21
Hi, hope someone can help me with a heating pressure loss problem. My valiant boiler has been loosing pressure over the last few months, resulting in me having to top up the water every week or so. Managed to get a boiler engineer to visit who diagnosed a faulty expansion tank. (Water evident at the valve on top of the EV). I replaced the EV but now the pressure drops to zero within a few hours. I’ve bleed all radiators and there are no visible leaks. Boiler working very well also and the EV was correctly charged when it arrived. If water spurts out of the Auto Air Vent (bottle type) when I depress the valve at the top does that mean it is faulty and would this affect my system pressure. The vent does not leak but perhaps it is not venting the system properly. Grateful if anyone can help. Thanks Alvin
 
1. Where is the Auto Air Vent (AAV) you refer to fitted on your system?
2. What was the air pressure in the EV before fitting, and was it altered after fitting?

The AAV should bleed air in the system as that air reaches the AAV. If you depress the valve at the top it should produce water, any air having already been bled. Sounds as if that is what you have, and if so, then the AAV is doing its job.

Have you checked that the boiler's pressure relief valve is not opening / dribbling? Test if there is any water coming out of the pressure relief pipe. This is normally copper, goes outside, and has its open end turned back against the wall.

What Vaillant model boiler do you have, and specifically is it a combi, system boiler, or open vent boiler on a sealed heating system?
 
Hi Steadyon, thanks for getting back to me. The boilers is a Vaillant eco TEC Condensing boiler. The AAV is situated between the actuator switch and the Emerson Tank.
I tested the pressure of the EV before fitting (Tuesday) and it read 24psi. Tested again a couple of hours ago and pressure still 24psi.
Boiler pressure relief valve not leaking, tested before buying new EV and again on a daily basis as I struggled to work out why pressure dropping. During boiler operation, pressure climbs up to just above 1.5 bar but once the boiler switches off the pressure then drops over an hour or two to close to zero. Before fitting the new EV the pressure would take at least a week to fall to zero, but now it drops to zero during the night.
 
1. Where is the Auto Air Vent (AAV) you refer to fitted on your system?
2. What was the air pressure in the EV before fitting, and was it altered after fitting?

The AAV should bleed air in the system as that air reaches the AAV. If you depress the valve at the top it should produce water, any air having already been bled. Sounds as if that is what you have, and if so, then the AAV is doing its job.

Have you checked that the boiler's pressure relief valve is not opening / dribbling? Test if there is any water coming out of the pressure relief pipe. This is normally copper, goes outside, and has its open end turned back against the wall.

What Vaillant model boiler do you have, and specifically is it a combi, system boiler, or open vent boiler on a sealed heating system?
 
Thanks for getting back to me Steadyon. I am having problems with this site as I have written a response and sent it but doesn’t look like it survived contact with the internet. I will try agai.
My boiler is a Vaillant eco TEC condensing boiler. Fitted in Feb 2011
The AAV is fitted between the directional auctuator valve and the Emerson tank.
I tested the new EV before fitting (24psi) on Thursday last week and again today 24psi.
The PRV is working fine as no dripping from the discharge pipe outside.
Before fitting replacement EV the pressure would take over a week to drop to zero but now it does it over night. I find myself getting up early hours to ensure I top the system up befor the boiler switches on at 7am.
I should have added on my original post that once I had fitted the new EV I also took the opportunity to add 500ml of inhibitor to the system.
 
Thanks for getting back to me Steadyon. I am having problems with this site as I have written a response and sent it but doesn’t look like it survived contact with the internet. I will try agai.
My boiler is a Vaillant eco TEC condensing boiler. Fitted in Feb 2011
The AAV is fitted between the directional auctuator valve and the Emerson tank.
I tested the new EV before fitting (24psi) on Thursday last week and again today 24psi.
The PRV is working fine as no dripping from the discharge pipe outside.
 

Reply to Pressure loss in Heating System post fitting new Expansion Tank in the USA area at PlumbersForums.net

Similar plumbing topics

Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no...
Replies
6
Views
265
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
282
PSxxxxxx
P
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I...
Replies
8
Views
395
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
443

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock