Mark_#9638

Hi, Hopefully someone can throw some light on if this is a real issue or not.

I have had this boiler for about 10 years, I noticed just recently that when the CH has been turned off that a couple of the rads closest to the boiler were slightly warm. When the boiler had demand to heat the DHW I felt all the flow and returns and discovered the CH flow pipe was hot.

From looking at the boiler the DHW and CH copper pipes inside the boiler are teed together so the 3-way valve had to be on the return, from what I can see there is a small stepper motor that actuates an arm which is moving the valve, however the valve itself is all part of the Grundfos pump housing and that looks like a right nightmare to replace.

What I would like to please know is:-
1. Is the hot CH flow pipe normal or not? I guess not as it's a waste of energy.
2. Is there any possibility the issue lies with the stepper motor or the base and actuator the stepper mounts too and not the actual valve in the pump housing?
3. Can the travel of the stepper motor be adjusted in firmware to move the valve more tightly closed or not?
4. If it is the valve in the pump housing is it a pig to replace and best to put up with the slight loss of performance until it gets bad?

I have not tested to see when there is only a demand for CH if the flow to the cylinder DHW gets hot but I am guessing if it does then whatever is deemed here will also cure that.

Thanks in advance
 

Reply to Viessmann 200-w B2HA-35. CH flow pipe hot when only demand for DHW in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
207
I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about...
Replies
7
Views
254
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
273
PSxxxxxx
P
S
Hi, I seemed to have a blockage in kitchen sink. A plumber came and cleared all the pipework that is visible inside my home (there was debris and...
Replies
2
Views
152
Sonya K
S
I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler...
Replies
1
Views
183
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock