Can anyone give me some advice as to why when I switch central heating to water only in summer, it doesn't take long for the sounds of rushing water in and around the circulation pump inside the airing cupboard. If I call for radiator heating and the 3 way valve goes to mid position, all goes quiet with the system. The pump is an old WSP GOLD fitted in 1996 (year of house build) and this when circulating the full system is fairly quiet apart from a bit of humming heard.
I have recently cleared a blockage from F&E tank in loft which was the 15mm feed pipe to the heating system. I have also circulated FERNOX DS40 for a week and cleared a lot of sludge from the system. All radiators now heat up well, however, when calling for hot water only and 3 way valve closes to the radiators, the noise is loud and annoying. It feels like it might be damaging the pump running like this. Does any have any solutions to water only heating (quietly) Thanks in advance.

Mark
 
Hi there, thanks for responding... Yes from the 3 way valve 22mm pipe runs about 18" horizontal, then a sweeping bend upwards to the vertical for 24" before it enters the cylinder.

Thanks.. Mark

Check for an air vent located at the top of that pipe work, it might just be trapped air. It should look something similar to this:

1592554788228.jpeg


Slightly unscrew to release any air, keeping a cloth/paper towel for any water. If all you get is water, this may not be your issue.
 

Reply to Heating Water only causes rushing sounds from pump. in the USA area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
126
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
276
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
1
Views
132
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
323
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
445
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock