Hi i wonder if anybody can help with my query, the only gas appliance i have is a ideal Mexico super cf455 boiler, historically my gas usage was 12kwatts a year it is now double that figure at around 24,000 kwh, the boiler is only on for very short amounts of time as in not left on all day/night, i have left it off for 24 hours and checked the meter, no gas was used. the boiler seems to be using 1.7 units which i calculate as 53 kwh in one hour of run time. i have spoken the the engineer who services the boiler and he said the unit would not burn double the the amount of gas and thinks it might be the gas meter, any help would be much appreciated. there is no gas cooking.
thanks
 
Where have you got your figures from?
The first is in Kw the second in Kwh. We need to clear up what you're saying first of all so we are all in the same units.

The 1.7 units:
Is that meters cubed? If it is then it doesn't add up to 54 Kwh.

If you can clarify those things, we can help more.
 
Where have you got your figures from?
The first is in Kw the second in Kwh. We need to clear up what you're saying first of all so we are all in the same units.

The 1.7 units:
Is that meters cubed? If it is then it doesn't add up to 54 Kwh.

If you can clarify those things, we can help more.
hi,
thanks for reply.
a 45 minutes example from day before
reading before on 4228.664 M3
reading after 4229.941 M3
gas boiler only on . no cooking.
thanks
 
hi,
thanks for reply.
a 45 minutes example from day before
reading before on 4228.664 M3
reading after 4229.941 M3
gas boiler only on . no cooking.
thanks
If we use that and calculate the Kwh, it is 19.298. That's using the correction factor/calorific value and so on that I use currently.

I thought you only had the one gas appliance?
 
hi,
thanks for reply.
a 45 minutes example from day before
reading before on 4228.664 M3
reading after 4229.941 M3
gas boiler only on . no cooking.
thanks
So you are using 1.28 m^3 in 45 minutes, which is 1.7m^3 per hour. That's about 19.3kWhr per hour.

If you have the boiler on at that rate for five hours a day for the four cold months of the year you'd use 11,740 kW hr.

This year has been a bit colder (in terms of degree days) than last year so your consumption may well be up by, say, 20% or so because of the weather this season.

Where did the '24,000 kwh' figure come from?
 
If we use that and calculate the Kwh, it is 19.298. That's using the correction factor/calorific value and so on that I use currently.

I thought you only had the one gas appliance?
sorry, yes only that gas appliance. Electric oven and hob.
does that usage sound alot for 45 mins for that boiler?

I had used following reading 4229.941 -4228.664 = 1.277 for 45 mins
or 1.7 units per hour
1.7 units x 2.8 x 1.02264 x39.1 /3.6 = 52.86 kwh
calcs from Octopus energy

thanks
 
So you are using 1.28 m^3 in 45 minutes, which is 1.7m^3 per hour. That's about 19.3kWhr per hour.

If you have the boiler on at that rate for five hours a day for the four cold months of the year you'd use 11,740 kW hr.

This year has been a bit colder (in terms of degree days) than last year so your consumption may well be up by, say, 20% or so because of the weather this season.

Where did the '24,000 kwh' figure come from?
 
sorry, yes only that gas appliance. Electric oven and hob.
does that usage sound alot for 45 mins for that boiler?

I had used following reading 4229.941 -4228.664 = 1.277 for 45 mins
or 1.7 units per hour
1.7 units x 2.8 x 1.02264 x39.1 /3.6 = 52.86 kwh
calcs from Octopus energy

thanks
I think that calculation is for an imperial meter, but you have a metric meter. it should come out at 19kWh ish according to an online calculator I used!
 
i had always worked around 12,000.
24,000 is the figures on my bills consumed.
i have spent ages going through them and adding up in a spreadsheet.
it went wrong in 2020 when they put in a weird estimate which suggested I would use 85,000 kwh per year!
so the "estimate" has been wrong ever since so difficult to gauge plus increased unit rates
however, i have now been through my "actual use" and it is adding up to over 24,000KWH.
 
i had always worked around 12,000.
24,000 is the figures on my bills consumed.
i have spent ages going through them and adding up in a spreadsheet.
it went wrong in 2020 when they put in a weird estimate which suggested I would use 85,000 kwh per year!
so the "estimate" has been wrong ever since so difficult to gauge plus increased unit rates
however, i have now been through my "actual use" and it is adding up to over 24,000KWH.
hi
what is the digital meter calculation please.
 
sorry, yes only that gas appliance. Electric oven and hob.
does that usage sound alot for 45 mins for that boiler?

I had used following reading 4229.941 -4228.664 = 1.277 for 45 mins
or 1.7 units per hour
1.7 units x 2.8 x 1.02264 x39.1 /3.6 = 52.86 kwh
calcs from Octopus energy

thanks
I don't know what that 2.8 figure is for?

If you are converting from an imperial meter which measures cubic feet, then the conversion is not 2.8, it would be
0.0283168 (0.028 for short/ease).
 
hi
what is the digital meter calculation please.
someone may have hit the nail on the head!

bill says for 39 days
consumption 149.6 units (100s of ft3)

then there is the calculation 149.6 x 2.83 x 1.02264 x39.1 = 4701.2
4701.2 kwh used

but if my meter is digital (reading for example 04229.941m3)
does this mean they are converting a m3 reading which is already in m3 ? do you think?
 

Reply to gas usage doubled to 24,000kwh in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler...
Replies
1
Views
173
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
532
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
187
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
414
Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to...
Replies
9
Views
268
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock