Discuss Gas meter sizing and usage calcs in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Dan-HybridHeat

Gas Engineer
Messages
61
Hi all

I'm in the midst of starting a fairly large new build property. The main house has a boiler and fire and there is also a separate coach house with it's own boiler. All appliances will be ran from the same meter in the main house (the coach house is approx 5m from meter location).

Appliances are as follows

Worcester 40CDI Classic regular - 4.4m3/hr
Gazco Studio 3 - 0.962m3/hr
Worcester 25i combi - 2.63m3/hr

According to Technical Bulletin 089, I have calculated that the required gas flow rate required is 6.05m3/hr. I assumed before any of this we would need a U16 meter as all appliances running on max together will require 7.992m3/hr, but as TB089 says 6.05m3/hr I assume I use this reading? As this is so close to 6m3/hr would a U6 be adequate?

We've also been asked to supply gas usage - one for KWh and one for annual KW consumption? How do I go about calculating the annual consumption accurately?

I've never had to do this before so any help/advice would be much appreciated from anyone with experience.

Thanks
 

Reply to Gas meter sizing and usage calcs in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
526
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the...
Replies
5
Views
306
Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to...
Replies
9
Views
264
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
402
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
182
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock