Discuss Vitodens 200-W Combi WB2B Steppermotor does not move in the Central Heating Forum area at PlumbersForums.net

Messages
3
Hi,
My combi-boiler has just given up heating the house and basically only delivers hot water. While in central heating mode it heats up and stops to prevent overheating of the internal section of system. No fault or error code are displayed.

Suspicion: 3-way changeover valve assy.

So I temporarily switched boiler to hot water only. So finally I found some time to look under the hood:

I have suspected the stepper motor that controls the three way valve to be faulty. I pulled it off and measured it but it seems OK. Not sure if the valve itself works as it should, it lacks a bit of feeling to it.

So I have re-assembled everything and on power-up it seems to do a system self-test where the stepper motor moves up and down and then rests permanently in the up position (DHW), telling me that it is working and so is the electronic driver circuit. (This does not happen when pressing the reset button, which seems to be a more low-level reset.)

Again, when heating demand is active the stepper motor does not move from the DHW position yet the boiler starts heating, therefore reaching the temp limit of the internal hot water system and then switches off. Odd that there is no error feedback to stop this from happening, as the controller should be aware of the valve position, right?

When I pull the stepper motor off and move the three way valve to ‘heating circuit’ manually, the radiators warm up immediately, so pump and all else is good. Checked all the sensors, they measure OK as well.

Has anybody got an idea what might prevent the valve motor to change over? I suspect it is the valve itself or the hot water draw switch (that has priority) but the valve does not move. (It doesn’t require major force that the stepper motor would be overloaded). It just does nothing and just sits there. I checked the HW draw switch a year ago and it worked fine.

Anybody go any ideas where else to look before I start draining?

Thanks!

Michael


(While I am registered here as “DIY” I am a professional electrical and electronics engineer with degree and worked on quite a few heating systems and boilers. However I do not know the secrets of this boiler beyond the manuals and appreciate a hint from a professional.)
 
To answer my own question for those who were interested is that it seemed to have been the flow sensor switch that was stuck in the no-flow postion. (open circuit). When flow is detected the reed switch closes. It did nothing either way. A tiny bit of contamination was found. May have been something bigger that was already flushed down the drain. Switch cleaned and all seems normal (for now).
BTW only requires stopping and draining the fresh water side, thank god.
 
Hi
It seems like i have exatly same problem - the step motor push up and just hot water is working, when i remove the step motor it warm also the radiator.

What to do excatly ?
Thank you so much
 

Attachments

  • IMG_2050.jpeg
    IMG_2050.jpeg
    398.7 KB · Views: 13
  • IMG_2049.jpeg
    IMG_2049.jpeg
    439.2 KB · Views: 13

Reply to Vitodens 200-W Combi WB2B Steppermotor does not move in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
123
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
1
Views
127
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
224
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
270
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
441
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock