Salamander 3 bar pump. The pump and installation seem fine and a S fitting was used on the tank.

She complained of a drumming/vibrating noise whenever they ran a shower (which i heard) and after the showers were used the over flow would 'shoot' water out. I saw the marks on the mud outside and the water does not just drip out but comes out with some pressure.

The vibrating noise I found to be the cold feed to the tank, which i clipped up to reduce the noise but obviously not fix it.

We ran the shower for a while but I could not get the tank to overflow.

I suspect air/pressure from somewhere! Also, the showers drip massively after they are switched off.

Ideas please anyone?
 
Status
Not open for further replies.

Reply to Pumped shower and overflow problem in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...
Replies
0
Views
231
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
323
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
243
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
443
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock