Probably been asked before but cannot see where. Inside my boiler there is written nozzle 1.25 x60 W. In an envelope attached to boiler is a new nozzle marked 1.25 x 60 S are they compatible? Boiler is an old Boulter Camray.
 
The first number is capacity (tho this will alter depending on pump pressure) the second number is spray angle the letter refers to spray pattern W is what you would probably expect on your boiler as no doubt it has a riello burner?
If your going to play with different nozzles you need pressure gauge and commission analysis equipment to make sensible adjustments.
 
The first number is capacity (tho this will alter depending on pump pressure) the second number is spray angle the letter refers to spray pattern W is what you would probably expect on your boiler as no doubt it has a riello burner?
If your going to play with different nozzles you need pressure gauge and commission analysis equipment to make sensible adjustments.
Yes is a Riello boiler. Will tell my man which nozzle to bring when he pops round later this week.
Thanks
 
If I remember right, the W is a delavan nozzle and the S a danfoss. Different manufacturers use different codes for the same thing.
 
Her is coming over tomorrow so will get it clarified.
All taken a bit of a nose dive as poor soul broke his leg day before due. Any excuse not to turn up. So being curious I took out the old nozzle and is a Danfoss F7N this is marked 1.00 60 ES and 3kg/hr. Now doing a bit of conversion work I find that 1 US gallon in weight equals a smidge over 3kg. Now I think yes the 1.00 then equates to 3kg/h. Confused now as to why label in boiler and new nozzle states 1.25 which obviously means 1.25 x 3 = 3.75kg/h. Is this any big deal? Tried ringing my guy but his phone has been off for days.
 
You can’t change nozzles or anything combustion wise without the knowledge and equipment to set it up.

Different nozzle sizes, pump pressures and air settings are required to get the required output.

You can’t just change something without cocking up combustion. Even like for like nozzle changes typically require adjustments.

You need to find an oil guy.
 
You can’t change nozzles or anything combustion wise without the knowledge and equipment to set it up.

Different nozzle sizes, pump pressures and air settings are required to get the required output.

You can’t just change something without cocking up combustion. Even like for like nozzle changes typically require adjustments.

You need to find an oil guy.
I have one but like I say is somewhat indisposed. Will be weeks to get another.
 

Reply to Boiler nozzle sizing in the Oil and Solid Fuel Forum area at PlumbersForums.net

Similar plumbing topics

Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
230
P
Hi all, this is probably a daft question but I need to run my cold feed from one side of my wall mounted boiler to the other. Running it beneath the boiler is difficult with lots of obstacles, is it okay if I run soldered copper over / across the top of the boiler? It'll be about 4" off the top...
Replies
2
Views
152
I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler pump menu for either 70% or 100%, so, is the pump set at either one of two fixed speed percentages or does the pump actually vary speed, (modulate)...
Replies
1
Views
160
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
284
Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to space for servicing and changing parts if ever needing to. I am finding my decision rather hard due to the different clearances on flue runs and cupboards...
Replies
9
Views
227
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock