Hi hoping someone can help with this as its beginning to drive me nuts. Boiler generally well serviced and working fine, no problems with DHW. Central heating recently began to occasionally fire up as normal and run until it reached temperature set by flow control thermostat at which point burner would turn off, do its little overun thing and then go completely silent. Realising that at this point CH water pump should be running and radiators should be hot not cold, I presumed pump not running, no hot flow to radiators, so burner off as water temp limit reached. Sharp tap to pump makes it whir into life, radiators get hot and burner fires up after a bit as ch water temp drops. This sometimes happens on initial demand for heat or randomly during a cycle. My boiler service guy has mentioned I might need a new pump soon, noisy, so I fit a new pump. Unfortunately still the same problem occurs. Tapping pump sometimes makes it run. Sludge, blockage stopping pump running is my initial thought but system relatively clean, dosed up and magnaclean type filter fitted. Put a plug on pump and plug it into a wall socket all works fine including boiler CH. Being mostly an electrician I get my meter out and discover only 75v ish on control board pins that suppy CH pump when its misbehaving and the requisite 240v when working as it should. I have a spare control board removed from a decommissioned but working heatslave so I swapped boards - same problem. I have also replaced the flow control thermostat like you do as one gets more baffled and could change the high limit thermostat, surely both control boards cant have the same fault?
Any ideas? Ive tried all the obvious, bypassing room thermostat, shorting out thermostats.
Thanks
 
Does it have the built in clock? If so it will.be that.
It doesn't have internal clock
Does it have the built in clock? If so it will.be that.
Does it have the built in clock? If so it will.be that.
It doesn't have the internal clock and i have bypassed all that. Too easy
I have actually been testing my spare board and have discovered open contacts, no continuity, on one relay that should be closed ( although to the eye it looks closed) like all the other 15 identical dpdt switches in all 4 relays, it even traces back to the pump terminals. If the board in use is the same I may have found the problem and although unlikely both boards do have the same fault. Intermittent partial contact in the relay could definitely be giving me 70ish volts at the pump instead of 240
 

Reply to Baffled by intermittent running CH pump on Heatslave 15/19 in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hi, I have a Vailant EcoTec Boiler with a Megaflo. These are controlled by a Honeywell controller. I have one 3 port diverter, where one of the outputs goes to a 2 port diverter prior to the Megaflo (I believe this is some safety feature). I have run into an intermittent problem where some...
Replies
5
Views
225
I just had a quote for a new boiler install as follows I dont undertand why a 15-60 boiler pump is needed and a 25-100 pump is needed as well I currently have an ideal mexico 2 heat only boiler - It has one DAB pump on the boiler return and a 2 port valve at the flow pipe to allow for heating...
Replies
3
Views
534
    • Like
Hello, my Mothers heating failed in the recent UK cold snap. I found the pump was stuck. I have a question about pump orientation. The existing pump flows downwards. The manual for the proposed replacement recommends that it should pump upwards. This would involve rearranging the flow &...
Replies
8
Views
606
Hi Folks, I have a challenge with a Main Eco Elite 30 Combi which is short cycling on the CH. Water works fine. As soon as you have call for heat, the boiler fires up, modulates, but jumps very quickly (about 30 seconds or so from 40'ish all the way to 70, burner disengages putting it the...
Replies
6
Views
368
Last May had a new Greenstar 4000 boiler fitted and only recently started using the heating. Once the set room temperature is reached the boiler modulates (presumably) and stays running for very long periods (many hours) but the circulating water is only luke warm (about 35 degrees) Any heating...
Replies
12
Views
787
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock