Discuss Five degree differential btw CH outflow/return - condensing combi in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.
K

Kmac

I recently had a Baxi Duotec 24 installed. The commissioning paperwork says that the central heating outflow is 70 degrees, return is 65 degrees (DHW at 55 degrees, if you're curious). It serves seven rads in six rooms, including one towel rail - all bar the towel rail have TRVs and all are fully open.

The loss seems really low to me and I'm concerned about efficiency - one of the drivers for getting our almost 20 year old Vokera non-condensing combi replaced was to improve the heating efficiency. I just want to make sure that I'm doing that.

Several things are confusing me:
1. The installation engineer told me very clearly not to put the central heating outflow temperature down below 70 degrees because "that's what the manufacturer recommends". I can't find this recommendation anywhere.
2. Don't condensing combi boilers rely on relatively low return temperatures (lower than 65 degrees, anyway) to condense?
3. I don't think the radiators have ever been balanced on the system - the boiler installer certainly didn't do this - could this be a (contributory) cause?

From the bits of information I have, it seems to me that what I want to do is have the outflow nice and hot but have a much greater loss across the system, returning at a much lower temperature, right? How might I achieve that?

For background, what's prompted my curiosity is that it's taking ages for room temperatures to get up to what the thermostat demands (19 degrees is all) and the rads seem much less hot to the touch than they did with the old boiler. They used to be scalding, but I have no idea what temp the central heating was set to because the temp gauge on the old Vokera was bust. We have our heating on evenings and weekends - off all day during the week and on low (15 degrees) at night.

Any ideas appreciated...
 
Depends on the original radiators. If they were sized small, as many were years ago (make em small and burny hot) then you may never get them to put out enough meaningful heat while maintaining a low return temp.
With old boilers efficiency wasnt dependent on return temp as they didnt condense.
 
Last edited by a moderator:
Have you tested the temperature of the flow (out pipe) & Return (In pipe) just below the boiler, (don't go off what they have wrote in the installation book) and see what the difference is
 
Depends on the original radiators. If they were sized small, as many were years ago (make em small and burny hot) then you may never get them to put out enough meaningful heat while maintaining a low return temp.
With old boilers efficiency wasnt dependent on return temp as they didnt condense.

With the old boiler they were indeed burny hot - so, if I follow you, even if I do balance the rads, I may never get a decent differential anyway if they are undersized...

...reading between the lines of your reply though, I guess you're confirming that in an ideal world I'd have a much lower return temp with a much wider differential? For me, I'd actually like the rads to be hotter too, given how long it now takes the rooms to heat compared to the old system...

...hmmm.

Point taken on measuring the temperatures myself - I just don't have a thermometer (yet!). I take it this is best done when the heating has been on for a while?
 
It all depends when you measure the temperature. At first you get a large difference, but after all the rads become hotter. The return temperature will go up near to the flow temp.

Oversized rads help, but still eventually the return temp will be similar to the flow.
 
I have an idea, that you are over thinking it.

All rads have trv's bar the towel rail. Room stat in the bathroom?
 
I have an idea, that you are over thinking it.

All rads have trv's bar the towel rail. Room stat in the bathroom?


Part of me wishes it was that simple. Room stat is wireless and not fixed to the wall - sits in the living room (well away from the rads!) during the day and the bedroom at night.
 
It all depends when you measure the temperature. At first you get a large difference, but after all the rads become hotter. The return temperature will go up near to the flow temp.

Oversized rads help, but still eventually the return temp will be similar to the flow.


Ok, makes sense - so when should I measure the temp?

And what am I aiming for - if anything in particular?
 
Get those rads properly balanced, if captain plumb put inhibitor into the system then it could have reacted and left you with air in the system so make sure the rads are bled. After this i'd take a look at your pump, turning it can help!

Also you're right about the condense.. you want it around 55 if you want to save some cash.
The 70 degrees sound a bit too high!
 
Status
Not open for further replies.

Reply to Five degree differential btw CH outflow/return - condensing combi in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

WB 4000 installed a few months back, just balanced the 7 rads - managed to get around 15 degrees delta across most rads. Not quite the 20 degrees...
Replies
2
Views
633
Hello everyone i have a Baxi 424 combi the system working fine but the maximum tempruter on the screen reach only 57 degrees for heater and 51...
Replies
8
Views
463
So a strange conundrum regarding water temp if anyone can help resolve, would be much appreciated. Ive tried to give as much info as possible to...
Replies
1
Views
187
Hi there, I have the following system boiler setup with a low loss header and four different circuits. I've set the boiler flow to different...
Replies
19
Views
2K
M
Hello, We’ve recently moved into a fairly old, fairly big detached house (i.e. fairly draughty, but not too bad by any means) with a fairly new...
Replies
0
Views
285
MartinPod81
M
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock