W

wisewol

I have a Potterton Performa System 24HE boiler. It is configured in a typical S-plan with 2 external 2-port zone valves (V4043H) along with hot water cylinder stat, a room temperature stat and timing controller. In general it has been a reliable boiler.


A few years ago, it started intermittently stopping with the pump/low pressure warning light (60deg) flashing. When I found this situation (and usually a cold house), I found that if I switched it off at the restart switch and on again, it would burst back into life again, only to fail a day or two later. At that time, I found that turning the main boiler thermostat down a bit made the fault appear less often. I didn't call in a plumber as the chances were that when visiting he would find nothing wrong.


After a year or so with the lower thermostat setting, the fault started appearing again, so down went the thermostat a bit further. Recently on this lower setting, the fault started appearing again. Time to start investigating it more seriously.
I happened on one occasion to be next to the boiler when the fault started. The boiler was at full temperature when it happened. Switching the boiler off and on at this time did not reset and start the boiler, it thought about it for a couple of seconds and then started to flash the low pressure light again. However, once the boiler cooled down, switching off and on again did start the boiler again.


I should add, the water pressure is fine, about 1 bar when cold, rising to 1.5 or maybe 2 when hot. The zone valves work OK, heating the hot water when required and radiators when required, or both. The pressure diaphragm seems OK as does the microswitch attached. I recently changed the pump, but the fault still happens. I have seen some posts on this and other forums of similar symptoms, but no real solution. Some indicated soldering on the pcb may be a problem, so I took out the pcb and examined it closely, but saw no evidence of poor soldering.


As with any problem, you cannot try to solve it unless you can repeat it, so I tried a few experiments. Eventually, I found a sequence of events that I could cause the error and repeat it. This is what I can do to get the fault:


Turn the boiler thermostat up to a relatively high setting. Ensure there is demand for HW, no demand for CH, boiler then fires and starts to heat up. When boiler temp gets to 80C (as indicated by front panel lights), burner still on, remove demand (switching override on controller next to boiler). Burner goes out, pump stays on. After 3 mins, the pump stops and then warning light starts to flash. If I do the same experiment, but remove demand when at 60C, when pump stops, boiler OK and lights just show the temperature.


Anyone any idea what might be wrong with the boiler?
 
If you are gas safe registered. Get your posts up to ten pm thevadmins with you gsr details and they eill likely let you in the private gsr forum. Boiler faults, what causes them and how to fix them is not discussed on the open forum as per the rules.
 
You wont get any detailed info on here unfortunately. Please ring a gsr plumber for your own safety and house insurance..
 
Status
Not open for further replies.

Reply to Potterton Performa low pressure warning in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello Wondering if anyone can offer any clues please // Potterton Promax 18 // Had an E1 error code, repressurised via with filling loop // Boiler fires but now the pressure runs up from 1.5 mark in the green up to 2.5 in the red then flicks off. // Error code again // Once held in reset for...
Replies
1
Views
252
  • Locked
Hello, I have a ferroli falcon 2 boiler (yes it is pretty old). A few days ago the hot water started going hot and cold when running. Monitoring the boiler, the demand light works fine. When the water gets up to temperature every 10 seconds or so, the boiler stops for a fraction of a second...
Replies
3
Views
315
A
Hi, I have Worcester combi boiler which has developed a 'fault' recently. When I switch the heating on, the fire in boiler starts for a second or two and then goes off. After another few seconds it starts again and then stays on. This happens around 8 out of 10 times. I had engineer having a...
Replies
0
Views
329
Andy Jackson
A
I have been facing central heating low pressure on unvented hot water RM Cylinders but can't see any leak on the PRV, expansion vessels and plasterboard celling. I have got unvented pressurized RM Cylinders hot water system with 27KW Worchester gas boiler with expansion vessels . When...
Replies
2
Views
471
losing pressure
L
Conditions: nearly 10 year old boiler WB2B, heating mode off, DHW on or also in standby, Boiler shows no fault LED on, no new fault logged, room thermostat deactivated. Boiler gets odd attacks of suddenly turning on the fan 100%, then (gas valve and ignition are clicking?) potentially tries to...