Koogatubac

Boiler had no hot water but heating, fault was diverter valve.

Replaced that, now it fires on DHW however gets up to overheat and cuts out.

Replaced the temp stat however didnt fix the boiler. The old stat probe was thick in sludge, phoned viessman, they recon its a circulation problem and recommend a powerflush.
Anyone have any ideas?
 
Blocked hex ? Fill her up with x400 and let it cook for a week. Would also check pump, does pressure skyrocket? Any idea which over heat is kicking in? Main or pipework?
 
Its had ALLSORTS changed, boss said it was a new pump. Took it off and didnt look that bad, plus it span croppie :) merchants werent open and didnt have any cleaner, my next thought was either heat ex or pump chemicals in and give it a good flush. On heating its gained to 98* and never overheated, however when i changed the overheat stat on heating it rises to 83* max.

Ive worked on other boilers and they all have dirt in, but i wouldnt of said powerflushing should solve the problem :S
 
I defo clean it's the plate . 1/2 tub of flux is good cleaner when your stuck!
 
Oh you poor soul, although i cant help but smile.

viessmann boilers go hell with a spec of sludge.
 
Haven't had much dealing with them on repairs but didn't rate the vitodens 100 I serviced the other day much, maybe the 200 is a different kettle of fish?

plastic worcester like hydro blocks and the condensate trap was right at the back, awkward to get out etc

looked cheap and nasty really, thought they were supposed to be a reputable boiler?
 
Last edited:
Cheers guys, ill let ya's know what happens when i get hack there!
 
Which is strange as they claim sludge won't touch there heat exchangers lol


On the other hand they say any sludge in the system and they wont cover you.
on training they advice you to repipe system on boiler replacement.

having had a few viessman off the wall and flushed out (over ten) for a previous employer

they fire aggressively and bake the sludge into hard deposits around the hex.
 
hyjubama.jpg
went to a vitodens 100 regular boiler which had been dry firing and this was the out come! Was on a one pipe system with a blockage in it!!
a4ede5uv.jpg
 
as previously said is the hex been fully vented. i had this once had to attach a hose and run it outside off the cock.
 
I have had to deal with this boiler twice and in both case ended up stripping the boiler and cleaning each bit on it. The sludge sticks to every part on it.
 
Cleaned the heat ex today, was absolutely black!! Make a big difference however still overheats eventually, ordered a new heat ex, fitting thurs morning! Keep u guys informed
 
Ok so put in new heat exchanger, hasnt fixed. 5yr old boiler, got longest history of repairs, all parts have been changed some have been changed twice!
Solution - new worcester going in!
 
The 100 are just easier to replace. Fan, gas valve pcb, sensors thermisters = rubbish
 
Well i have a poor view of them. Every part is easy to change mind compared to some boilers which leave your hands getting chewed off
 
Status
Not open for further replies.

Reply to Viessman vitodens 100 problem in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

hey all, Based in South England, UK. Hope this is the correct place to ask and that ive added all the required info/images. I had an old boiler...
Replies
2
Views
1K
Hi Folks, I have a challenge with a Main Eco Elite 30 Combi which is short cycling on the CH. Water works fine. As soon as you have call for...
Replies
6
Views
437
Hello all, I have a WorcesterBosch Greenstar 42CDi classic combi, which is providing DHW fine, but not heating. Was working fine in spring...
Replies
11
Views
1K
B
Hello, I hope someone can give some advice with this problem. I have a Vaillant ecoTec plus 418 with Drayton MA1 mid-position actuator, Drayton...
Replies
2
Views
770
We are a few months into our Viessmann Vitodens 100-W 19KW Heat Only boiler and it is working fine. We replaced an old 1999 Baxi. Our house is a 2...
Replies
5
Views
3K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock