Discuss Worcester Greenstar 38cdi Classic Combi Minimum Flow Rate in the USA area at PlumbersForums.net

Messages
6
Hello there, I'm wondering if anybody can advise me, please. I'm in the process of switching my thermostatic radiator valves to Drayton Wiser valves. I currently have one radiator fitted with lockshield valves as a bypass, but I would like to put a Wiser valve on this as well and incorporate an automatic bypass valve into the system. My only problem is finding the information that I need to correctly set the bypass valve.

Could anybody advise me what the minimum flow rate requirement is for a Worcester Bosch Greenstar 38CDi Classic combi, or even better, advise me what the bypass valve should be set at, please? I have looked for the information, but I just can't find it anywhere.

Many thanks in anticipation.

Richard
 
I would leave it as a lockshield or fit an external bypass
 
Thanks for that Shaun, it is an external bypass that I am going to fit (I don't want to leave the radiator with lockshields), so I'm trying to find out what to set a new external bypass valve to.

Kind regards,

Richard

you set them under normal conditions with all the trvs open so there’s no flow through eg no heat and add half a turn / number so eg no flow on 2 you set it to 2.5
 

Reply to Worcester Greenstar 38cdi Classic Combi Minimum Flow Rate in the USA area at PlumbersForums.net

Similar plumbing topics

Hello, I have quite low flow rate for my electric shower (a piddling 5L/min), and would like some tips or advice about how to solve or find the...
Replies
14
Views
892
Essaboy
E
Hello all, I have a WorcesterBosch Greenstar 42CDi classic combi, which is providing DHW fine, but not heating. Was working fine in spring...
Replies
11
Views
1K
Hoping someone can give me advice with this one. At an annual gas service today I found a Worcester Greenstar Junior 28i to be using only running...
Replies
10
Views
2K
Hi everyone! My Worcester Greenstar 30CDi Combi boiler started making a rather loud juddering noise two nights ago. I bled all the radiators and...
Replies
3
Views
958
Deleted member 120897
D
I am going back to a Worcester Greenstar 30 CDi Classic that's failing a CO2 emissions test on minimum rate only. I do adjust the gas valve but...
Replies
9
Views
1K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock