Alright guys, just a quick one. Fitted a vailliant ecotec pro 28 today and upon commissioning the gas rate was slightly lower than 10% of the nominal, which baffled me because ive probably fitted 20 of these boilers and they have all been within range.
All of my other checks where fine so i was just how it was so low?

meter working pressure 21mb
working pressure at boiler 20mb
gas rate was 2.70m3/h at full rate which is slightly lower than 10%
All FGA readings where accepible 87ppm 9.1% with casing removed 0.0010 etc etc.

Pipework run is literally 5m of 28m pipe with 1m of 22m.

If anyone could give me a reasonable answer i would be grateful.

cheers:whatchutalkingabout:punk:
 
You need to follow the forum rules regarding gas advice in open forum.

Sent a message to [email protected] with an image of your gsr card to gain access to the gsr private forum.
 
Status
Not open for further replies.

Reply to Vailliant ecotec pro 28 LOW GAS RATE. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, I am a homeowner but caught between a rock & a hard place. I am trying to get a Vaillant ecoTEC 630 plus serviced but the gas safe engineer &...
Replies
8
Views
2K
Hi there, thanks for your time to look at this record long post!! I work on the operational management side or a small building contracting firm...
Replies
9
Views
1K
H
Hi there, thanks for your time to look at this record long post!! I work on the operational management side or a small building contracting firm...
Replies
0
Views
663
HRP123
H
I would like some opinions on this situation. Vaillant Ecotec pro 28 Installed 2 years ago, Commissioned Gas pressure reading 16.5mb at max...
Replies
57
Views
13K
Hi all, We’ve just moved into our new house. The boiler is an ecoTech Pro 28. Identical - or so I thought - to the one in our previous house. It...
Replies
12
Views
2K
Back
Top