So we have a standard 2 splan - one M.valve for heating (which feeds all the radiators in the house) and one one for water.

Tado controls both independently. When the downstairs thermostat calls for heat - it tells the tado controller to open the DHW valve - and boiler starts etc etc. the other thermostats around the house just tell the radiators in their “zone” to open and close as needed. If the downstairs is calling for heat at that moment - the radiators will get hotter. If downstairs isn’t calling for heat - they won’t get hotter. (That’s our choice - and was recommended by tado to do this)

When I was mentioning about hearing the pump - I was referring to the overrun. It sounds like the pump keeps pumping for about 5 mins from the time the last valve closes - and then the boiler is quiet. I presume this is by design.

When either valve is open - you hear the boiler in full force.

You mentioned about the boiler pump running constantly with a call to the boiler to run - and not burning if the output is > the heating demand? But surely if the heating demand isn’t met - the boiler should be burning? And if the heating demand is met (room stat hits temperature) the value would close - and the boiler would stop anyway? So what scenario would the valve be open - but not calling for heat?
P.s - thank you so much for your patience, advice and understanding! I really appreciate it!
 
Tbh all looks normal so just higher use
 
The meter reads nothing when not on / out

The meter is reporting the correct kWh over time heating / hot water been on around 8 hours total at 24kw

How long has the tado kit been installed?
 
That's correct, all boilers have a minimum output, depending on boiler manufacturer, boiler output etc, it will be ~ say 3 to 6 kw so if the heating demand is below this then the boiler temperature will rise and the burner will cut out when this temperature reaches its setpoint+3C (normally) and the burner will cut back in when the boiler temp is its setpoint-3C plus the boilers anticycling time which may be ~ 3 mins, the pump will continue to run because the demand for heat has not gone away.

"When the downstairs thermostat calls for heat - it tells the tado controller to open the DHW valve" do you mean the CH m.valve? The DHW valve is also controlled by the cyl stat.
 
The meter reads nothing when not on / out

The meter is reporting the correct kWh over time

How long has the tado kit been installed?
Correct - the question is is the boiler using more gas than it should?

Tado been installed for 10 years. I added digital tado room stats about a year ago in the hope that it would help… alas it didn’t!
 
Doesn’t look like so you’ve had this problem for a while ?

“I added digital tado room stats about a year ago in the hope that it would help… alas it didn’t!”
 
That's correct, all boilers have a minimum output, depending on boiler manufacturer, boiler output etc, it will be ~ say 3 to 6 kw so if the heating demand is below this then the boiler temperature will rise and the burner will cut out when this temperature reaches its setpoint+3C (normally) and the burner will cut back in when the boiler temp is its setpoint-3C plus the boilers anticycling time which may be ~ 3 mins, the pump will continue to run because the demand for heat has not gone away.

"When the downstairs thermostat calls for heat - it tells the tado controller to open the DHW valve" do you mean the CH m.valve? The DHW valve is also controlled by the cyl stat.
Apologies yes - when the CH valve will open when downstairs calls for heat!
 
So, what tells the boiler to start when there is a call for DHW in high summer or anytime for that matter when all TRVs are shut?.
 
Doesn’t look like so you’ve had this problem for a while ?

“I added digital tado room stats about a year ago in the hope that it would help… alas it didn’t!”
Yes - I’ve had it for over a year - maybe 2. I’ve gone through cycles of trying to find a solution. Each plumber that came - serviced it and said - “it cold - so you use more heat! - and that was it! They didn’t really check anything - never checked the gas meter for usage per min etc… I just couldn’t find anyone with any drive to just confirm their theory! If it is just I’m using more gas - then so be it!

I just can’t understand why for 8years or so of living in the house - my estimated average gas usage on every bill has been 6-10,000 and a bill of around £120 a month (averaged over the year). I’m now heading to an average of 60,000 according to their estimations (185kwh today!)
 
Only thing I can think is the tado is trying to heat the rooms often instead of a central room stat coming on once maybe twice an hour the tado is bring it on every 2-5 mins as the room temp fluctuates / drops

185x365 67k kWh so seems in the realm of correct
 
So, what tells the boiler to start when there is a call for DHW in high summer or anytime for that matter when all TRVs are shut?.
Tado had a schedule that tells the boiler when to be on. Before I used to have it on 24x7, but after our chats it’s now just 2 hours a day.

When tado tells the hot water to be “on” - the tank stat is then monitored and when the water drops below its Temp - it fires the boiler and Opens the valve.
 
Only thing I can think is the tado is trying to heat the rooms often instead of a central room stat coming on once maybe twice an hour the tado is bring it on every 2-5 mins as the room temp fluctuates / drops

185x365 67k kWh so seems in the realm of correct
185kwh x 365 days is 67525kwh. Is that a normal Amount? Maybe I have unrealistic views? Id checked online and it seemed to suggest around 10-15000 was average to high for a 4 bed house.
 
185kwh x 365 days is 67525kwh. Is that a normal Amount? Maybe I have unrealistic views? Id checked online and it seemed to suggest around 10-15000 was average to high for a 4 bed house.

Depends how long you have the heating on/ your system

That figure will be for a dumb system eg central stat
 
Tado had a schedule that tells the boiler when to be on. Before I used to have it on 24x7, but after our chats it’s now just 2 hours a day.

When tado tells the hot water to be “on” - the tank stat is then monitored and when the water drops below its Temp - it fires the boiler and Opens the valve.
So once again back to square one with that huge usage last summer with no logical reason as there was no demand for CH.
 
185kwh/17.5 heating hours is 10.6kwh/hr so one would expect to see very high room temperatures?

If the boiler is running at 24kw tho due to the flow being enough for high fire
 
So once again back to square one with that huge usage last summer with no logical reason as there was no demand for CH.

Unless there was and the op didn’t notice ?
 
Tado had a schedule that tells the boiler when to be on. Before I used to have it on 24x7, but after our chats it’s now just 2 hours a day.

When tado tells the hot water to be “on” - the tank stat is then monitored and when the water drops below its Temp - it fires the boiler and Opens the valve.
Depends how long you have the heating on/ your system

That figure will be for a dumb system eg central stat
We sort of do have a central stat. There is only one stat that’s downstairs that can call for heat. It’s set to 21 degrees and is on from 6-9pm. The rest of the house is basically just TRV’s (the external thermostat just makes the TRV’s more efficient by sensing the temperature in the room - rather than the temperature on the TRV itself)
 
Unless there was and the op didn’t notice ?
Let’s say I didn’t notice (very possible) - and the heating was on. It wouldn’t be higher than 21 degrees as the TRV’s and thermostats would have controller it) and with the hotter weather outside - it shouldn’t have taken much time keep the house at that temperature. So it still wouldn’t really explain?
 
And there not conflicting with each other eg trvs shut down but stat still calling ?
 
Let’s say I didn’t notice (very possible) - and the heating was on. It wouldn’t be higher than 21 degrees as the TRV’s and thermostats would have controller it) and with the hotter weather outside - it shouldn’t have taken much time keep the house at that temperature. So it still wouldn’t really explain?

Depends what time you have it set for off ?
 
It might be worth converting the system back to a dumb one for a month and see the usage as Jan and feb are normally similar
 
I would expect a "normal" house to need ~ 5/6 kwr/hr to keep it at 21C so 17.5hras @ 6 = 105kwh/day, i heat mine over the last few days 16 hr days for ~ 75/90kwh BUT my (4) bedrooms are kept at 16/18C, all downstairs kept at 21/22C.
 
Plus hot water at around 30kwh ish as depending on usage
 
Depends what time you have it set for off ?
And there not conflicting with each other eg trvs shut down but stat still calling ?

Heating always goes off at 9

It’s possible - although I’ve tested time and time again with the downstairs stat. Pushing to 25 degrees and the ch valve opens - putting it to 5 degrees - it closes. I’ve never seen it not do it! But it’s possible it malfunctioned - but I guess the questions is:

The house was 17.9 degrees at 6am this morning before the heating came on. It was set to 21 degrees and we were in all day. It used 185kwh to try and keep it at 21 degrees. If that’s to get expected - then your view of “I just use more gas” could be right?

4E5684CE-67D3-45A8-90CC-14CD9DF77DDC.png
 
Dumb can be the smartest in the end as long as you don't need room temp control to the nearest 0.1 or 0.2C.

That I think is the problem each room has its own stat that’s opening and shutting prob 1-2 degrees and firing the boiler up for maybe 5 mins each time
 
Dumb can be the smartest in the end as long as you don't need room temp control to the nearest 0.1 or 0.2C.
So that was tados opinion - and the reason we made it so that only downstairs can call for heat. The others TRV’s are just set so that the rooms are not too hot.

I found when we knocked the bedrooms down lower (or turned them off during the day) - the downstairs zone was working harder/longer - I presume trying to bring the whole house up to temp - without the radiators in bedrooms etc helping!
 
Where is the stat placed ?
 
Yes - bedrooms - bathrooms are 20/21 - but they can’t call for heat. They just make sure the rooms do not go over 20/21

Why not use normal trvs are they connected to a hub ?
 

Reply to High gas usage for boiler. in the USA area at PlumbersForums.net

Similar plumbing topics

Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
224
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
451
Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to space for servicing and changing parts if ever needing to. I am finding my decision rather hard due to the different clearances on flue runs and cupboards...
Replies
9
Views
199
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
324
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock