I hope someone can comment on my setup and let me know if I have a problem or not !

I have old gas central heating system, all was working:

gravity fed hotwater heating
radiators via pump.

We then had back boiler fitted to wood burner and replacement cylinder with 2 coil element type fitted by professional plumber, so water can be heated by gas or wood.

Can't seem to heat water from boiler

Can gravity work fast enough to transfer the heat, from cold.

When I try there is lots of scary banging and sound of water rushing through pipes, the input of cylinder gets too hot to touch, the bottom exit gets slightly warm, Water clearly not flowing through it properly.

Even with the radiators on, hot water doesn't seem to get heated, but as the pump is pulling water through radiator circuit it's hard to see why it would flow down into the hot water circuit, but no banging or venting but water does not get heated

As a layman I can think of three possibilities

1/ The water heats up too quickly to create circulation current, boils and vents off
2/ There is a Honeywell valve on exit - I replaced the head, and checked the spigot turns, this seems to be OK, and does activate when powered - and tried locked open - seems to be ok but could be blocked
3/ An air block in hot water heating element

What I want is to be able to heat water from boiler without radiators being on....

Should gravity be enough for water heating only

As there are two parallel circuits (rads/pumped+ water/gravity), it's hard to see how they can both exist together...

If you made it this far - thanks for reading - any comments very welcome

Matt
 
You've had a motorised valve fitted to your cylinder, it is now NOT gravity.
DO NOT USE until you have got the fitter back, you are heating water against a closed valve.
 
Nothing wrong with a motorised valve on a gravity hot water return.
It should be wired up as a "c plan" incorperating a white wire in the head.
 
Your right, just never came across C plan, but do remember them.
Still, banging noises there's a problem
 
You've had a motorised valve fitted to your cylinder, it is now NOT gravity.
DO NOT USE until you have got the fitter back, you are heating water against a closed valve.

When I set the controller to call for hot water it activates the valve so valve is open.

The logic being in winter we can have radiators on without the boiler heating water. The wood burner produces more than enough heat to heat the water, but only heats lounge so we need radiators on...

In summer, we want the opposite - no wood burner, no radiators, but gas heated water..

So in summer, controller calls for hot water, valve does activate, boiler heats up, after maybe 2 minutes, clanging, whoosh, and boiler turns off due to it's thermostat.
upper pipe too hot to touch, lower pipe slightly warm. I have tested with Honeywell head off and manually turned spigot anti-clockwise

Should gravity work - or do I have blockage or air lock...
 
Why is the flow pipe rising from the tee to the coil?
Sorry to tell you this, but your plumber doesn't know much about pipework
Another thing is some cylinders have coils that only suit pumped water.
You have to order a cylinder that is suitable for gravity circulation that solid fuel fires require
 
Gravity should work no bother at all and fairly fast.
 
Not all cylinders are suitable for gravity-circulation systems. Most of them these days assume a pumped system. Check you've had the right type installed.

Air locks will, of course, prevent circulation but the installed pipework should have the correct gradients and vents to ensure they don't occur.

Looking at your photo. I would expect to see the hot water rise from the boiler, turn right flow down a slight gradient (your's is upward) through the Honeywell (?) valve, into the top of the heat exchanger where it transfers heat to the cylinder, cools, and emerges from the return near the bottom.

The upward gradient on the upper pipe, which you call 'return' and I think should be 'flow' would be a great place for an air lock to form.

If anything I've guessed/suggested conflicts with the manufacturer's installation instructions then I'm wrong, follow the MI!

Edit: While I was typing this Best posted essentially the same points. He was more economical with his words, and I paused to get a mug of tea midway, so he won.
 
Last edited:
Why is the flow pipe rising from the tee to the coil?
Sorry to tell you this, but your plumber doesn't know much about pipework
Another thing is some cylinders have coils that only suit pumped water.
You have to order a cylinder that is suitable for gravity circulation that solid fuel fires require

I am not a plumber but understand the pipe has to rise for gravity to work. Around the back of the boiler (photo doesn't show) are similar 28mm pipes for wood burner circuit which works well.
 
