It's still a strange one though because if the diverter valve was working originally its hard to understand why not enough water flowed even if the bypass was fully closed, the diverter valve should have directed the primary water to the zone(s) valves which presumably opened at the same time and even one rad/towelrad should provide the minimum flow necessary.
Well, I think I spoke too soon. It's doing the same thing again... Adding more turns on the internal bypass did not help - put it back to the original position now. Does this boiler not have a flow rate sensor for the heating circuit? I'm sure the flow rate is good, because I have 3 towel rails all fully open and they heat up very quickly when the boiler outputs 60C.

So the situation now is that it would sit at minimum flame for a while with return temperature about 38 and flow about 42... If I turn the hot water it heats it up perfectly fine - flow goes above 60 immediately... Then after DHW pump overrun it goes back to heating mode and temperature drop to 40 again. What else could be wrong?
 
In heating mode your boiler has a minimum output of 6kw so assuming that this is correct then a deltaT of 4C (flow/return) = a flowrate of > 20 LPM so no problem there it would seem.

Not sure what you mean by DHW pump overrun, if its a combi?? then the primary circ pump (the only one?)
may go in to overrun when finished with DHW and depending on the pump overrun time could reduce the temperature from 60C to 40C but should then fire up on CH/UFH and very quickly go to 60c again. Are you sure that there is nothing (remotely) setting the boiler flow temp to a very low value when CH/UFH requested?.
 
DHW pump overrun is what it shows in the Status menu after I turn the hot water off. After it's done with overrun and back to heating mode - flow temperature doesn't want to go to 60 and stays about 40.
Both zone vales are just simple 240V, no fancy smart controls connected to the boiler itself. So I'm pretty sure there is nothing setting Flow temp to low value
 
Just used your formula to calculate the flow rate assuming it is firing at min 6kW. If I have 4 degrees flow/return difference it gives me 21.5 l/min. Is this reasonable flow for 3 towel rails?
 
all default settings so OK.

May have asked before but presume you are sure that boiler stays on low firing after CH request because one of the Vaillant's big problems was/is that it fires up at ~ 75% output for up to 1 minute before modulating and sometimes exceeds the SP and cuts out and goes to overrun and anti-cycling before firing up again.
 
Have you down rated your boiler as advised by myself and John g in earlier posts ?? 3 towel rails may only be 1 kw a piece your system flow and return temperatures are to close to each other ideally you need between 10° - 20° differential across your system, at present you have 4° you can go into the diagnostic menu of your boiler and find out your flow rates , flow and return temperatures, pump speed. In my opinion the boiler boiler output is set to high ? reduce to 10 kw with a 60° c flow temperature and monitor can you open up the ufh zones or more rads ? What is the system rated at in kw ufh + rads + towel rails ? Can you post pictures of your install ?
 
Last edited:
Sorry, I was a bit busy with other things.

It seems to work fine now. What I did compared to where I started:
1) set pump speed to Auto (was 100%)
2) set partial heating load to 12kW (was Auto)
3) returned internal bypass to it's original setting (mid-point)

Now my towel rails heat up as expected and I have not experienced boiler running at min flame with flow temperature below 40 over the last few days.

Thanks everyone for your help with this.
 
Good to hear you are back in business, so the changes you have made permanent is: pump speed from 100% to Auto and changed partial heating load from Auto to 12kw. The 3 towel rails were always in the picture even with problems?.
 
Towel rails were initially not ON when UFH was running. Now the rads zone valve opens together with UFH zone to provide additional bypass. However, when I did this first I was still having that problem with low flow temperature, until I changed pump speed and partial load settings. I have not tried running UFH only without rads zone yet - but will do this later.
 
When you get a chance, it would be interesting to see how the auto pump speed works, ie flow/return temp differential or whatever. you might take the following readings on Rads only, UFH only and Rads+UFH, Flow/return temps d.040/d.041 and Target pump speed/Actual pump speed values d.014/d.015.
the UFH on its own can be a challenge for some boilers as the boiler circ flow might only be a third of the UFH circulating flow but the towel rads by pass should help this if they are circulating with UFH only required.
 
Last edited:

Reply to Vaillant EcoTec Plus 938 temperamental in heating mode in the USA area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
139
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
292
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
206
P
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
339
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
481
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock