So after bleeding the air off each time the pressure returns to normal ?. I know it doesn't add up but could/can you remove the filling loop to absolutely rule it out.

I’m not sure that the pressure rises. I will try and monitor.

It’s hard because it fluctuates a little bit. Baxi engineers said this is normal.

Not sure how to remove the filling loop exactly. Would I have to drain the system?
 
There should be a flexible hose somewhere where it connects to the boiler return with isolating valves or can you post a photo of the isolation valve you described previously?

Do mean by PG fluctuations that it changes fairly rapidly while watching it and have you watched it for any unusual behaviour while using hot water?
 
There should be a flexible hose somewhere where it connects to the boiler return with isolating valves or can you post a photo of the isolation valve you described previously?

Do mean by PG fluctuations that it changes fairly rapidly while watching it and have you watched it for any unusual behaviour while using hot water?

Will see if there are isolating valves behind.

The pressure only drops/rises when the pump goes on/off. Not during heating.

Haven’t checked when using hot water but will check tomorrow.
 

Attachments

  • 1A03E920-D763-46E0-A46E-84F208D57900.jpeg
    1A03E920-D763-46E0-A46E-84F208D57900.jpeg
    348.5 KB · Views: 15
Will see if there are isolating valves behind.

The pressure only drops/rises when the pump goes on/off. Not during heating.

Haven’t checked when using hot water but will check tomorrow.

That is the filling loop with a non return valve where shown and a isolating valve where shown on the other end, ensure the isolation valve is closed "across (at right angles to) the pipe" then just slacken the flexible hose where attached to the NR valve but do not remove it, when slackened a few turns water should only dribble out for a few seconds and then stop.
There may be another isolation valve on top of the NR valve but I don't think so, if there is, shut it as well
 

Attachments

  • Filling Loop with NRV.jpeg
    Filling Loop with NRV.jpeg
    121.6 KB · Views: 15
Last edited:
That is the filling loop with a non return valve where shown and a isolating valve where shown on the other end, ensure the isolation valve is closed "across (at right angles to) the pipe" then just slacken the flexible hose where attached to the NR valve but do not remove it, when slackened a few turns water should only dribble out for a few seconds and then stop.
There may be another isolation valve on top of the NR valve but I don't think so, if there is, shut it as well
Ok, I’ll try this tomorrow along with the hydrogen check!

Do you think air could be somehow being pulled into the system here?

If so, would it be the loop or the NRV?
 
No, I think it highly unlikely because even if the flexible hose is perished/holed then with a sealed system the pressure should still keep the NR valve shut. I also find it difficult to imagine that you are pulling in air anywhere in the volumes that you are getting especially if the boiler pressure is normally 1bar or higher. Lets hope in one way that its hydrogen!.
 
No, I think it highly unlikely because even if the flexible hose is perished/holed then with a sealed system the pressure should still keep the NR valve shut. I also find it difficult to imagine that you are pulling in air anywhere in the volumes that you are getting especially if the boiler pressure is normally 1bar or higher. Lets hope in one way that its hydrogen!.

I’ll take a video of the amount of air/hydrogen coming out so it’s easier to see.

Is it worth doing the bleed when the system is cold? And by cold, how long should the system be off for?
 
I've only had to vent some air from my open vented system after a complete drain down and refill, I would stop the circ pump/boiler and then vent when hot. Hot or/& cold better IMO to vent with pump off.
 
I vented the bathroom towel rail today. Heating was turned off. System was still a bit warm.

I got about 7 seconds worth of air with a quarter turn of the bleed valve.

Here is the pressure before bleeding:

1634905354785.png


And pressure after bleeding:

1634905376096.png


Thing is, the pressure gauge usually varies a bit.

From earlier in the week:

1634905550925.png

1634905565181.png


@jim843 I tried the hydrogen test. There was no pop.

@John.g do you still think it's worth removing the filling loop?

@johntheo I turned on the hot water and the pressure does drop. It went from about 2.4 to about 2. Is this a problem?

Thank you all for your help. It's been very useful for me to vent (no pun intended?!) and discuss this.
 
Yes, definitely remove (after first slackening) that filling loop, it's only hand tightened at the connection to the NRV, obviously ensure that the isolaton valve is shut, as it appears to be, then post back.
 
Yes, definitely remove (after first slackening) that filling loop, it's only hand tightened at the connection to the NRV, obviously ensure that the isolaton valve is shut, as it appears to be, then post back.

Ok. Just so I'm clear, remove loop and leave it a couple days and see if there's any air in the system?
 
I would't have thought so as difficult to see how this would pull in air so as one would expect the pressure to slowly decay with time, just leave the hose disconnected and see what happens to the pressure.
 
Last edited:
I would't have thought so as difficult to see how this would pull in air so as one would expect the pressure to slowly decay with time, just leave the hose disconnected and see what happens to the pressure.

So filling loop has been off since about 1400 (5 hours or so).

Pressure was at 2.5 a while ago. I heard some bubbling sound in bathroom rad. So bled rad again - few seconds of air - and now pressure is 2.4.

Still confused why the pressure drops when the pump comes on…
 
The expansion vessel is normally teed into the pump suction so will rise by the generated pump head when it starts so if connected to the pump discharge will fall but when when off should return to the original pressure if water temp doesn't change,
Can you bring on the hot water very briefly say for 10 secs and then switch off and see if pressure returns to its original.
 
The expansion vessel is normally teed into the pump suction so will rise by the generated pump head when it starts so if connected to the pump discharge will fall but when when off should return to the original pressure if water temp doesn't change,
Can you bring on the hot water very briefly say for 10 secs and then switch off and see if pressure returns to its original.
Ok. Pressure drops slightly when hot water comes on.

I waited about 30seconds and then the pressure goes (more or less) back to what it was before.
 
In the attachment is that a PRV on the filling system??.

It's also possible I suppose but very unlikely as I said above that the pump is pulling in a tiny amount of air through that leaking NRV each time it starts especially if the E.vessel is on the discharge side of the pump, the closer to the boiler the greater the chance, if the boiler is under warranty then that should be covered? its the only part that has direct communication to the atmosphere via the leak even though pressurized.
 

Attachments

  • Leaking NRV.jpeg
    Leaking NRV.jpeg
    121.1 KB · Views: 12
In the attachment is that a PRV on the filling system??.

It's also possible I suppose but very unlikely as I said above that the pump is pulling in a tiny amount of air through that leaking NRV each time it starts especially if the E.vessel is on the discharge side of the pump, the closer to the boiler the greater the chance, if the boiler is under warranty then that should be covered? its the only part that has direct communication to the atmosphere via the leak even though pressurized.

Maybe I’m mixing this up: the leak is on the valve that has an arrow on it.

The arrow you have drawn on the photo: do you mean a pressure release valve? I don’t know what that black thing is.
 
In the attachment is that a PRV on the filling system??.

It's also possible I suppose but very unlikely as I said above that the pump is pulling in a tiny amount of air through that leaking NRV each time it starts especially if the E.vessel is on the discharge side of the pump, the closer to the boiler the greater the chance, if the boiler is under warranty then that should be covered? its the only part that has direct communication to the atmosphere via the leak even though pressurized.
This is where the leak is (see attached).

Do you think it’s worth replacing that NRV?
 

Attachments

  • F435E0D7-8452-4FFB-A926-212EF71FD672.png
    F435E0D7-8452-4FFB-A926-212EF71FD672.png
    6 MB · Views: 11
Yes, I would replace it as every other possibility seems to have been reasonably exhausted. Maybe its under warranty?.

The valve thats leaking is a non return valve (NRV). the PRV I'm referring to is a pressure reducing valve called a PRV (as is the safety valve also called a PRV, a bit confusing) the pressure reducing valve above is/should be connected dirrectly to the filling hose?.

Forget my reference to that PRV, thats the isolating valve for the filling hose.
 
Yes, I would replace it as every other possibility seems to have been reasonably exhausted. Maybe its under warranty?.

The valve thats leaking is a non return valve (NRV). the PRV I'm referring to is a pressure reducing valve called a PRV (as is the safety valve also called a PRV, a bit confusing) the pressure reducing valve above is/should be connected dirrectly to the filling hose?.

Forget my reference to that PRV, thats the isolating valve for the filling hose.
I seem to remember from a couple years back a Baxi engineer saying that this filling loop is old and should have been replaced when the boiler was replaced. Maybe I’m misremembering, though.

You’d think the boiler would be under warranty but the installer has moved and I’ve no idea where they live now. Considering the mess they made - leaking joints under the boiler, not fitting the soak away - I should probably get someone else in.
 
As a temporary measure you could attach another filling hose which has isolating valves at both ends, connect one end to the NRV and shut it.

Something like R24 Filling Loop - https://www.NoLinkingToThis/p/r24-filling-loop/83905 with some pipe and compression fittings to connect to that new loop?
 
As a temporary measure you could attach another filling hose which has isolating valves at both ends, connect one end to the NRV and shut it.

Another thought: the isolation valve with the handle before the filling loop would stop the leak, if any, right?

Or are you thinking that the leaking NRV is somehow pulling air into the system even though the filling loop isolation valve is closed?
 
Last edited:

Reply to Gurgling and air in central heating in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
1
Views
131
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
323
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
125
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
442
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
243
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock