Hi, first post here and am after some advice please.
I'm having solar panels fitted in the next few weeks and the fit will include an iboost+ to use the immersion element to generate hot water.
I've checked the immersion and using a couple of heat sensors it's apparent the element only heats the top half of the tank, which normally generates hot water via a gas boiler.
My plan is to fit a de strat pump so that the solar energy will provide a full tank of hot water.
The pump has an NRV and a Stop valve built in and also has an integral timer.
The attached picture is a simplified diagram of my vented system hot and cold water pipes. The cold feed comes from the header tank in the loft and the head of the cold water feed is approx 3-4 feet above the top of the hot water tank.
The copper pipes in the diagram are only accessible above the top of the tank.
I know the connecting pipe with the pump attached needs to go from the hot water pipe to the cold feed.
Can I fit the T piece above the joint on the right hot water supply pipe? The vent pipe will have a good few feet of water in it before the vent goes above the header tank water level.
If I then take the pump straight across to the cold feed pipe and connect it via another T piece, will this provide adequate circulation of the hot tank water?
Is there any possibility that cold feed water will be drawn from the header tank when the pump is running?
Have I missed anything?
Thanks.
 

Attachments

  • 20221022_171832.jpg
    20221022_171832.jpg
    246.4 KB · Views: 18
Nrv where the red line is on both pipes eg black line and cold feed
 

Attachments

  • 26928C47-CCB1-4B98-9262-E73A612E3B62.jpeg
    26928C47-CCB1-4B98-9262-E73A612E3B62.jpeg
    132.3 KB · Views: 15
I don't think it would be good practice.
Not only would you risk dragging air into pump when pump and outlets are running but you should maintain a 400/450mm ( can't remember) horizontal run on cylinder outlet partly to avoid convection in pipework from heating vent.
Could consider somewhere close to cylinder outlet or pos on shower feed?
 
Where is the tank located eg is there a wardrobe or somewhere that doesn’t mind an access hatch ?
 
The attached picture is a better representation of the shower pipe t-off position. I could get another t piece at the blue line and attach it 6 inches below the top of the tank on the cold feed. That is as good as it will get access wise. The only access to the back of the cupboard would be thro' the bathroom, but all that rooms walls are fully tiled.
 

Attachments

  • 20221022_211959.jpg
    20221022_211959.jpg
    252.3 KB · Views: 8
that’s fine but you would mostly need around 12” as you have valves and check / nrv s
 
Knappers,
above new picture is the best I can do access wise. The point you make about a 400mm run and convection; all I can say is that I plumbed the shower feed in many years ago and it supplies a pump under the bath prior to a thermostatic mixer and it's always performed really well, no cavitation or other problems. Would the blue line lay out above be much different?
 
You will require valves on the pump and a nrv on the cold feed
 
Correct
 

Reply to Plumbing in a de-strat pump. in the DIY Plumbing Forum area at PlumbersForums.net

Similar plumbing topics

I want to reconnect some outbuildings to an existing water supply. The supply pipe is old 22mm MDPE and buried for a fair distance so not going to dig it up and replace it 😬. Question is can I use normal 22mm plumbing push-fit connectors to make the connection as finding 22mm MDPE fittings...
Replies
1
Views
270
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
344
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
258
Hi, basic question, any insight much appreciated. Looking to have an outdoor tap in my front porch fed from 15mm pex coming up from suspended floor. Pic 1 is inside porch, pex temporarily clipped to give an idea of pipe placement (ignore shoddy blockwork of booted cowboy builder!), Pic 2 is...
Replies
6
Views
236
Copper pipes, I think its fair to say, is not what it used to be, the copper is getting thin while the cost is going up. Meanwhile, plastic Pushfit seems to be getting better and better, cost and convenience was always better, but now the quality is to, have we reached a stage where plastic will...
Replies
2
Views
254
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock