Worcester Bosch Greenstar 30 CDi Classic System ErP, Underfloor heating and DHWSystem.
I have non return valve in the secondary return before the pump (DAB 65/150-3) which constantly rattles when the pump is running. Its been tried in both the horizontal and vertical modes with no effect. The only way I can silence it is by throttling the isolation valve on the cylinder side of the pump to around 1/3 open but this just seems to defeat the object by having to wait ages to recieve hot water at the furthest bathroom in the line.
I have advised that installing a pump with a built in non-return valve could help but I have been unable to sourse one. Can you recommend any solutions?
 
Why is there a NRV fitted?
Is the NRV a spring loaded type or a swing check type, if a swing check then you could probably install the spring loaded type but on the circ pump discharge side.
 

Attachments

  • Poppet Type NRV.jpg
    Poppet Type NRV.jpg
    208 KB · Views: 4
  • Swing Check Valve Sectioned.jpg
    Swing Check Valve Sectioned.jpg
    32.5 KB · Views: 6
Hot water secondary return

sounds like there’s too much flow going through the valve have you tried turning the pump down as it only wants a trickle through
 
It seems to be a DAB 65..... which I think is 65dM or 6.5M, if so, this would circulate enough water for a small town, a DAB10 or less should be more than adequate, I think these pumps are single speed.
 

Reply to Secondary non-return valve in the USA area at PlumbersForums.net

Similar plumbing topics

Hi. I need a new toilet supply line but don’t know the size type of the fitting at the shut off valve. It is not 3/8 compression. It is a plastic nut about the same size as the one going into the cistern but has a different thread. Attached is a photo. Can you advise. Thanks.
Replies
2
Views
182
I have a plumber coming tomorrow to change a cartridge on a badly dripping tap on my bathroom mixer unit. There is no separate isolating valve for this tap so I'll have to close the stopcock. I tried closing it today but it won't go absolutely 100% closed and there is still a very slight flow...
Replies
1
Views
235
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
316
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
184
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
226
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock