Hello,

I have UFH set up with a HIU in my flat.

My issue is that one zone (Bedroom 2) does not heat up. All other zones working and heating as expected.

Have checked the relevant thermostat, as well as the electrical actuator for the specific zone. Both look ok

Checked return pin valve - closed and stiff. Pulled pin up manually however still no heat (seemed odd) in bedroom 2 or on the flow pipe leading to zone from manifold. Pin also stays down when pushed in manually (no spring back)

My assumption is that the pin valve needs replacing...
1. Is this a sensible next step given above?
2. If so, how do I do it? I have tried a Hex socket but the blue actuator adapter connection wont let me get to the actual valve (gap not wide enough to take the socket). Pic attached

Cheers
 

Attachments

  • 1674561421951.jpg
    1674561421951.jpg
    297.3 KB · Views: 11
  • 1674561421964.jpg
    1674561421964.jpg
    314.8 KB · Views: 12
Push it down/pull it up a few times to ensure it’s free. Check flow meter to ensure it’s not closed.

If that fails, isolate manifold. Depressurise, remove pin/actuator and see if it’s come apart inside manifold. Could possibly repair it.
 
Push it down/pull it up a few times to ensure it’s free. Check flow meter to ensure it’s not closed.

If that fails, isolate manifold. Depressurise, remove pin/actuator and see if it’s come apart inside manifold. Could possibly repair it
Thanks for the input @Timmy D.

I've pushed and pulled and the pin does move when I manually manipulate in this way with pliers.

How would you check a flow meter? I've observed the meter when the heating is on and it reads zero for the zone/pipe in question.

Have now isolated and depressurised. Could you advise how I get the pin/actuator out to see inside the manifold? I had assumed hex socked but the blue adapter ring stops me getting onto the valve to unscrew
 
It’s likely that the blue head adapter unscrews to give spanner access. Then unscrew it.

Have you got a pic of full manifold showing all flows and returns. Usually the flow meter is separate opposite the actuator and can be adjusted, but it looks like yours might be inline with the actuator. You usually twist them to change the flow. Yours may be set closed or stuck closed.
 
It’s likely that the blue head adapter unscrews to give spanner access. Then unscrew it.

Have you got a pic of full manifold showing all flows and returns. Usually the flow meter is separate opposite the actuator and can be adjusted, but it looks like yours might be inline with the actuator. You usually twist them to change the flow. Yours may be set closed or stuck closed.
@Timmy D
Indeed. Based on what I've seen online this may not be a standard install. I've previously tried to get at the flow meter but it seems easier said than done - looks like it's encased in metal..
Unfortunately twisting the blue plastic adapter doesn't seem to work. Also tried to lever it off with a flathead - it's on there pretty good
Pics attached
 

Attachments

  • 1674580422782.jpg
    1674580422782.jpg
    326.9 KB · Views: 11
  • 1674580422794.jpg
    1674580422794.jpg
    386.8 KB · Views: 16
  • 1674580422805.jpg
    1674580422805.jpg
    406.6 KB · Views: 15
Get the blue head adapter off and unscrew the actuator.

There must be a way to adjust the flow. It’s either on the actuator (just looked at what I believe is the manufactures website, some of their actuator adjust this way, I don’t think yours do, pics from site attached).

Or undo the screwed cap on the below manifold on the corresponding loop and you may find an adjustment pin.

D2643505-5CF6-46D5-AFE0-1C0D9D69D940.png
D30CCE5C-E3D1-49D8-9E08-049CDA08B904.png
83AAAFAA-3931-44FF-803D-9A42BE55A78A.png
 
Get the blue head adapter off and unscrew the actuator.

There must be a way to adjust the flow. It’s either on the actuator (just looked at what I believe is the manufactures website, some of their actuator adjust this way, I don’t think yours do, pics from site attached).

Or undo the screwed cap on the below manifold on the corresponding loop and you may find an adjustment pin.

View attachment 81070View attachment 81071View attachment 81072
ok, cheers. Will have a look at that

Finally got the valve out. Looks intact - but should presumably move when you push the pin in?!
 

Attachments

  • 1674583695737.jpg
    1674583695737.jpg
    153.7 KB · Views: 17
  • 1674583695751.jpg
    1674583695751.jpg
    129 KB · Views: 12
ok, cheers. Will have a look at that

Finally got the valve out. Looks intact - but should presumably move when you push the pin in?!

So you’re saying that the jumper/washer/internal piece doesn’t move when you push/pull the external pin?

Yes, they should move in unison.
 
So you’re saying that the jumper/washer/internal piece doesn’t move when you push/pull the external pin?
Yep, that's it. I've uploaded a video to illustrate for ref if anyone has a similar issue in the future.

Primary issue now resolved (no heat to zone).

Next job is to figure out how to increase the zone temperatures (the floors/rooms warm up but don't heat as much as I'd like them to)
 

Attachments

  • VID_20230201_095740.mp4
    68.6 MB

Reply to How to replace UFH return pin valve in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
139
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
480
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
339
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
245
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock