Hi there guys i know this might sound like a silly question. I am a new learner (not qualified yet) and i just want to know the correct procedures on what you should do in an event of a boiler breakdown. For example lets say if the boiler is leaking... Do you Isolate water and gas to the boiler first? or do you have to do the usual let by and tightness test and then the other stuff?
 
@Scott_1979 @Riley thanks for the reply guys but lets say once you have have fixed the issue with the boiler. do you have to do all of the testing again like...

let by, stabilisation and tightness test?
gas rate?
Working pressures?
Co2 combustion checks?

if you get what i mean?
 
depends what the fault was

lets say diverter leaking

i wouldnt do a

let by or tt
gas rate
working pressure
or fga test

i would do a visual check of the boiler
visual check of the case seals
and i would listen to how it starts up you can normally guess how its running
 
1 rule I’ve always followed is

Anything I do with out removing the combustion chamber it’s a visual only.

For example changing a Baxi 105e pump visual only not disturbed anything affecting combustion. Documented well because no one will help you when your standing in the doc. That piece of paper can be your get out of jail card.

If I was changing a pump on a Worcester 24i junior greenstar I’d do a gas rate and record flue analyser readings. Again documented well.

Only do a full tightness test when necessary. If you do a tightness test on every job you’re opening a can of worms.

BG started doing a tightness test on every job but scrapped it soon after.

Homeserve used to do a mini tightness test on the gas valve they scrapped that pretty quickly. (Only do it when changing a gas valve or see if it’s opening)

According to the old regs after a tightness test we had to purge and relight each appliance thankfully now it’s changed. Only purge and relight once you’ve let air in to the system from the furthest appliance away.
 
Hi there guys i know this might sound like a silly question. I am a new learner (not qualified yet) and i just want to know the correct procedures on what you should do in an event of a boiler breakdown. For example lets say if the boiler is leaking... Do you Isolate water and gas to the boiler first? or do you have to do the usual let by and tightness test and then the other stuff?
There is one important issue here which sometimes gets forgotten. Go through with the customer what is wrong in their words AND then EXAMINE all the rest of the system as much as possible check for other unreported defects. Unscrupulous customers can try and load pre existing problems they know about on to naive fitters. Like you fix a diverter then find afterwards the timer is LALA but they will leave it with you. Generally people are nice and honest but some ...usually well healed ones
Can try it on, ones from Formby where I live are the worst ever for this In my opinion
 
Regarding Gas, for me, follow the ignition sequence to see where it fails. For more complex problems do all the basics. Pressure, Gas rate, measure voltages and resistances. Never be afraid to call the manufacturers Technical helpdesk, they know their boiler.
 

So you give an appliance a service after you replace a water part for free

In the real world no one does anything more than a visual

Unless theve changed something that would effect them
 
So you give an appliance a service after you replace a water part for free

In the real world no one does anything more than a visual

Unless theve changed something that would effect them

Who mentioned a service? You are REQUIRED to conduct the tests outlined in 26.9 whenever you work on a gas appliance. Or does repairing/replacing a diverter valve not count as working in a boiler?
 
Who mentioned a service? You are REQUIRED to conduct the tests outlined in 26.9 whenever you work on a gas appliance. Or does repairing/replacing a diverter valve not count as working in a boiler?

Which is what a basic service is

Fga gas rate etc
 
(9) Where a person performs work on a gas appliance he shall immediately thereafter examine—
(a)​
the effectiveness of any flue;​
(b)​
the supply of combustion air;​
(c)
its operating pressure or heat input or, where necessary, both;
(d)​
its operation so as to ensure its safe functioning,​
 
Jeez. You may call that a service. You have no idea to what I am referring, do you?

Yes 26.9 Reference is

Flue gases
Combustion air
Op pressure / input
Operation

Which in turn is the same as you would do in servicing
 
But you will not comply with the regs? Bit surprised, Shaun, did not expect that of you

So after topping up an expansion vessel you would service the boiler
 
Shaun. 26.9 is NOT a service. It is the minimum required when attending a gas appliance. Even if you are there to top up an EV, your attention and subsequent leaving it working counts as an affirmation that all is safe with the boiler. The regs demand that, to be sure, you complete 26.9.

Really, what bit do you not understand?
 
Shaun. 26.9 is NOT a service. It is the minimum required when attending a gas appliance. Even if you are there to top up an EV, your attention and subsequent leaving it working counts as an affirmation that all is safe with the boiler. The regs demand that, to be sure, you complete 26.9.

Really, what bit do you not understand?

Think you should email bg then

How's the homeowner supposed to do these checks when they replace a diverter valve on a 105
 
Come on, Shaun, stop digging holes. A homeowner is not subject to 26.9, but, as a RGI, presumably, you are.

Why not same situation also you haven't addressed anything in regards to bg

Also sparkys wiring boiler same checks must be applied then as theve disturbed the seal
 
Why not same situation also you haven't addressed anything in regards to bg

Also sparkys wiring boiler same checks must be applied then as theve disturbed the seal

Homeowners are not trained as RGI's therefore not subject to the same rules,or have the same responsibilities. In the same way that a removal man can disconnect a plug in cooker without being subject to the regs, whereas we would be.

What about BG? Their RGI's are subject to 26.9. Whether an individual complies is another thing - you clearly do not. I did a short stint as a BG contractor, and their "service", includes all of 26.9.

Re electricians. They should not be removing the case and breaking the seal, unless a RGI is also in attendance to reinstate the appliance. Apart from electricians who also hold gas certs.

Can you not see that the regs insist that you do 26.9. I am a little confused that you are arguing on this. I suspect that any GS inspector reading this would be interested in your ID.
 
Homeowners are not trained as RGI's therefore not subject to the same rules,or have the same responsibilities. In the same way that a removal man can disconnect a plug in cooker without being subject to the regs, whereas we would be.

What about BG? Their RGI's are subject to 26.9. Whether an individual complies is another thing - you clearly do not. I did a short stint as a BG contractor, and their "service", includes all of 26.9.

Re electricians. They should not be removing the case and breaking the seal, unless a RGI is also in attendance to reinstate the appliance. Apart from electricians who also hold gas certs.

Can you not see that the regs insist that you do 26.9. I am a little confused that you are arguing on this. I suspect that any GS inspector reading this would be interested in your ID.

This is from an inspector

Unless your changing a gas part that could effect the burning / you something you need to set it up visual only

Carry on how you are and I will do the same
 
Fair enough we can agree to do that. But your inspector is wrong, or you misunderstood him. Get him to put it in writing. As I posted earlier, this is a direct lift from the regs:

(9) Where a person performs work on a gas appliance he shall immediately thereafter examine—
(a)

the effectiveness of any flue;
(b)
the supply of combustion air;
(c)
its operating pressure or heat input or, where necessary, both;
(d)
its operation so as to ensure its safe functioning,

I do not see any bit saying this only applies when fitting parts. Are you sure he was not referring tp the need or otherwise of conducting a FGA?

EDIT: For some reason, copying this is affecting the text set up.
 
Fair enough we can agree to do that. But your inspector is wrong, or you misunderstood him. Get him to put it in writing. As I posted earlier, this is a direct lift from the regs:

(9) Where a person performs work on a gas appliance he shall immediately thereafter examine—
(a)

the effectiveness of any flue;
(b)
the supply of combustion air;
(c)
its operating pressure or heat input or, where necessary, both;
(d)
its operation so as to ensure its safe functioning,

I do not see any bit saying this only applies when fitting parts. Are you sure he was not referring tp the need or otherwise of conducting a FGA?

EDIT: For some reason, copying this is affecting the text set up.

Only says examine which could mean visual
 
Hi there guys i know this might sound like a silly question. I am a new learner (not qualified yet) and i just want to know the correct procedures on what you should do in an event of a boiler breakdown. For example lets say if the boiler is leaking... Do you Isolate water and gas to the boiler first? or do you have to do the usual let by and tightness test and then the other stuff?

Ibraheem, hopefully your mentor / trainers will put you right on this. Breakdown jobs range from the stupidly easy, to the practically impossible. Fault finding demands a logical approach, which (as someone else suggested) is a skill learned and developed.

Before opening your toolbox, you should first try to employ the most useful tool. The customer. Some are complete idiots, but with careful questioning you can often pinpoint the problem, before taking the case off. But never actually take their word as Gospel. Some are dishonest, some are confused, and some don't actually understand the questions.

In the absence if common sense, or to confirm your initial diagnosis, you essentially work out how far into the expected sequence the boiler is going. For example, if the ignition is trying to spark, you can be pretty sure the fan is running.

On most boilers, if the HW works, but he CG doesn't, the pump is working. But those are basic and obvious.

But do not start pulling things out before you have attempted to run the appliance, observed and listened.

And comply with 26.9, which I am sure you have come across in training.

Are you in a job, or do you intend going SE? If the latter, invest in the 3 day Baxi Course. It is excellent, and is not a sales pitch. You also get a reasonable lunch. Also join the Honeywell installers club. They offer a free (at least they used to) one day course on wiring and fault finding. It is pretty good. And the lunch is excellent, especially as it is free.

I do like lunch :)
 
Gas rate you can as it says or only need one

Seriously?

I suspect that the lack of comments from other RGI's is be cause you are a generally popular correspondent, whereas I am an infrequent visitor. If you were supporting my argument, and I yours, we would be inundated with responses.

How can you visually check a Gas Rate?
 
Seriously?

I suspect that the lack of comments from other RGI's is be cause you are a generally popular correspondent, whereas I am an infrequent visitor. If you were supporting my argument, and I yours, we would be inundated with responses.

How can you visually check a Gas Rate?

its not hard if you know if you dont

write the number down time then write the numbers down work it out from there or time it if imperial

or if you do know what kw should give you like

.10 is 30kw
.095 is 28kw
.08 is 24 kw
.05 is 15kw
 
its not hard if you know if you dont

write the number down time then write the numbers down work it out from there or time it if imperial

or if you do know what kw should give you like

.10 is 30kw
.095 is 28kw
.08 is 24 kw
.05 is 15kw

A bit of back tracking? What you are describing is actually Gas Rating. My personal preference, as it happens, to calculate (metric) is finish - start (2 mins) * 322.8 = Kw/hr.

However this farcical series of posts started when you stated:

i wouldnt do a

let by or tt
gas rate
working pressure
or fga test

i would do a visual check of the boiler
visual check of the case seals.

But now you are acknowledging that you would do a gas rate.
 
A bit of back tracking? What you are describing is actually Gas Rating. My personal preference, as it happens, to calculate (metric) is finish - start (2 mins) * 322.8 = Kw/hr.

However this farcical series of posts started when you stated:

i wouldnt do a

let by or tt
gas rate
working pressure
or fga test

i would do a visual check of the boiler
visual check of the case seals.

But now you are acknowledging that you would do a gas rate.

only to keep you happy and end this debate as its going no where

if you look back you asked how you could do a visual gas rate which ive answered, didnt say i did one i just know the figures off my head

these days you could as you do it or use an app or get to know the figures gets to the same end
 
Okay. We can end this nonsense. As you keep twisting, and obviously do not comply with your obligations.

To the OP: be very careful about accepting advice from any forum, without double checking. This forum, in particular, is replete with guys who have little knowledge of the regulations.
It is full if inaccurate statements, for example, regarding the REQUIREMENTS for tightness testing, and the status, nature and requirements of Landlord Certs (CP12's).
Having said that, Shaun is normally one of the better ones.
 
dont need to tt on land lord gas safety certificates
 
Also @ShaunCorbs & @firemant isnt what you are both describing a KW rating and not a gas rating. A gas rating for a 30kw boiler is about 3.2kw not 30kw? Or am I missing something here?

I don't quite understand your post, HF.
Probably strictly speaking, a gas rate would be measured in M3 but after saying Kw is not a gas rating, you go onto suggest it is.
A 30Kw boiler will be typically about 31/32Kw input, not 3.2. was that a typo?
 
I don't quite understand your post, HF.
Probably strictly speaking, a gas rate would be measured in M3 but after saying Kw is not a gas rating, you go onto suggest it is.
A 30Kw boiler will be typically about 31/32Kw input, not 3.2. was that a typo?
I mean that this is a gas rate mate

3D31C1DB-8248-4A3D-9475-4FAF0E193CC2.jpeg
 
My figures are direct on the meter to give you x amount of kw
 
But my view is that what you are both taking about is an output rating not a gas rate.

It is a gas rate (meter) comes out at 30kw

Eg

004.10
004.20

On the meter
 
I get that, but when you do this calculation 2.8 x 10.65 = 30 ish kw. The end figure which is 30 kw is not the boilers Gas rate it is an output rating.

I don't get what your trying to say ?

You want the input rating ?
 

Reply to Gas Engineers > What is the correct procedure attending a boiler breakdown? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Had a call to a 82 Old man, he paid these £300 up front for a years cover, and I find out on arrival he's been waiting for 3 weeks, no heating or...
Replies
3
Views
607
Just an update to anyone who was following the thread on this site: Tify to gas engineer, what will it take? I got a DM from a user asking for an...
Replies
2
Views
485
Hi everyone I currently work in oil and gas industry working in North Sea and further afield operating on high pressure oil and gas plants. This...
Replies
0
Views
896
Had our gas Baxi Combi inspected and serviced today, as it has been every year. Gas safety cert issued and says all okay, but engineer gave what I...
Replies
4
Views
595
Hi everyone, Is this set up correct: Attic stop valve turns off the cold water to my bathroom (I think it is the rising main in the attic which...
Replies
0
Views
536
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock