Discuss Baffled by intermittent running CH pump on Heatslave 15/19 in the Central Heating Forum area at PlumbersForums.net

Messages
2
Hi hoping someone can help with this as its beginning to drive me nuts. Boiler generally well serviced and working fine, no problems with DHW. Central heating recently began to occasionally fire up as normal and run until it reached temperature set by flow control thermostat at which point burner would turn off, do its little overun thing and then go completely silent. Realising that at this point CH water pump should be running and radiators should be hot not cold, I presumed pump not running, no hot flow to radiators, so burner off as water temp limit reached. Sharp tap to pump makes it whir into life, radiators get hot and burner fires up after a bit as ch water temp drops. This sometimes happens on initial demand for heat or randomly during a cycle. My boiler service guy has mentioned I might need a new pump soon, noisy, so I fit a new pump. Unfortunately still the same problem occurs. Tapping pump sometimes makes it run. Sludge, blockage stopping pump running is my initial thought but system relatively clean, dosed up and magnaclean type filter fitted. Put a plug on pump and plug it into a wall socket all works fine including boiler CH. Being mostly an electrician I get my meter out and discover only 75v ish on control board pins that suppy CH pump when its misbehaving and the requisite 240v when working as it should. I have a spare control board removed from a decommissioned but working heatslave so I swapped boards - same problem. I have also replaced the flow control thermostat like you do as one gets more baffled and could change the high limit thermostat, surely both control boards cant have the same fault?
Any ideas? Ive tried all the obvious, bypassing room thermostat, shorting out thermostats.
Thanks
 
Does it have the built in clock? If so it will.be that.
It doesn't have internal clock
Does it have the built in clock? If so it will.be that.
Does it have the built in clock? If so it will.be that.
It doesn't have the internal clock and i have bypassed all that. Too easy
I have actually been testing my spare board and have discovered open contacts, no continuity, on one relay that should be closed ( although to the eye it looks closed) like all the other 15 identical dpdt switches in all 4 relays, it even traces back to the pump terminals. If the board in use is the same I may have found the problem and although unlikely both boards do have the same fault. Intermittent partial contact in the relay could definitely be giving me 70ish volts at the pump instead of 240
 

Reply to Baffled by intermittent running CH pump on Heatslave 15/19 in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler pump menu for either 70% or 100%, so, is the pump set at either one of two fixed speed percentages or does the pump actually vary speed, (modulate)...
Replies
1
Views
137
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to run the water line underneath. There are existing drain (and who knows what) pipes running along the same wall so I'm nervous about digging too far...
Replies
6
Views
215
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
237
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
4
Views
390
I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about this one. Granddaughter just moved house and this valve decided to leak when it was closed. When open its fine. Normally I have repacked the gland on...
Replies
7
Views
168
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock