Discuss New Boiler to replace a old Worcester 35CDi II in the Central Heating Forum area at PlumbersForums.net

And this was with the bath tap running just checking ?
 
11.59net (12.86gross)
 
If these two (post31) then
12.09 secs @ 42.4c 4.96LPM, 12.07kw
18.10 secs @ 54.4c 3.31LPM, 10.83kw
Average 11.45kw

Very close to flow/temp calc??falls off with increasing temp

Might be something to do with combi temp control? as output decreases with increasing HW temp and boiler gets close to rated output at reducing temps.
 
Had a look at the Baxi830 manual, it states minimum flowrate 2 LPM but recommend 2.5 LPM and the minimum output is 6.1kw.
The lowest test flow reading was 2.74LPM (bathroom tap) which gave a measured temp of 41.1C from mains at 7.5C = 6.42kw.
With the DHW temp control to max, 60C, and if the measured HW temp was 60C, then 10.04kw required so no reason why the boiler shouldn't have achieved this.
 
Some more 2 minute hot tap runs with readings.

Bath start 383,730 finish 383,812
Main bathroom sink tap start 383,812 finish 383,894
Ensuite sink tap start 383,894 finish 383,973
Ensuite shower set at 38c start 383,973 finish 384,028
 
If these two (post31) then
12.09 secs @ 42.4c 4.96LPM, 12.07kw
18.10 secs @ 54.4c 3.31LPM, 10.83kw
Average 11.45kw

Very close to flow/temp calc??falls off with increasing temp

Might be something to do with combi temp control? as output decreases with increasing HW temp and boiler gets close to rated output at reducing temps.
They are both kitchen tap readings which is directly next to the boiler. That tap is certainly the hottest and the only one where you wouldn't be able to keep your hand under at the correct flow to achieve the hottest water.
 
Bath 23.76 kw
Mbst 23.76 kw
Est 22..89 kw
Ess 15.94 kw

And your getting around 12 lpm out of the bathroom and sink taps if you are boiler fault as the top two should be 30kw
 
If you have 12 lpm coming out of the tap then yes
 
Some more 2 minute hot tap runs with readings.

Bath start 383,730 finish 383,812
Main bathroom sink tap start 383,812 finish 383,894
Ensuite sink tap start 383,894 finish 383,973
Ensuite shower set at 38c start 383,973 finish 384,028

From post#31 (below) My calcs in bold.
Bathroom ensuite
12.82 secs @ 39.4c 4.48LPM 9.97kw
20.31 secs @ 43.1c 2.96LPM 7.35kw
Main bathroom sink
12.51 secs @ 35.1c 4.79LPM, 9.22kwkw
21.83 secs @ 41.1c 2.74LPM, 6.44kw
From post #62 (Shaun)
Bath 23.76 kw
Mbst 23.76 kw
Est 22..89 kw
Ess 15.94 kw

Which, if any, of the above (Shaun) taps correspond to the post #31 taps (Ignore power outputs)

Edit: Also, if the shower temp was actually 38C then a boiler output of 15.94kw gives flowrate of 7.5LPM
 
Last edited:
From post#31 (below) My calcs in bold.
Bathroom ensuite
12.82 secs @ 39.4c 4.48LPM 9.97kw
20.31 secs @ 43.1c 2.96LPM 7.35kw
Main bathroom sink
12.51 secs @ 35.1c 4.79LPM, 9.22kwkw
21.83 secs @ 41.1c 2.74LPM, 6.44kw
From post #62 (Shaun)
Bath 23.76 kw
Mbst 23.76 kw
Est 22..89 kw
Ess 15.94 kw

Which, if any, of the above (Shaun) taps correspond to the post #31 taps (Ignore power outputs)
Now....in simple terms what does this mean? I get the LPM but don't understand the kw readings and what it all means in comparison to my iasue. But I assume the LPM is irrelevant if we are not getting the required HW output?
 
You should be getting 12lpm and 30kw
 
One is a check on the other.

IF the measured flowrates and temperatures are correct then the calculated boiler output can a is very accurately calculated.

Now....in simple terms what does this mean? I get the LPM but don't understand the kw readings and what it all means in comparison to my iasue. But I assume the LPM is irrelevant if we are not getting the required HW output?

A bit long winded but....
From one of your readings above of 1 litre fill in 12.82 secs and 39.4C then this equals to a flowrate of 60/12.82, 4.68LPM and the water must be raised in temperature from 7.5C to 39.4C, a dT of 31.9C.
The well know calc for the energy required is kw= LPMX60XdT/860, in this case, 4.68X60X31.9/860, 10.42kw. this will be IMO almost100% correct, as a check you can take the gas meter readings, these readings in M3 can be converted to the boiler output required or visa versa in our case, I don't know the exact conversion factors but if you use 10.8kw/M3 of gas and a boiler efficiency of say 88% then you won't be far out .
So, gas consumption in M3/hr is 10.42/10.8/0.88, 1.096M3/hr or 0.0365M3/2mins. So if both of these calcs marry up then you are happy but either one will give be almost 100% correct.
 
One is a check on the other.

IF the measured flowrates and temperatures are correct then the calculated boiler output can a is very accurately calculated.



A bit long winded but....
From one of your readings above of 1 litre fill in 12.82 secs and 39.4C then this equals to a flowrate of 60/12.82, 4.68LPM and the water must be raised in temperature from 7.5C to 39.4C, a dT of 31.9C.
The well know calc for the energy required is kw= LPMX60XdT/860, in this case, 4.68X60X31.9/860, 10.42kw. this will be IMO almost100% correct, as a check you can take the gas meter readings, these readings in M3 can be converted to the boiler output required or visa versa in our case, I don't know the exact conversion factors but if you use 10.8kw/M3 of gas and a boiler efficiency of say 88% then you won't be far out .
So, gas consumption in M3/hr is 10.42/10.8/0.88, 1.096M3/hr or 0.0365M3/2mins. So if both of these calcs marry up then you are happy but either one will give be almost 100% correct.
Understand the logic of getting the figures now, thanks.

The gas readings were as you say M3. I'll ring baxi/plumber in the new year and get them to come out to it to try and find out exactly what the issue is.
 
You can see that the boiler just isn't giving anywhere near the required output if the DHW temp is set to 60C.
Take your own example again, above, you have a flowrate of 4.68LPM and you require a flowtemp of 60C (because that is what the max boiler DHW temp is) a dT of (60-7.5), 52.5C.
Boiler output required is 4.68X60X52.5/860, 17.14kw but you are only achieving a flowtemp of 39.4C (and a boiler output of 10.42kw). IF the boiler DHW temp had been set to 39.4C then, yes, you will get a flowrate of 4.68LPM at 39.4C but the settting is cranked up to max of 60C?. Really no need IMO but certainly no harm, to confirm with gas meter.
 
You can see that the boiler just isn't giving anywhere near the required output if the DHW temp is set to 60C.
Take your own example again, above, you have a flowrate of 4.68LPM and you require a flowtemp of 60C (because that is what the max boiler DHW temp is) a dT of (60-7.5), 52.5C.
Boiler output required is 4.68X60X52.5/860, 17.14kw but you are only achieving a flowtemp of 39.4C (and a boiler output of 10.42kw). IF the boiler DHW temp had been set to 39.4C then, yes, you will get a flowrate of 4.68LPM at 39.4C but the settting is cranked up to max of 60C?. Really no need IMO but certainly no harm, to confirm with gas meter.
I assume it could be a number of things could be why it is not giving the correct output? Or will it be easy to narrow down running some basic in house tests? Can I do the gas tests to confirm? I thought that's what the m3 readings were? Ta
 
The taps have some influence on flow rate if there modern they might have flow restrictors in etc hence bath taps giving the full amount
 
The taps have some influence on flow rate if there modern they might have flow restrictors in etc hence bath taps giving the full amount
I'm pretty sure they do have flow restrictors in them but not the bath as you say. But that still doesn't explain the lack of temperature at the bath taps does it? You certainly shouldn't be filling a bath or sink with hot water and not need to add cold to it. I can only think there's an issue with the boiler/install as it was giving red hot water previously at all taps apart from bath where it would go cold after a while which I put down to the old broken boiler as when we moved in it was fine.
 
Exactly your boiler should be at 30kw when doing 12lpm
 
If you had a very (very) large bath tap that gave a unrestricted flowrate of say 30LPM then a 30kw boiler will only give a temperature of 22C (21.8), not much use to anyone, if you want to heat it to 60C then you must restrict the flow rate to 8.2LPM and then add cold water (at 7.5C) to give the required bath temperature. The boiler output required will still be 30kw.
You could be caught out this way with a stored combi where you get lovely roasting hot water for a few minutes and then lukewarm thereafter except you throttle in the hot tap.

What can lead to a wrong diagnosis is say in the case above where you have a flowrate of 4.68LPM at a temperature of 39.4C despite having the DHW temp set to 60C. If this tap is a hot water tap only (no chance of mixing) then you can be 100% sure that it is a boiler problem.
But if the tap is a mixer and even though set to give full hot water flow, due to a problem with the mixer, you could end up with a flow of 2.84LPM at 60C and a flow of 1.84LPM at 7.5C to give that mixed flow of 4.68LPM at 39.4C. and the boiler will be running perfectly correctly at 60C with a output of 10.42kw. If you had a suspicion that this may be the case then just measure the hot water outlet temperature at the boiler.
 
Last edited:
Exactly your boiler should be at 30kw when doing 12lpm
Fine for a shower but a bit cool for a bath as it will cool down from 43C fairly rapidly, throttling the hot tap to give say 9LPM should give a temp of 55C, add cold to give required bath temperature but I suppose that's what most people do anyway.
 
Fine for a shower but a bit cool for a bath as it will cool down from 43C fairly rapidly, throttling the hot tap to give say 9LPM should give a temp of 55C, add cold to give required bath temperature but I suppose that's what most people do anyway.

Yes but the bath taps are only going to 23kw ish you would expect 30kw as these are full flow / non limiting normally
 
Yes, I think the bath tap flow was measured at ~ 15.5LPM so will definitely look for full boiler output as the flow temp at 30kw will only be 35C.
It seems a strange fault as it allows approx 77% (23kw) output at higher flowrates but only approx 61% at the lower flow rates, it only gives 10.42kw at a flowrate of 4.68LPM & 39.4C,should be 17.14kw & 60C.
 
Could be modulated but until they fix full flow it could be effecting everything else and no point with speculation atm
 
Also, is this the hot water feed as when kitchen tap and other hot taps are on this isn't overly hot, certainly not where you wouldn't want to touch it for too long.
 

Attachments

  • C40EFECD-4F68-497D-9BAD-E04AB8DE337A.jpeg
    C40EFECD-4F68-497D-9BAD-E04AB8DE337A.jpeg
    592.3 KB · Views: 25
Given it was fine to this boiler being put in, would the boiler perhaps be limiting something or could if be a failed part etc.
Until the experts arrive,
You could just reduce the DHW temperature setting by a division or two, to approx 50C, and see if it makes any difference to your very low flow taps, there's one there at 2.74LPM. If it results in the boiler firing at 30kw on the bath tap then you will still only achieve ~ 35C, you got, I think, 31.2C, but you were getting reasonable but not max boiler output on the higher flow rates.
 
Last edited:
So I have finally got onto Baxi and they are due to come out on Thursday, not ideal but hey ho. I have been on holiday all over xmas/new year so was unable to do anything. I had a shower last night and whilst it wasn't hot, it was enough to wash but definitely wasn't the 38C which the thermostatic tap was set at. I tried turning it to 50C to see if anything increased, it didn't in terms of hot, but went cold a few times, then back warm again. In the meantime, I emailed Baxi to ask the question re hot water and I got this response from their "technical team".

Good morning

Thank you for your email

The 830 has a 5KW less output to the Worecester 35CDii so that is where the issue lies.

The Baxi 836 Combi would have been the ideal replacement for it.
 
It’s the fact your kitchen / basin taps and shower which are normally regulated don’t get hot could understand if it was just a bath as these are full flow
 
So I have finally got onto Baxi and they are due to come out on Thursday, not ideal but hey ho. I have been on holiday all over xmas/new year so was unable to do anything. I had a shower last night and whilst it wasn't hot, it was enough to wash but definitely wasn't the 38C which the thermostatic tap was set at. I tried turning it to 50C to see if anything increased, it didn't in terms of hot, but went cold a few times, then back warm again. In the meantime, I emailed Baxi to ask the question re hot water and I got this response from their "technical team".

Good morning

Thank you for your email

The 830 has a 5KW less output to the Worecester 35CDii so that is where the issue lies.

The Baxi 836 Combi would have been the ideal replacement for it.

Their reply wouldn't exactly fill one with confidence but at least they are following it up with a visit.

Make sure you emphasize that the boiler, isn't giving the required temperatures, more obvious at the lower flowrates.
If you assume cold mains now at 6C then any 30kw boiler should give a flow rate of 8LPM @ 60C, 8.5LPM @55C, 9.5LPM @ 50C, 11LPM @ 45C & 12.5LPM @ 40C.

If you want to, ensure DHW temp set to 60C and measure the mains temperature, the flow temperature and the flow rate (once again) from one of the Hot (only) taps that gives around 5 or 6 LPM, you can then show him/her up to date info which may convince them that you will be quite happy with a 30kw boiler once its fixed.
 
Their reply wouldn't exactly fill one with confidence but at least they are following it up with a visit.

Make sure you emphasize that the boiler, isn't giving the required temperatures, more obvious at the lower flowrates.
If you assume cold mains now at 6C then any 30kw boiler should give a flow rate of 8LPM @ 60C, 8.5LPM @55C, 9.5LPM @ 50C, 11LPM @ 45C & 12.5LPM @ 40C.

If you want to, ensure DHW temp set to 60C and measure the mains temperature, the flow temperature and the flow rate (once again) from one of the Hot (only) taps that gives around 5 or 6 LPM, you can then show him/her up to date info which may convince them that you will be quite happy with a 30kw boiler once its fixed.
I will do my best. I have no issues with the boiler, it heats up the rads nice and toasty and is very efficient and quiet. They have sent this back this afternoon.
 

Attachments

  • 3F117EC7-4D91-4719-A818-8507085D6B9E.jpeg
    3F117EC7-4D91-4719-A818-8507085D6B9E.jpeg
    389.8 KB · Views: 22
That technical information applies to any Combi boiler, for example any 30kw boiler will give a flowrate of 30*860/60/30, 14.3LPM, with a temp rise of 30C and 30*860/60/35, 12.2LPM, with a temp rise of 35C. This is not in dispute but you are not getting the correct temperature rise at any flowrate as explained above several times, the challenge is to make them believe this. I can only suggest again to re take one or two of the tests that you carried out so well a few weeks ago. The one I suggested above at the lower rate of ~ 6LPM or whatever that hot tap flowed, it doesn't matter as long as you take your measurements accurately, again.
You might also consider taking the hot bath tap flow again with mains and hot water temps in both cases and you can then present these readings and calcs to them, they can't have any excuses for not fixing your boiler then.
 
This should be enough to demonstrate the boilers problems mainly at lower flow rates as, at the higher flow rates, your first two tests, the calculated boiler output is quite close to the rated boiler output of 30kw, but the last three clearly show a problem.

Mains Temp: 7.5C. DHW temp setpoint 60C, Boiler Rated Output 30kw.
3.74 secs @ 31.2c 16.04LPM 26.52kw Achievable Temp 34C Req output 30kw Actual output 26.5kw
3.86 secs @ 33.7c 15.54LPM 28.4kw Achievable Temp 35C Req output 30kw Actual output 28.4kw
6.30 secs @ 36c 9.52LPM 18.92kw Achievable Temp 53C Req output 30kw Actual output 18.9kw
10.16 secs @ 39.8c 5.91LPM 13.31kw Achievable Temp 60C Req output 21.6kw Actual output 13.3kw
16.26 secs @ 41c 3.69LPM 8.62kw Achievable Temp 60C Req output 13.5kw Actual output 8.6kw
 
This should be enough to demonstrate the boilers problems mainly at lower flow rates as, at the higher flow rates, your first two tests, the calculated boiler output is quite close to the rated boiler output of 30kw, but the last three clearly show a problem.

Mains Temp: 7.5C. DHW temp setpoint 60C, Boiler Rated Output 30kw.
3.74 secs @ 31.2c 16.04LPM 26.52kw Achievable Temp 34C Req output 30kw Actual output 26.5kw
3.86 secs @ 33.7c 15.54LPM 28.4kw Achievable Temp 35C Req output 30kw Actual output 28.4kw
6.30 secs @ 36c 9.52LPM 18.92kw Achievable Temp 53C Req output 30kw Actual output 18.9kw
10.16 secs @ 39.8c 5.91LPM 13.31kw Achievable Temp 60C Req output 21.6kw Actual output 13.3kw
16.26 secs @ 41c 3.69LPM 8.62kw Achievable Temp 60C Req output 13.5kw Actual output 8.6kw
Hi John,

Thanks for this and advising me what to say. I am going to carry out the above tests again this afternoon. Just to confirm, this is seeing how long each tap takes to fill a 1 litre jug and then what temp the filled jug is at?

Am I correct in saying the measuring of gas readings are 2 minute tap runs?
 
Hi John,

Thanks for this and advising me what to say. I am going to carry out the above tests again this afternoon. Just to confirm, this is seeing how long each tap takes to fill a 1 litre jug and then what temp the filled jug is at?

Am I correct in saying the measuring of gas readings are 2 minute tap runs?

Correct re jug, just rinse out a few times to ensure hot, also please take the mains cold water temp.
No need for gas meter readings.
Also ensure DHW temp setpoint set to 60C.
 
Correct re jug, just rinse out a few times to ensure hot, also please take the mains cold water temp.
No need for gas meter readings.
Also ensure DHW temp setpoint set to 60C.
Set to 60c on boiler.

Cold water was 12c out of the tap but bare in mind inside the house is 21c with heating having been on.

Kitchen tap

10.81- 47c
10.66 - 43.5c
10.55 - 42.9c
10.35 - 42.3c

Downstairs bathroom tap

6.23 - 37.7c
6.69 - 36.3c

Bathroom upstairs tap

5.96 - 35c
5:40 - 34.9c

Bath tap

4.12 - 31.7c
4.27 - 34.6c
19.5 - 41.2c
25.6 - 41.4c

Ensuite sink tap

6.67 - 37.8c
6.37 - 39.3c

All filled to approx 1 litre and each tap was left running for 30 seconds or so before starting.

Just to point out, I did the ensuite sink tap last and when I initially turned the hot tap on I put my hand under it as soon as water commenced and it was scolding for 3 seconds then cooled down. That's the first time since having the new boiler in that I've had to move my hand from a hot tap. Very odd!!!
 
Very similar to your previous readings, don't know what these two readings mean from the Bath Tap but not needed, the other two are fine.
19.5 - 41.2c
25.6 - 41.4c

I would also venture that the mains temp after a good run is ~ 7C so the actual output of the boiler with the bath flow rate of 14.6 LPM is more like 28kw but that doesn't in any way explain the problems at lower flow rates which will have to be addressed.

Mains Temp: 12.0C. DHW temp setpoint 60C, Boiler Rated Output 30kw.
Measured​
Achievable​
Required​
Actual​
Kitchen Tap​
Temp​
Temp​
Output​
Output​
LPM​
DegC​
DegC​
KW​
KW​
5.6​
47​
60​
18.6​
13.6​
5.6​
43.5​
60​
18.8​
12.4​
5.7​
42.9​
60​
19.0​
12.3​
5.8​
42.3​
60​
19.4​
12.3​
Downstairs​
Bathroom​
Measured​
Achievable​
Required​
Actual​
Tap​
Temp​
Temp​
Output​
Output​
LPM​
DegC​
DegC​
KW​
KW​
9.6​
37.7​
56.6​
30.0​
17.3​
9.0​
36.3​
59.9​
30.0​
15.2​
Upstairs​
Bathroom​
Measured​
Achievable​
Required​
Actual​
Tap​
Temp​
Temp​
Output​
Output​
LPM​
DegC​
DegC​
KW​
KW​
10.1​
35.0​
54.7​
30.0​
16.2​
11.1​
34.9​
50.7​
30.0​
17.8​
Ensuite​
Sink​
Measured​
Achievable​
Required​
Actual​
Tap​
Temp​
Temp​
Output​
Output​
LPM​
DegC​
DegC​
KW​
KW​
9.0​
37.8​
59.8​
30.0​
16.2​
9.4​
39.3​
57.7​
30.0​
17.9​
Bathroom​
Measured​
Achievable​
Required​
Actual​
Tap​
Temp​
Temp​
Output​
Output​
LPM​
DegC​
DegC​
KW​
KW​
14.6​
35.0​
41.5​
30.0​
23.4​
14.1​
34.9​
42.6​
30.0​
22.4​
 
Last edited:
Very similar to your previous readings, don't know what these two readings mean from the Bath Tap but not needed, the other two are fine.
19.5 - 41.2c
25.6 - 41.4c

I would also venture that the mains temp after a good run is ~ 7C so the actual output of the boiler with the bath flow rate of 14.6 LPM is more like 28kw but that doesn't in any way explain the problems at lower flow rates which will have to be addressed.

Mains Temp: 12.0C. DHW temp setpoint 60C, Boiler Rated Output 30kw.
Measured​
Achievable​
Required​
Actual​
Kitchen Tap​
Temp​
Temp​
Output​
Output​
LPM​
DegC​
DegC​
KW​
KW​
5.6​
47​
60​
18.6​
13.6​
5.6​
43.5​
60​
18.8​
12.4​
5.7​
42.9​
60​
19.0​
12.3​
5.8​
42.3​
60​
19.4​
12.3​
Downstairs​
Bathroom​
Measured​
Achievable​
Required​
Actual​
Tap​
Temp​
Temp​
Output​
Output​
LPM​
DegC​
DegC​
KW​
KW​
9.6​
37.7​
56.6​
30.0​
17.3​
9.0​
36.3​
59.9​
30.0​
15.2​
Upstairs​
Bathroom​
Measured​
Achievable​
Required​
Actual​
Tap​
Temp​
Temp​
Output​
Output​
LPM​
DegC​
DegC​
KW​
KW​
10.1​
35.0​
54.7​
30.0​
16.2​
11.1​
34.9​
50.7​
30.0​
17.8​
Ensuite​
Sink​
Measured​
Achievable​
Required​
Actual​
Tap​
Temp​
Temp​
Output​
Output​
LPM​
DegC​
DegC​
KW​
KW​
9.0​
37.8​
59.8​
30.0​
16.2​
9.4​
39.3​
57.7​
30.0​
17.9​
Bathroom​
Measured​
Achievable​
Required​
Actual​
Tap​
Temp​
Temp​
Output​
Output​
LPM​
DegC​
DegC​
KW​
KW​
14.6​
35.0​
41.5​
30.0​
23.4​
14.1​
34.9​
42.6​
30.0​
22.4​
Wow.....thanks for this John. It certainly makes it easier to understand what's going on now and cI an certainly put my point across to the engineer when he comes and even show him to experiment's I've conducted.

Atleast we can see there is a clearly issue with the actual output not matching the required output which the boiler is capable of.
 
A bit easier to see the problem all right, I have just cleaned it up a bit more here.

DHW​
Boiler​
Mains​
Setpoint
Rated​
Temp​
Temp​
Output​
DegC​
DegC​
KW​
12​
60​
30​
Measured​
Achievable​
Required​
Actual​
Kitchen​
Temp​
Temp​
Output​
Output​
LPM​
DegC​
DegC​
KW​
KW​
5.6​
47​
60​
18.6​
13.6​
5.6​
43.5​
60​
18.8​
12.4​
5.7​
42.9​
60​
19.0​
12.3​
5.8​
42.3​
60​
19.4​
12.3​
5.7
43.9
60.0
19.0
12.6
Average
Downstairs​
Bathroom​
Measured​
Achievable​
Required​
Actual​
Tap​
Temp​
Temp​
Output​
Output​
LPM​
DegC​
DegC​
KW​
KW​
9.6​
37.7​
56.6​
30.0​
17.3​
9.0​
36.3​
59.9​
30.0​
15.2​
9.3
37.0
58.3
30.0
16.2
Average
Upstairs​
Bathroom​
Measured​
Achievable​
Required​
Actual​
Tap​
Temp​
Temp​
Output​
Output​
LPM​
DegC​
DegC​
KW​
KW​
10.1​
35.0​
54.7​
30.0​
16.2​
11.1​
34.9​
50.7​
30.0​
17.8​
10.6
35.0
52.7
30.0
17.0
Average
Ensuite​
Sink​
Measured​
Achievable​
Required​
Actual​
Tap​
Temp​
Temp​
Output​
Output​
LPM​
DegC​
DegC​
KW​
KW​
9.0​
37.8​
59.8​
30.0​
16.2​
9.4​
39.3​
57.7​
30.0​
17.9​
9.2
38.6
58.7
30.0
17.1
Average
Bathroom​
Measured​
Achievable​
Required​
Actual​
Tap​
Temp​
Temp​
Output​
Output​
LPM​
DegC​
DegC​
KW​
KW​
14.6​
35.0​
41.5​
30.0​
23.4​
14.1​
34.9​
42.6​
30.0​
22.4​
14.3
35.0
42.1
30.0
22.9
Average
 
A bit easier to see the problem all right, I have just cleaned it up a bit more here.

DHW​
Boiler​
Mains​
Setpoint
Rated​
Temp​
Temp​
Output​
DegC​
DegC​
KW​
12​
60​
30​
Measured​
Achievable​
Required​
Actual​
Kitchen​
Temp​
Temp​
Output​
Output​
LPM​
DegC​
DegC​
KW​
KW​
5.6​
47​
60​
18.6​
13.6​
5.6​
43.5​
60​
18.8​
12.4​
5.7​
42.9​
60​
19.0​
12.3​
5.8​
42.3​
60​
19.4​
12.3​
5.7
43.9
60.0
19.0
12.6
Average
Downstairs​
Bathroom​
Measured​
Achievable​
Required​
Actual​
Tap​
Temp​
Temp​
Output​
Output​
LPM​
DegC​
DegC​
KW​
KW​
9.6​
37.7​
56.6​
30.0​
17.3​
9.0​
36.3​
59.9​
30.0​
15.2​
9.3
37.0
58.3
30.0
16.2
Average
Upstairs​
Bathroom​
Measured​
Achievable​
Required​
Actual​
Tap​
Temp​
Temp​
Output​
Output​
LPM​
DegC​
DegC​
KW​
KW​
10.1​
35.0​
54.7​
30.0​
16.2​
11.1​
34.9​
50.7​
30.0​
17.8​
10.6
35.0
52.7
30.0
17.0
Average
Ensuite​
Sink​
Measured​
Achievable​
Required​
Actual​
Tap​
Temp​
Temp​
Output​
Output​
LPM​
DegC​
DegC​
KW​
KW​
9.0​
37.8​
59.8​
30.0​
16.2​
9.4​
39.3​
57.7​
30.0​
17.9​
9.2
38.6
58.7
30.0
17.1
Average
Bathroom​
Measured​
Achievable​
Required​
Actual​
Tap​
Temp​
Temp​
Output​
Output​
LPM​
DegC​
DegC​
KW​
KW​
14.6​
35.0​
41.5​
30.0​
23.4​
14.1​
34.9​
42.6​
30.0​
22.4​
14.3
35.0
42.1
30.0
22.9
Average
Perfect. You certainly can't get away from these facts and if he wants to conduct the same tests then he'll get the same results.

The only thing I noticed was the bathroom measured temps were the same which was a typo I assume as they were slightly different in temps.
 
These ones?,
Downstairs bathroom tap

6.23 - 37.7c
6.69 - 36.3c

Bathroom upstairs tap

5.96 - 35c
5:40 - 34.9c
These,

Bathroom upstairs tap

5.96 - 35c
5:40 - 34.9c

Bath tap

4.12 - 31.7c
4.27 - 34.6c

Think you just forgot to change the temps as the bath tap was the same temperature as bathroom upstairs in the table you created but different LPM. Honestly not an issue as you've been more then helpful to spend time doing such things.
 
Oh Yes, quite right, corrected now and important to get it as your tests show, actually makes a better case as the average boiler output is lower again, at 21.1kw.
As a matter of interest, you seem to have shut the bath tap in a bit? to get the temperature up for the last two tests but the (flow) times make no sense, do you have them?.

Bath tap
4.12 - 31.7c
4.27 - 34.6c
19.5 - 41.2c
25.6 - 41.4c


DHW​
Boiler​
Mains​
Setpoint​
Rated​
Temp​
Temp​
Output​
DegC​
DegC​
KW​
12​
60​
30​
Measured​
Achievable​
Required​
Actual​
Kitchen​
Temp​
Temp​
Output​
Output​
LPM​
DegC​
DegC​
KW​
KW​
5.6​
47​
60​
18.6​
13.6​
5.6​
43.5​
60​
18.8​
12.4​
5.7​
42.9​
60​
19.0​
12.3​
5.8​
42.3​
60​
19.4​
12.3​
5.7
43.9
60.0
19.0
12.6
Average
Downstairs​
Bathroom​
Measured​
Achievable​
Required​
Actual​
Tap​
Temp​
Temp​
Output​
Output​
LPM​
DegC​
DegC​
KW​
KW​
9.6​
37.7​
56.6​
30.0​
17.3​
9.0​
36.3​
59.9​
30.0​
15.2​
9.3
37.0
58.3
30.0
16.2
Average
Upstairs​
Bathroom​
Measured​
Achievable​
Required​
Actual​
Tap​
Temp​
Temp​
Output​
Output​
LPM​
DegC​
DegC​
KW​
KW​
10.1​
35.0​
54.7​
30.0​
16.2​
11.1​
34.9​
50.7​
30.0​
17.8​
10.6
35.0
52.7
30.0
17.0
Average
Ensuite​
Sink​
Measured​
Achievable​
Required​
Actual​
Tap​
Temp​
Temp​
Output​
Output​
LPM​
DegC​
DegC​
KW​
KW​
9.0​
37.8​
59.8​
30.0​
16.2​
9.4​
39.3​
57.7​
30.0​
17.9​
9.2
38.6
58.7
30.0
17.1
Average
Bath​
Measured​
Achievable​
Required​
Actual​
Tap​
Temp​
Temp​
Output​
Output​
LPM​
DegC​
DegC​
KW​
KW​
14.6​
31.7​
41.5​
30.0​
20.0​
14.1​
34.6​
42.6​
30.0​
22.2​
14.3
33.2
42.1
30.0
21.1
Average
 

Reply to New Boiler to replace a old Worcester 35CDi II in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hi I seek some advice on replacing an existing regular boiler. I currently have an old Potterton 10-16 Netaheat electronic, which is around 35...
Replies
7
Views
692
Hi, I have a Worcester Bosch Greenstar 30Si combi boiler, the analog clock has stopped and the On-Timer-Off switch only works on Timer setting...
Replies
4
Views
293
Just had a new worcester bosch. 1000 combi boiler to replace 18yr old vokera. No problems with new boiler. Enquiring about yearly maintenance /...
Replies
4
Views
338
Hi, I am replacing our 11 year old boiler (due to H.Ex. leak) with a new one. This is in a "sealed" system with red expansion vessel in airig...
Replies
3
Views
547