Discuss Potterton Prima Gas Valve in the Plumbing Jobs | The Job-board area at PlumbersForums.net

bennythedip

Gas Engineer
Messages
162
Just been to look at Potterton Prima that’s not lightning. Boiler goes through ignition sequence but there’s no gas coming through the valve to light the pilot. There’s 240v on the white wire going to the gas valve but nothing on the black. I presume there should be 240v on the black as well. If there’s no 240v does the pcb need replacing? Thanks for any help
 
how many wires to the gas valve?
 
how many wires to the gas valve?
There’s 2 solenoids on the gas valve. The one on the left with the black wire has no voltage going to it. The one on the right with the white wire has 240v

F0710C3E-784E-4F13-A42F-25A16D1A8265.jpeg
 
should be a pilot light due to two solenoids
 
Check the resistance of the coil- remove the wires first -if it’s open circuit you can change coil I think on these .
I took a wire off the white lead which has 240v on it and jumpered it onto the black wire to see if the solenoid would open and it opens ok as you can hear it and smell the gas coming through so I think the solenoid is ok, it’s just there doesn’t seem to be 240v going to it to fire it. I’m wondering if the pcb is the problem if it’s not sending out the 240v
 
Cannot remember this boiler. (Brain freeze) is this thenone woth the electrical plug on the front so you can plug the gas valve into to see if it opens?
No there’s no plug but I took a wire off the white lead which has 240v on it and jumpered it onto the black wire to see if the solenoid would open and it opens ok as you can hear it and smell the gas coming through so I think the solenoid is ok, it’s just there doesn’t seem to be 240v going to it to fire it. I’m wondering if the pcb is the problem if it’s not sending out the 240v
 

Reply to Potterton Prima Gas Valve in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hiya fellow gas engineer. Need some help on this boiler fault. Went out to this E133 Error on a Potterton Titanium 24 (GC: 47-393-39) I checked...
Replies
9
Views
497
Dear All New member here, coming looking for help. A few weeks ago I had work carried out by a British Gas Homecare service technician. It...
Replies
14
Views
1K
  • Locked
Replacing a remote gas control valve with its manual equivalent. My daughter has a gas coal effect fire. First, I know they're crap, she'll just...
Replies
8
Views
979
    • Like
Hi everyone, Just wanted to share my experience with "upgrading" an S plan setup to Opentherm and Vaillant Control Center (VR66). There are a few...
Replies
1
Views
1K
Hello, This post is a continuation of my post of yesterday entitled Short cycling in Potterton Kingfisher, BUT with an important change in...
Replies
1
Views
715
Back
Top