Search the forum,

Discuss Which is the more powerful pump? in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Messages
62
Hi all just picking your brains 2 pumps with flow rates of 3.8 and 5.7 which is the more powerful, also can you fit a commercial pump into a domestic system?
 
5.7 is a higher flow rate but might be the same pressure as the 3.8

Need more info
 
Are we taking heating or water and what’s the problem with the existing set up ?
 
Hi all well here is the problem in it's entirety, when we bought our house ( 2 bedroom ) up and down, the central heating was by way of a back boiler it had 3 radiators upstairs and 3 downstairs, but because of concrete floors downstairs, as it was previously council owned, the downstairs radiators were on what is known as dead legs. I put in a feature fireplace and ( as then you did not have to be gas safe ) I put a wall hung boiler in the bathroom and installed a fully pumped15mm pipe "Y" plan system which was open vented. The pump was a bog standard Grundfos one and as the boiler was getting long in the tooth I decided to get it replaced, in doing so I noticed that there was something wrong with the pump ie the body could be scraped with a knife and large chunks could be cut out of it so that was replaced with a new one. the chap who replaced the boiler put in a pressurised system. Not long afterwards I decided to take out the radiator in the bathroom and install a heated towel rail, now this was a big one, I noticed that the radiator in the entrance way was not getting hot at all but just left it . After a while I decided to get a Grundfos Alpha 2 L pump but it made no difference, so I then decided to get a Grundfos alpha 3b and take out the radiator in the sitting room and put in a big 2 panel one , for got to mention that I replaced all of the rads in the house with modern single panel ones the full length of the windows and put the bedroom ones on TRV's,. this is where everything went wrong, the Alpha 3b is setup and balanced using the 2 apps, Go Remote and Go Balance but these would not touch my system and could not balance it no matter what I did, I tried my best to manually balance the system, as I know how to, but that made no difference either, the entrance rad would not heat up the big one in the sitting room would not heat up the kitchen one would just get warm to the touch (these are all the rads on the dead legs) upstairs ones were getting quite warm, now I am left with the upstairs heating ok but nothing downstairs ( there are no air locks) I have come to the conclusion that the Alpha 3b is not powerful enough to pump the water round the system, I have spent quite a bit of time and money on pumps to try and rectify this problem but to no avail, so if any one out there knows of a powerful pump that can do the job drop me a line, one other thing I have come across is a Super 25 pump but it is a commercial one is there any reason why I cannot install it in my system obviously I would have to extend the port dimension as it is 180 mm not 130.
 
:D a standard 15-60 eg ups2 or ups3 will be more than good enough for your system but it sounds like you have either a design issue or a blockage changing the pump
Won’t change much
 
The Alpha3 may display the head in meters, the flowrate in M3/hr and the power in watts, does it?.
What control mode are you running it on, CC (constant curve), CP (constant pressure) or PP (proportional pressure) ?.
 
:D a standard 15-60 eg ups2 or ups3 will be more than good enough for your system but it sounds like you have either a design issue or a blockage changing the pump
Won’t change much
Problem is it is the same design as before the only thing I have done is replaced the bathroom rad with a heated towel rail and replaced the flatpanel rad in the sitting room with a big double panel one, i know for certain that there is no blockage in the system because when I did the work I used the rad valves to get water down the dead legs on both sides of the rads before I connected then up.
 
The Alpha3 may display the head in meters, the flowrate in M3/hr and the power in watts, does it?.
What control mode are you running it on, CC (constant curve), CP (constant pressure) or PP (proportional pressure) ?.
yep head in meters and the flowrate in M3/hr and power in watts and it is on proportional pressure
 
It’s not a pump problem as it’s very unlikely you have two bad pumps out the gate

You sure it’s not a one pipe system?
 
It’s not a pump problem as it’s very unlikely you have two bad pumps out the gate

You sure it’s not a one pipe system?
I'am not saying the pumps are bad, I am saying they are not powerful enough to pump the water round the system because of the dead legs, I am going to do an experiment tomorrow and will let you know the outcome
 
Unless the dead legs are connected together which your system would never work these dead legs don’t matter as there just capped off services
 
I'am not saying the pumps are bad, I am saying they are not powerful enough to pump the water round the system because of the dead legs, I am going to do an experiment tomorrow and will let you know the outcome
Can you get any readings from the pump as it will reveal quite a lot IMO.
 
Shaun OP is saying dead legs when what he actually means is drops.
This is a case of a little knowledge is a bad thing!

Agreed kinda guessed that also probably old back boiler with I’m guessing when removed flow and return linked hence why no flow to the rads as it’s talking the easiest route
 
Give us the numbers then please , and the PP setting, should be a good indication of whats happening.
Hi all well what I did was shut off all the upstairs rads so just the downstairs rad were open, set the pump to constant curve @100% operating mode @Max estimated head was 5.9 m and the speed was 5295.
The sitting room rad (which is the new big one) got hot but I could not balance it, the kitchen one which was cold or just barely warm was heating up but did not get hot, the entrance rad was still cold, my conclustion is either the pump cannot push the water round the system (all the above rads are on dead legs) or there is a blockage or trapped air in the return legs, which all I can do is bleed the return legs (not the rads) and see if it makes any difference, if it does not then the only solution is to find a much more powerful pump, if anyone can tell me what would happen if I fitted a commercial pump, of which I have the specs :- UP UPS 14m3/h 13m head pmax 10bar
UPS 25-80 :- 8.5m3/h 7mhead
 
Agreed kinda guessed that also probably old back boiler with I’m guessing when removed flow and return linked hence why no flow to the rads as it’s talking the easiest route
When I took out the back boiler I renewed the upstairs pipework to 15mm flow and return, the downstairs (as the boiler is upstairs) was put on dead legs or drops 15mm flow and return
 
Do the test again but shut all but one rad eg one problem one does that get hot ?
 
Hi all well what I did was shut off all the upstairs rads so just the downstairs rad were open, set the pump to constant curve @100% operating mode @Max estimated head was 5.9 m and the speed was 5295.
The sitting room rad (which is the new big one) got hot but I could not balance it, the kitchen one which was cold or just barely warm was heating up but did not get hot, the entrance rad was still cold, my conclustion is either the pump cannot push the water round the system (all the above rads are on dead legs) or there is a blockage or trapped air in the return legs, which all I can do is bleed the return legs (not the rads) and see if it makes any difference, if it does not then the only solution is to find a much more powerful pump, if anyone can tell me what would happen if I fitted a commercial pump, of which I have the specs :- UP UPS 14m3/h 13m head pmax 10bar
UPS 25-80 :- 8.5m3/h 7mhead
You are pumping practically NIL as you can see from the pump curve that the flowrate at 5.9M is 0.
The pump power is 22/23kw, you should see this displayed and also the flowrate showing 0 M3/hr, so you might note these.
Also just shut the pump outlet valve for 10 secs or so with it running and the above numbers 5.9M/22kw/0.0M3/hr should remain the same.


1661613131800.png
 
Do the test again but shut all but one rad eg one problem one does that get hot ?
Hi well interesting results:- I turned off the rad in the sitting room (which is 2400mm x 600mm double panel) and left the kitchen one open and left the entrance rad open, the entrance rad started to get hot, the kitchen started to get hotter than before so turned that one off and the entrance rad got hotter, which means to me there is no airlocks, here's some info on the pipe work the entrance is on 10mm pipework the kitchen is on 8mm pipe work, the sitting room is on 15mm pipe work. Being a disabled pensioner (72) I am at my time of life not able to rip out the dead legs and increase the size of the pipe work, I could shut off the kitchen rad as the kitchen is open to the sitting room so the sitting room rad would warm up the kitchen, I could also put TRV's on the bathroom towel rails as they can get pretty hot and the room stat is in the sitting room ( a data term box) which means that when the bedrooms and the bathroom reached the desired temp they would close down resulting in an increased flow to the down stairs dead legs but probably not enough to heat up all the downstairs rads. As I have always maintained the pumps I selected to run my system are not suitable ( silly me) what do you think about using one of the commercial pumps that I listed, i can vividly remember years ago I did put a big pump in the system ( i suppose I could find out which one but it would take me a long time) I even had to manufacture a plate with rubber mountings for the vibration noise and special connection hoses to the system) it worked ok, that's all I can say, anyone want to buy a Grundfos Alpha 3b 15 50/60 bought 4 months ago and has only just started to be used (no heating over the summer months)
 
You are pumping practically NIL as you can see from the pump curve that the flowrate at 5.9M is 0.
The pump power is 22/23kw, you should see this displayed and also the flowrate showing 0 M3/hr, so you might note these.
Also just shut the pump outlet valve for 10 secs or so with it running and the above numbers 5.9M/22kw/0.0M3/hr should remain the same.
 
Have a careful look at the pump power as iis possible that its pumping 0.65m3/hr (10.8LPM), if so the pump power will be 34W so carefully note this and then briefly shut the pump outlet valve and again note the power.
 
Just note the pump power as above "Have a careful look at the pump power as its possible that its pumping 0.65m3/hr (10.8LPM), if so the pump power will be 34W so carefully note this and then briefly shut the pump outlet valve and again note the power.

Even if you installed a 10M pump the flowrate (if any) will only increase by 30% (sqroot 10/6) so maybe from 10.8LPM to 14.0LPM, so checkout the power please.

Also if you only now changed to 100% CC from PP3 then the flowrate would only have been 7.9LPM at 3.15M. assuming the pump is running at 34w above.
 
Last edited:
Hi John thanks for your input, I need to shut down (my head is spinning from all that's going on) so as I told you I am getting on a bit, would it be possible to give me the settings for the pump so as to obtain the measurements you require, then I will shut the outlet down and record the settings again and we can take it from there thanks.
 
OK, (I'm getting on a good bit more than you).

Just put or leave the pump in CC (constant curve) mode at 100% which is the highest possible setting that will give the greatest circulation.

Leave what ever rads you have open to the circuit now and just start the boiler/pump and note the pump head in (meters) M, the flowrate in M3/hr and the most important one of all the power output in (watts) W. and then just shut the pump outlet valve for say 5 secs (boiler/pump running) and just note the above readings again, re open the pump outlet valve and if desired then shut down the boiler/pump. You may wish to post the first set of readings before doing the closed valve test.
 
OK, (I'm getting on a good bit more than you).

Just put or leave the pump in CC (constant curve) mode at 100% which is the highest possible setting that will give the greatest circulation.

Leave what ever rads you have open to the circuit now and just start the boiler/pump and note the pump head in (meters) M, the flowrate in M3/hr and the most important one of all the power output in (watts) W. and then just shut the pump outlet valve for say 5 secs (boiler/pump running) and just note the above readings again, re open the pump outlet valve and if desired then shut down the boiler/pump. You may wish to post the first set of readings before doing the closed valve test.
OK, (I'm getting on a good bit more than you).

Just put or leave the pump in CC (constant curve) mode at 100% which is the highest possible setting that will give the greatest circulation.

Leave what ever rads you have open to the circuit now and just start the boiler/pump and note the pump head in (meters) M, the flowrate in M3/hr and the most important one of all the power output in (watts) W. and then just shut the pump outlet valve for say 5 secs (boiler/pump running) and just note the above readings again, re open the pump outlet valve and if desired then shut down the boiler/pump. You may wish to post the first set of readings before doing the closed valve test.
Hi thanks John I get tired very easily these days with the problems associated with me being diabetic and problems with my knees and arms, I never thought that having arthritis in my arms would feel like I had bad toothache but it does with me been to the dentist and he pointed this out to me, will talk with you tomorrow if that is ok with you, got to get this sorted out before the cold weather sets in as this is another problem with being diabetic I cannot stand the cold, never mind.
 
Hi thanks John I get tired very easily these days with the problems associated with me being diabetic and problems with my knees and arms, I never thought that having arthritis in my arms would feel like I had bad toothache but it does with me been to the dentist and he pointed this out to me, will talk with you tomorrow if that is ok with you, got to get this sorted out before the cold weather sets in as this is another problem with being diabetic I cannot stand the cold, never mind.
 
Good morning John
Did like you said and the results from closing the outlet of the pump were no different than the previous results namely :- estimated pump head 5.9M, flow rate 0.0m3/h, power output 22watts
 
Just to be clear
Pump definitely in CC3 mode and results with the pump outlet open were the same as with it closed, above, ie, 5.9M, flow rate 0.0m3/h, power output 22watts??, extraordinary as you are getting some circulation through the rads.
Also check that the pump inlet valve is fully open.
Just confirm the above please and I will have another look through the pump manual
 
Just to be clear
Pump definitely in CC3 mode and results with the pump outlet open were the same as with it closed, above, ie, 5.9M, flow rate 0.0m3/h, power output 22watts??, extraordinary as you are getting some circulation through the rads.
Also check that the pump inlet valve is fully open.
Just confirm the above please and I will have another look through the pump manual
Yes John exactly the same, I had the same query how come the downstairs big radiator (upstairs closed) was heating up with a flow rate of 0.0m3/h dos'nt seem possible, the system is a sealed fully pumped "Y" plan
one
 

Reply to Which is the more powerful pump? in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

    • Like
  • Sticky
We have 2 brand new cordless, battery powered press tools in stock, and flying off the shelves. Our TekTools TZ1930 & TZ1550 are packed with advanced features - these cordless press tools are engineered for speed, precision, and ease of use across various applications. Just reply to this thread...
Replies
5
Views
935
Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...
Replies
0
Views
246
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
291
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
501
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
376
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock