Hello we are having issues with our Ariston gas boiler, it’s not a combo boiler, we have a separate hot tank. The boiler trips off when the hot water boosts. We store pans in the cupboard under the boiler and I suspect we have knocked a valve. I have taken pictures, would anyone be able to tell me if the valves are positioned correctly?
 
Sorry forgot to attach them….I’m stressing out 🤦🏻‍♀️
 

Attachments

  • 48FBF567-2EB3-4BD9-9334-27315034FC47.jpeg
    48FBF567-2EB3-4BD9-9334-27315034FC47.jpeg
    358.5 KB · Views: 15
  • BBD79C23-EE15-49DA-A2D9-B43DBEB6B5B3.jpeg
    BBD79C23-EE15-49DA-A2D9-B43DBEB6B5B3.jpeg
    211.9 KB · Views: 14
Difficult to say, but one filling valve looks off. Have a look in the cylinder cupboard at the motorised valve(s) for water egress from spindle and ingress into the valves.
 
It’s possible it’s overheating on hot water, so could just be a fault somewhere. On the zone valve in the cylinder cupboard, they’ll be a lever , select hot water on the programmer, and check out the lever, if there’s resistance then the valve isn’t opening up as it should. This valve will be where the pipes enter the cylinder.
 

Reply to Ariston boiler cuts off when hot water boosts in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
125
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
276
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
224
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
443
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
114
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock