P.s - thank you so much for your patience, advice and understanding! I really appreciate it!So we have a standard 2 splan - one M.valve for heating (which feeds all the radiators in the house) and one one for water.
Tado controls both independently. When the downstairs thermostat calls for heat - it tells the tado controller to open the DHW valve - and boiler starts etc etc. the other thermostats around the house just tell the radiators in their “zone” to open and close as needed. If the downstairs is calling for heat at that moment - the radiators will get hotter. If downstairs isn’t calling for heat - they won’t get hotter. (That’s our choice - and was recommended by tado to do this)
When I was mentioning about hearing the pump - I was referring to the overrun. It sounds like the pump keeps pumping for about 5 mins from the time the last valve closes - and then the boiler is quiet. I presume this is by design.
When either valve is open - you hear the boiler in full force.
You mentioned about the boiler pump running constantly with a call to the boiler to run - and not burning if the output is > the heating demand? But surely if the heating demand isn’t met - the boiler should be burning? And if the heating demand is met (room stat hits temperature) the value would close - and the boiler would stop anyway? So what scenario would the valve be open - but not calling for heat?