I am not a plumber but understand the pipe has to rise for gravity to work. Around the back of the boiler (photo doesn't show) are similar 28mm pipes for wood burner circuit which works well.

You have me confused. I thought you said the solid fuel stove won't heat the hot water?
 
I am not a plumber but understand the pipe has to rise for gravity to work.

It's more complicated. One needs the correct combination of temperature gradients, pipe gradients and points of heat extraction and input for 'gravity to work'.

Whether a pipe rises or falls depends on which direction the water is travelling inside it.
 
Last edited:
gravity fed wood burner circuit works
(can't see pipework on photo - on back of cylinder, same 28mm fittings)

gravity DHW does not seem to work - seems circuit is blocked

I understand the logic and location of the airlock on heat exchanger input at top

To remove I need to force water through the coil ?. Does it matter which direction (ie from vent, or supply in attic). Isn't there a danger I'll just flush water through the boiler, bypassing the cylinder, as it offers lower resistance

Would cracking open the bolt remove airlock - I suppose not as not much pressure to push air out, unless I heat the system, but knowing me if I did that I'd spray boiling steam into my face, so not too keen in that idea....
 
If a pro fitted the cylinder you need to get them back to fix the problem. This will involve first checking that the cylinder is suitable for gravity circulation. If so then I would expect them to move the tee feeding the top part of the heat exchanger upwards to get the gradient correct. If it's not a gravity cylinder, they need to fit a circulating pump for the HW or replace the cylinder depending on which you are happy with (and paid for).

Musings: This is a strange mistake for a pro to make. They've used end-feed fittings and and the soldering looks okay but they've left an inverted trap in a gravity-circulation system. Did they assume that your boiler had a pump on the HW circuit, perhaps?

Would cracking open the bolt remove airlock - I suppose not as not much pressure to push air out, unless I heat the system, but knowing me if I did that I'd spray boiling steam into my face, so not too keen in that idea..

. . . and while you were screaming in pain water would continue to pour out of the open joint causing a remarkable amount of damage to your house in the process. Damage that probably wouldn't be covered by your home insurance policy.
 
Last edited:
I still remain confused! You say the "gravity fed wood burner" circuit is connected to the rear coil and is working. But then you say the " gravity DHW " isn't working? There is no such term as that in a heating system. Your coil that isn't heating must be from another boiler, - gas I think you said? Gravity circuits not allowed on new gas or oil installs now.
But as you are not a plumber, you could make a mistake.
The job has clearly not been done by someone who understands the basics of connecting to a cylinder coil. Even if that front coil was on a pumped circuit, it is wrong and air will be trapped in top of coil.
I would get the plumber back who did the job to see what he says is wrong with his work. The job probably needs another plumber who is experienced in gravity circuits and dual heating link ups to check all the pipework.
 
Last edited:
I still remain confused! You say the "gravity fed wood burner" circuit is connected to the rear coil and is working. But then you say the " gravity DHW " isn't working? There is no such term as that in a heating system. Your coil that isn't heating must be from another boiler, - gas I think you said? Gravity circuits not allowed on new gas or oil installs now.
But as you are not a plumber, you could make a mistake.
The job has clearly not been done by someone who understands the basics of connecting to a cylinder coil. Even if that front coil was on a pumped circuit, it is wrong and air will be trapped in top of coil.
I would get the plumber back who did the job to see what he says is wrong with his work. The job probably needs another plumber who is experienced in gravity circuits and dual heating link ups to check all the pipework.


There are two heat sources and two coils both for domestic hot water (DHW), wood and gas.

The system was installed many years ago, I did test it then, but not really used gas for hot water much due to wood burner and unlimited free wood. We also use the immersion heater as we have PV solar power that provides free electricity. (sometimes!)

Anyway I slackened off the 28mm input to cylinder and air hissed out and carefully heated up the system to create more pressure.

It seems to all work now - I can hear the boiler boil but it doesn't vent, and both ends of the coil now get hot soon after system is turned on.

After about 5 minutes the boiler turns off due to thermostat control, and when cools due to heat transfer it comes on again. I guess this regular on/off/on/off is an unavoidable fact for gravity fed systems as there is not much water in the transfer system when the radiators aren't being used

So a massive thanks to everyone who commented.

I now have a working system and a much better understanding of how my C-Plan system works
 
Anyway I slackened off the 28mm input to cylinder and air hissed out and carefully heated up the system to create more pressure.

That was a dangerous thing to do. You are lucky you didn't injure yourself.

It seems to all work now - I can hear the boiler boil

You shouldn't normally be able to hear water boiling inside a 'boiler'.

both ends of the coil now get hot soon after system is turned on.

One end should get hot, typically 75°C. The other should start cold and gradually rise to 60°C over a period or an hour or so, at which point the boiler should stop supplying heat.

After about 5 minutes the boiler turns off due to thermostat control, and when cools due to heat transfer it comes on again. I guess this regular on/off/on/off is an unavoidable fact for gravity fed systems as there is not much water in the transfer system when the radiators aren't being used

If the system is installed and working correctly the cylinder should heat constantly without the short-cycling you observe.

In my opinion, your system is not properly installed and is neither safe nor efficient. You really should get a competent heating engineer to review it and fix any issues.

Also, it doesn't normally make financial sense to use PV-generated energy to heat water if you can use gas instead and sell the surplus electricity.
 
That was a dangerous thing to do. You are lucky you didn't injure yourself.



You shouldn't normally be able to hear water boiling inside a 'boiler'.



One end should get hot, typically 75°C. The other should start cold and gradually rise to 60°C over a period or an hour or so, at which point the boiler should stop supplying heat.



If the system is installed and working correctly the cylinder should heat constantly without the short-cycling you observe.

In my opinion, your system is not properly installed and is neither safe nor efficient. You really should get a competent heating engineer to review it and fix any issues.

Also, it doesn't normally make financial sense to use PV-generated energy to heat water if you can use gas instead and sell the surplus electricity.


Points taken

However with solar power you are paid for all the power you generate, whether you use it locally or feed it back to grid, so not a choice to sell or use, you either sell and use or sell and don't use...

So on a sunny day it produces 3Kw. I am paid for 3Kw regardless. I have choice to dump it in immersion heater, or if I don't use it it flows into grid. Either way makes no difference in terms of £, but one provides tank full of hot water.
 
However with solar power you are paid for all the power you generate, whether you use it locally or feed it back to grid, so not a choice to sell or use, you either sell and use or sell and don't use...

Interesting. My comment was based on this:

Feed-in tariffs: get money for generating your own electricity: Overview - GOV.UK

, which seems to describe a generation-tariff (as you describe) plus a 4.85p/kWhr export-tariff, which is more than gas costs at the moment. Evidently you either don't have an export meter or have another type of feed-in agreement.
 
My solar system was installed 8 years ago - the contracts were much more "interesting" then, and the contract holds for 25 years.

Would be a very different contract for a new system today
 
Boiler is coming under pressure and forcing gravity flow to work, I reckon. You removing air was only a temporary sort of fix, but not correct or a solution. Get a heating engineer in to repipe the fault we mentioned and anything else they find wrong
 
..... Evidently you either don't have an export meter or have another type of feed-in agreement......
Another GOV scheme to get the ball rolling .
(Won't be wanting a Smart meter (IF it can cope !))
... Combining heat sources was expensive to do right ..(Safely)
 
Status
Not open for further replies.

Reply to Sanity check..., gravity hot water and pumped radiators, should they work together in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

J
Hi Can somebody tell me if a standard heat source pump installation uses a pressurized hot water tank? Or will the pressure for the hot water be...
Replies
1
Views
459
  • Question
My disabled daughter’s hot water has stopped working. It’s a relatively modern Potterton boiler with an indirect sealed hot water system and a...
Replies
12
Views
920
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
217
M
Hello, We’ve recently moved into a fairly old, fairly big detached house (i.e. fairly draughty, but not too bad by any means) with a fairly new...
Replies
0
Views
283
MartinPod81
M
Hi, I'm looking for a water pump to pump water from a storage tank at a constant 3 bar pressure. It's at a campsite I run that's at the bottom of...