Hi guys I've been ut to a boiler and it keeps firing up .when programmer is turned off .on heating and hot water.but there still power to both 2 x Port valves .and pump / boiler .there no frost stat . any ideas ?
 
How did you check the power to both valves and on what colours? normally it would be a stuck micro switch in one of the valves. If you switch it off, disconnect the oranges, turn back on and check witch orange is live then this would be the one with the stuck micro switch if the programmer is turned to off on both hot water and heating. Depending on the make of two port you can replace the micro switch or just replace the head. Whilst the head is off check the valve is freely turning.
 
checked power with volt stick .to both cables to valves both lit up and pump boiler is on with programmer off .do you think faulty programmer or you think it's a faulty valve.but if faulty valve then why power to both valves .when off ??
 
checked power with volt stick .to both cables to valves both lit up and pump boiler is on with programmer off .do you think faulty programmer or you think it's a faulty valve.but if faulty valve then why power to both valves .when off ??

well the prog sends power to the room stat which opens the zone valves when heating call, so could be easy way to test

but get a multimeter
 
Stuck micro switch.
Volt stick will be useless as there is always power to the grey. Check voltage on the brown first. If there is, then it's getting power from somewhere else. If no power on brown, but there is on the Orange. Then it's a micro switch.
 
You gas safe cruiser? We could do with knowing before we give out advise mate. We don't know who were telling what!
 
volt sticks are only good for touching boiler cases etc before you work on them,fault finding can only be done with a multi meter
 
Status
Not open for further replies.

Reply to constant boiler firing in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, I have a Vailant EcoTec Boiler with a Megaflo. These are controlled by a Honeywell controller. I have one 3 port diverter, where one of the...
Replies
5
Views
279
Hi, I have just moved into a house that has a Worcester oil fired boiler, when powered up it burns constantly even when the heat setting is off...
Replies
2
Views
574
I am having a problem with my main 24he boiler where the flame is constantly clicking on and off with the heating and when using hot water. Some...
Replies
6
Views
459
Hi all, I have a wallstar combi oil fired boiler. We got low on oil a couple of weeks ago but didn't run out. Since we've had our oil delivered...
Replies
6
Views
665
Hi there. I have Grant oil fired boiler which when cold, takes multiple times to fire up. It will run for say 20 or 30 seconds with hot exhaust...
Replies
1
Views
770
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock