Tried repressurising by turning valve on filling loop. Normally you hear water whoosh through. This time no water. Took lever off and turned with spanner then took loop off and tried again. Water is coming through so now thinking broken NRV, is there a way to fix them or could it be an issue further up the boiler (Baxi 105E)? Is there any other valves that may be switched off? Any help would’ve greatly appreciated.
 
Is there not a valve at both ends of the filling loop?.
Hi, no there is a valve at one end and a non return valve at the other
CA94A4FD-CCF1-41B1-9090-E8F7DE059E4B.png
 
Water is going through the loop but then seems to stop and not going into the boiler. I did have an external vessel added a couple years ago and has been fine until now. Does that have any affect on how you pressurise?
 
The external E.vessel shouldn't have any effect, normally with a cold system you may have 1.5 bar and then when pressure falls to ~ 0.6/0.7 bar you would re pressurize.
 
The external E.vessel shouldn't have any effect, normally with a cold system you may have 1.5 bar and then when pressure falls to ~ 0.6/0.7 bar you would re pressurize.
That’s where I am at, but water not going in so am assuming there is a blockage somewhere? Trouble is hot water keeps going off with low pressure error light 😕
 
Do you have a manual gauge on the boiler ?
 
If you want to inspect the NRV you will have to drain the boiler if your sure that you have sufficient pressure, very unlikely that you have a filling PRV like in the attachment that needs adjustment.

If a boiler sensor fault you will have to get a RGI
 

Attachments

  • Filling PRV.jpg
    Filling PRV.jpg
    11 KB · Views: 9
I have a combi boiler with flexi filling loop, valves at both ends. I topped up ok a month ago but yesterday when I opened the valves no water came through. Probably not calcium because I have a water softener.
 

Reply to Filling loop not working!! in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

If you are qualified to do a Gas Safety check on a property I assume that entails checking the boiler. If, when checking a Combi, you notice the...
Replies
9
Views
303
Hello Wondering if anyone can offer any clues please // Potterton Promax 18 // Had an E1 error code, repressurised via with filling loop //...
Replies
1
Views
287
On my Valliant eco tec boiler the pressure guage is on red when cold . I drain a radiator to correct to pressure and it works fine and stays in...
Replies
5
Views
539
Oliver1234
O
Hi Folks, Where is the place to order a Vaillant filling loop, please? I looked around on the net but can't seem to find it as a kit. I'm not...
Replies
3
Views
136
In our sealed Megalo system, when hot water tap is used (say in bathroom shower) the megaflo is taking in some fresh water, I guess to compensate...
Replies
4
Views
379
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock