Leak on exchanger with boiler running maybe. Going down condense drain. Or possibly a leak in cylinder coil.
It would be normal for pressure t drop when cooling especially if exp vessel pressure incorrect
 
Your only way isolate boiler from system

And pressure test system to 6 bar if no drop it's the boiler

But I think there will be a drop
 
Your only way isolate boiler from system

And pressure test system to 6 bar if no drop it's the boiler

But I think there will be a drop

Interesting... when I pulled the flexi off the condensate and piped it in to a bucket then fired up the system from cold, we got about 2 litres of water in an hour... this seems a hell of a lot. Other information, he has a 50 litre expansion vessel for 2 floors , 21 large radiators in total.
I have been today and stuck a pressure gauge on a towel rail, isolated the flow and return at the boiler, and left the loop heating the hot water cylinder ( the ch thermostat is set to 5, so it should not kick in at all )
I have set it at 2 bar because there are some old compression fittings in the system that I dont want to blow.
So the boiler is being tested at the same time as the ch loop being isolated. I will update on the results.
Thanks for all your help so far guys.
 
Interesting... when I pulled the flexi off the condensate and piped it in to a bucket then fired up the system from cold, we got about 2 litres of water in an hour... this seems a hell of a lot. Other information, he has a 50 litre expansion vessel for 2 floors , 21 large radiators in total.
I have been today and stuck a pressure gauge on a towel rail, isolated the flow and return at the boiler, and left the loop heating the hot water cylinder ( the ch thermostat is set to 5, so it should not kick in at all )
I have set it at 2 bar because there are some old compression fittings in the system that I dont want to blow.
So the boiler is being tested at the same time as the ch loop being isolated. I will update on the results.
Thanks for all your help so far guys.

i would say thats about right how much condensate it should produce
 
50l vessel wow that's some size??? Id expect a smaller size vessel as if oversized that will cause issues mate
 
50l vessel wow that's some size??? Id expect a smaller size vessel as if oversized that will cause issues mate

its not far off (think around 35-40l) and no it wont
 
That would correspond to 24kW continuous operation and with a decently low return temperature.

Yep , the system would have been cold as it had been off and just topped up with cold mains.... So I guess it was trying to circulate and heat roughly 300 litres of cold water up to 25 degrees. Still it was surprising to see water literally spurting out of the condensate pipe,
 
When the boiler isn't on does it still drip ?
 
When the boiler isn't on does it still drip ?

I will check, obviously I am not there... frustrating, I want to call the client, but its just another job at the end of the day. By the way.. I went down the bathroom fitting route then got in to leak detection... boilers is probably my weakest discipline because i never did gas work, getting great results with sewerin audio equipment on external pipe leaks, and a ferret machine which inflates a small balloon at the head of a long cable - pressure behind lets you know when you go past the leak. We could start a leak detection forum on this site so that I can help the other way instead of you lads bailing me out all the time :)
 
Status
Not open for further replies.

Reply to boiler losing pressure - ch pipes not leaking. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no...
Replies
6
Views
277
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
292
PSxxxxxx
P
I have been facing central heating low pressure on unvented hot water RM Cylinders but can't see any leak on the PRV, expansion vessels and...
Replies
2
Views
506
losing pressure
L
Hi, Looking to see if anyone can give some advice please. My Baxi boiler has been losing pressure and I am having to top it up approx. every 4...
Replies
7
Views
784
Can central heating / gas engineer expert help me with below issue. During winter time only, I have been having issue with low pressure or...
Replies
0
Views
606
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock