50l vessel wow that's some size??? Id expect a smaller size vessel as if oversized that will cause issues mate
its not far off (think around 35-40l) and no it wont
Discuss boiler losing pressure - ch pipes not leaking. in the Plumbing Jobs | The Job-board area at PlumbersForums.net
50l vessel wow that's some size??? Id expect a smaller size vessel as if oversized that will cause issues mate
we got about 2 litres of water in an hour... this seems a hell of a lot.
That would correspond to 24kW continuous operation and with a decently low return temperature.
When the boiler isn't on does it still drip ?
Still it was surprising to see water literally spurting out of the condensate pipe,
As above the first thing to check is the expansion vessel, on a system like this it will need to be drained to check the internal pressure i would think the charge pressure would measure between 1-2 bar ? depending on meters of head , on a system that size the vessel size would need to be around 36 litres it maybe the one fitted is to small it should not be fitted laying on its side eithier and i would expect it to be red or grey in colour not blue as these ade normally used for potable water ? , all the heating pipework should be insulated and its not a good idea to have a calor gas bottle stored internally in there , check for a gas saftey certificate on the property , check the benchmark in the boiler manual ? something does not look right here. Regards kop.
View attachment 30007
Leak on the primary coil in the hot water cylinder is another thing worth checking cheers kop